<div dir="ltr"><div>Great comments all, and correct for LEED v3.</div><div><br></div><div>This is changing in the new LEED v4. It references ASHRAE 90.1 2010 which does <i>not </i>match the baseline Ventilation rate to a proposed design that exceeds the rates set by the rating authority or building official. </div>

<div><br></div><div>This matches Jim's comments - a high ventilation rate will be penalized under LEED v4, since the baseline is the minimum, and the proposed matches the higher value of the design. </div><div><br></div>

<div>Cheers,</div><div>Alex</div></div><div class="gmail_extra"><br clear="all"><div><div dir="ltr"><p></p><div style="font-size:13px"><b><span lang="EN-CA" style="font-family:Arial,sans-serif;color:rgb(127,127,127);font-size:10pt">Alex Krickx</span></b><span style="font-family:Arial,sans-serif;color:rgb(127,127,127);font-size:10pt"> | </span><span style="color:rgb(127,127,127);font-family:Arial,sans-serif;font-size:10pt;background-color:transparent">LEED</span><span style="color:rgb(127,127,127);font-family:Arial,sans-serif;font-size:10pt;background-color:transparent"> AP</span></div>

<div style="font-size:13px"><font color="#7f7f7f" face="Arial, sans-serif">Project Engineer</font></div><div style="font-size:13px"><span style="font-family:Arial,sans-serif;color:rgb(127,127,127);font-size:10pt"></span><b><span style="font-family:Arial,sans-serif;color:rgb(127,127,127);font-size:10pt">Integral Group </span></b><span style="font-family:Arial,sans-serif;color:rgb(127,127,127);font-size:10pt">| 427 13th Street | Oakland CA USA 94612<br>

T </span><span style="font-size:10.0pt;line-height:115%;font-family:"Arial","sans-serif";color:#3649d2">510.663.2070 x 247</span></div><div style="font-size:13px"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(127,127,127)"><a href="http://www.integralgroup.com/" style="color:rgb(17,85,204)" target="_blank"><span style="color:rgb(127,127,127)">integralgroup.com</span></a> | </span><u style="font-size:13px"><span style="font-family:Arial,sans-serif;color:rgb(127,127,127);font-size:10pt"><a href="mailto:akrickx@integralgroup.com" style="color:rgb(17,85,204)" target="_blank"><span style="color:rgb(127,127,127)">akrickx@integralgroup.com</span></a></span></u><br>

</div><div style="font-size:13px"><span style="font-family:Arial,sans-serif;color:rgb(127,127,127);font-size:10pt"></span></div><p style="font-size:13px"><span lang="EN-GB" style="font-family:Arial,sans-serif;color:rgb(31,73,125);font-size:6pt"></span></p>

<div style="font-size:13px"><b><span style="font-family:Arial,sans-serif;color:rgb(176,188,34);font-size:10pt"></span></b><b><span style="font-family:Arial,sans-serif;color:rgb(176,188,34);font-size:10pt">Trust</span></b><span style="font-family:Arial,sans-serif;color:rgb(51,51,51);font-size:10pt"> </span><span style="font-family:Arial,sans-serif;color:rgb(176,188,34);font-size:12pt">|</span><span style="font-family:Arial,sans-serif;color:rgb(51,51,51);font-size:10pt"> </span><b><span style="font-family:Arial,sans-serif;color:rgb(118,118,98);font-size:10pt">Nurture</span></b><b><span style="font-family:Arial,sans-serif;color:rgb(51,51,51);font-size:10pt"> </span></b><span style="font-family:Arial,sans-serif;color:rgb(51,51,51);font-size:12pt">|</span><span style="font-family:Arial,sans-serif;color:rgb(0,164,228);font-size:10pt"> <b>Inspire</b></span></div>

<div style="font-size:13px"><p><span style="color:rgb(176,188,34);font-family:Arial,sans-serif;font-size:8pt">Please consider the environment before printing this email.</span><br></p></div></div></div>
<br><br><div class="gmail_quote">On Fri, Mar 7, 2014 at 6:47 AM, Robby Oylear <span dir="ltr"><<a href="mailto:robbyoylear@gmail.com" target="_blank">robbyoylear@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">

<div dir="ltr">Joe,<div><br></div><div>Your last bit there about taking credit for constant OA flow from full-load to part-load conditions on a VAV system is a bit of a red flag for me.  The Baseline system should be minimally compliant with ASHRAE 62.1.  ASHRAE 62.1 section 6.2.6.1 requires that ventilation systems shall be designed to be capable of providing the required ventilation rates in the breathing zone including all full- and part-load conditions.  Outside of Demand Control Ventilation scenarios, I would always expect the Baseline and Proposed case to deliver the same outside airflow at all hours.</div>


