Do you mean the relative humidity on the weather file? <br>
<br>
That would require changing the weather file, but that's not a task
for the timid because:<br>
1) the weather file is in a binary format that you can't read, so
you'd have to convert it to ASCII, make the changes, and convert
that back. There are Fortran programs for doing that, though.<br>
2) RH is a derived value that's not in the weather file. You would
have to change several weather elements and make sure that they're
all consistent - absolute humidity, wet bulb, and enthalpy. <br>
<br>
Joe<br>
<pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
<br>
On 4/9/2014 12:29 PM, Fakeha Sehar wrote:
<blockquote
cite="mid:1397071781.54113.YahooMailNeo@web121804.mail.ne1.yahoo.com"
type="cite">
<div style="color: rgb(0, 0, 0); background-color: rgb(255, 255,
255); font-family: HelveticaNeue,Helvetica
Neue,Helvetica,Arial,Lucida Grande,sans-serif; font-size: 12pt;">
<div>How can relative humidity be changed in eQuest?</div>
</div>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
</body>
</html>