<div dir="ltr">Nick,<div><br></div><div>eQuest limits the HVAC systems for a thermal zone to (1) air-side system that may have reheat and/or supplemental heat, (1) baseboard heat source, (1) exhaust system. To model the VAM system you need to create an equivalent system to the overall systems operating in the thermal zone.</div>
<div><br></div><div>I think you can model your system by creating an exhaust fan (and schedule) for the zone and incorporating the HEX into the FCU using Outdoor Air Heat Recovery. You will need to make some adjustments to system performance (e.g. kW/cfm) to make sure overall performance of the simulated system and actual system align.</div>
</div><div class="gmail_extra"><br clear="all"><div>- Matt Hein<br></div>
<br><br><div class="gmail_quote">On Wed, Mar 26, 2014 at 10:29 AM, Nick Patsos <span dir="ltr"><<a href="mailto:nick.patsos@gmail.com" target="_blank">nick.patsos@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div dir="ltr">Hello everyone,<div><br></div><div>I'm trying to model in eQuest a ventilation air machine (VAM), which is a simple plate heat exchanger with an OA fan and an exhaust fan.</div><div><br></div><div>How can it be modelled to operate with an FCU type of system? (VAM for fresh air heat recovery and FCU for cooling/heating).</div>


<div><br></div><div>Best regards</div><span class="HOEnZb"><font color="#888888"><div><br></div><div>Nick Patsos</div><div>Mechanical Engineer
</div></font></span></div>