<div><br></div><div>That being said, I'm not certain how you're actually getting a credit for what you're saying.  What input are you modifying in eQUEST to accomplish proportional outside air flow control?</div>


<div><br></div><div>-Robby</div></div><div class="gmail_extra"><br><br><div class="gmail_quote"><div><div class="h5">On Thu, Mar 6, 2014 at 1:48 PM, Joseph Lewis <span dir="ltr"><<a href="mailto:jlewis@fortierengineering.com" target="_blank">jlewis@fortierengineering.com</a>></span> wrote:<br>


</div></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div><div class="h5">




<div lang="EN-US" dir="ltr" link="#0563c1" vlink="#954f72">
<div dir="ltr">
<div style="font-size:12pt;font-family:'Calibri'">
<div>You are going to follow 90.1 Appendix G for the model.  This means 
both the baseline and proposed design outdoor air flow rates will need to be the 
same except if you are using demand control ventilation in the proposed and it 
is not required by 90.1 section 6.</div>
<div> </div>
<div>In the case where you have demand controlled ventilation in the proposed 
and it is not required in the baseline then the USGBC has stated that they would 
like the baseline to be modeled as compliant with 62.1 without the system level 
corrections.  There also should not be any temperature difference 
corrections because the other appendix G rules require your CFM sizing to be 
based up on a 20 °F delta T.</div>
<div> </div>
<div>If demand controlled ventilation is required by 90.1 then it must be 
modeled in the baseline and proposed with the same design flow.</div>
<div> </div>
<div>I personally take credit on my models for where the proposed VAV system has 
controls to maintain a constant OA flow across from design to minimum supply, by 
modeling the baseline as just proportional.  I have not been flagged for 
it, but I also have not found any definitive ruling that what I am doing is 
allowed.    </div>
<div> </div>
<div>Joe Lewis</div>
<div>Fortier Engineering</div>
<div style="font-style:normal;font-size:small;display:inline;font-family:"Calibri";text-decoration:none;font-weight:normal">
<div style="FONT:10pt tahoma">
<div><font size="3" face="Calibri"></font> </div>
<div style="BACKGROUND:#f5f5f5">
<div><b>From:</b> <a title="JoeC@designengineers.com" href="mailto:JoeC@designengineers.com" target="_blank">Joe Chappell</a> </div>
<div><b>Sent:</b> Thursday, March 06, 2014 3:50 PM</div>
<div><b>To:</b> <a title="equest-users@lists.onebuilding.org" href="mailto:equest-users@lists.onebuilding.org" target="_blank">mailto:equest-users@lists.onebuilding.org</a> 
</div>
<div><b>Subject:</b> [Equest-users] LEED Increased Ventilation Credit and Energy 
Modeling</div></div></div>
<div> </div></div><div><div>
<div style="font-style:normal;font-size:small;display:inline;font-family:"Calibri";text-decoration:none;font-weight:normal">
<div>
<p class="MsoNormal">Good day,<u></u><u></u></p>
<p class="MsoNormal"><u></u><u></u> </p>
<p class="MsoNormal">I have a question regarding the LEED credit for Increased 
Ventilation (IEQc2).  This is the credit awarded for exceeding ventilation 
in all spaces by 30% beyond the ASHRAE standard 62.1 requirements.  It 
seems obvious that the design model ventilation rates would be those 30% higher 
than 62.1 requirements.  What then would the baseline model ventilation 
rates be?  <u></u><u></u></p>
<p class="MsoNormal"><u></u><u></u> </p>
<p class="MsoNormal">If you strictly follow 90.1 Appendix G, you should always 
model baseline and proposed equivalent except for when taking credit for demand 
controlled ventilation.  However, it seems in this case that it could also 
be argued (by LEED) that you should model the ASHRAE 62.1 required ventilation 
rates in the baseline model, not those that are 30% higher and therefore pay the 
energy expense( most climates) for increased outside air.<u></u><u></u></p>
<p class="MsoNormal"><u></u><u></u> </p>
<p class="MsoNormal">Does anyone have any experience with LEED on this 
issue?  Thanks in advance.<u></u><u></u></p>
<p class="MsoNormal"><u></u><u></u> </p>
<p class="MsoNormal">Kind regards,<u></u><u></u></p>
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:"Arial","sans-serif"">Joe 
Chappell</span></b><span style="font-size:10pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p>
<p class="MsoNormal"><u></u><u></u> </p></div></div></div></div></div></div></div>
<br></div></div>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>