<div dir="ltr"><div>Joe hi!</div><div> </div><div>Thanks for your response. I had autosized the systems in both programs. Since the loads were different, then the air flow rates ended up being different. Based on your comments, I entered the air flow rate calculated by eQUEST into EnergyPlus. I also added the Daylight saving time of eQUEST into EnergyPlus. Attached is how my charts currently look like. I am also attaching the new EnergyPlus file. Most of the problems seem to have been resolved except the night time control. I would appreciate any suggestion on solving this discrepancy between the two models.</div>
<div> </div><div>Thank you very much in advance,</div><div>Best Regards,</div><div>Simge Andolsun, Ph.D.</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Thu, Feb 13, 2014 at 1:40 PM, Joe Huang <span dir="ltr"><<a href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank">yjhuang@whiteboxtechnologies.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><u></u>

  
    
  
  <div bgcolor="#ffffff" text="#000000">
    (repost of comment on EnergyPlus_Support bulletin board in case any
    eQUEST-Users readers have other thoughts or corrections)<br>
    <br>
    -------- Original Message --------<br>
    Subject:     Re: [EnergyPlus_Support] eQUEST vs EnergyPlus: Fan
    Energy Consumption<br>
    Date:     Thu, 13 Feb 2014 11:32:17 -0800<br>
    From:     Joe Huang <a href="mailto:YJHuang@whiteboxtechnologies.com" target="_blank"><YJHuang@whiteboxtechnologies.com></a><br>
    Reply-To:     <a href="mailto:EnergyPlus_Support@yahoogroups.com" target="_blank">EnergyPlus_Support@yahoogroups.com</a><br>
    To:     <a href="mailto:EnergyPlus_Support@yahoogroups.com" target="_blank">EnergyPlus_Support@yahoogroups.com</a><br>
    <br>
    Simge,<br>
    <br>
    Looking at your plots, it seems that the eQUEST fan is simply larger
    by 40% or so.  Are you letting the programs autosize the equipment,
    and did you use any sizing-factors  or sizing-ratios in the runs?  I
    would just take the larger<br>
    capacity of the two runs, and use that for both runs, which should
    take care of the discrepancy.<br>
    <br>
    Other observations:<br>
    1. eQUEST CYCLE-ON-ANY seems to keep the fans on the entire hour,
    whereas EnergyPlus seems to cycling them on<br>
        only when the HVAC is on.<br>
    <br>
    2. You seem to have daylight savings in the eQUEST, but not in the
    EnergyPlus model.<br>
    <br>
    Joe<br>
     <br>
    <pre cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank">yjhuang@whiteboxtechnologies.com</a>
<a href="http://weather.whiteboxtechnologies.com" target="_blank">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) <a href="tel:%28925%29388-0265" target="_blank" value="+19253880265">(925)388-0265</a>
(c) <a href="tel:%28510%29928-2683" target="_blank" value="+15109282683">(510)928-2683</a>
"building energy simulations at your fingertips"
</pre><div><div class="h5">
    <br>
    On 2/13/2014 9:06 AM, Simge Andolsun wrote:
    </div></div><blockquote type="cite"><div><div class="h5">
      <div dir="ltr"><font color="#000000" face="Times New Roman" size="3">
        </font>
        <p style="background:white"><span style="font-family:"Helvetica","sans-serif""><font size="3">Dear EnergyPlus users,<br>
              <br>
              We have modeled a test case with exactly same inputs in
              eQUEST and EnergyPlus
              to compare the results of these programs for an identical
              situation. This case
              had a PTAC system with electric heating. The fan inputs
              were as follows in both
              eQUEST and EnergyPlus:</font></span></p>
        <font color="#000000" face="Times New Roman" size="3">
        </font>
        <p style="background:white;margin:5pt 0in 6pt 0.5in"><span style="font-family:Symbol"><span><font size="3">·</font><span style="font:7pt/normal "Times New Roman";font-size-adjust:none;font-stretch:normal">        
              </span></span></span><span style="font-family:"Helvetica","sans-serif""><font size="3">0.3 inWG (74.7 Pa), 0.6 total efficiency fraction</font></span></p>
        <font color="#000000" face="Times New Roman" size="3">
        </font>
        <p style="background:white;margin:5pt 0in 6pt 0.5in"><span style="font-family:Symbol"><span><font size="3">·</font><span style="font:7pt/normal "Times New Roman";font-size-adjust:none;font-stretch:normal">       </span></span></span><span style="font-family:"Helvetica","sans-serif""><font size="3">In eQUEST: Fan control is constant volume, with
              night time cycling<br>
              In EnergyPlus: Fan control is constant volume (fan control
              schedule=1) when the fans are scheduled to be on and it is
              cycling
              (fan control schedule=0) when the fans are scheduled to be
              off. I used AvailabilityManager:NightCycle to set this
              control (Please let
              me know whether there is any better way to model the same
              fan control condition
              in eQUEST and EnergyPlus).</font></span></p>
        <font color="#000000" face="Times New Roman" size="3">
        </font>
        <p style="background:white;margin-left:0.5in"><span style="font-family:Symbol"><span><font size="3">·</font><span style="font:7pt/normal "Times New Roman";font-size-adjust:none;font-stretch:normal">        
              </span></span></span><span style="font-family:"Helvetica","sans-serif""><font size="3">California Title 24 fan availability schedules
              were used in both
              programs. These schedules turn the fan off during the
              hours listed below:</font></span></p>
        <font color="#000000" face="Times New Roman" size="3">
        </font>
        <p style="background:white;margin:0in 0in 0pt;text-indent:0.5in"><span style="font-family:"Helvetica","sans-serif""><font size="3">Weekdays: Between
              8pm-5am</font></span></p>
        <font color="#000000" face="Times New Roman" size="3">
        </font>
        <p style="background:white;margin:0in 0in 0pt;text-indent:0.5in"><span style="font-family:"Helvetica","sans-serif""><font size="3">Saturday: Between
              3pm-5am</font></span></p>
        <font color="#000000" face="Times New Roman" size="3">
        </font>
        <p style="background:white;margin:0in 0in 0pt;text-indent:0.5in"><span style="font-family:"Helvetica","sans-serif""><font size="3">Sundays and Holidays:
              Off all day.</font></span></p>
        <font color="#000000" face="Times New Roman" size="3">
        </font>
        <p style="background:white"><span style="font-family:"Helvetica","sans-serif""><font size="3">The fan energy consumption of the two programs
              ended up differing
              from each other significantly. Attached are the charts
              that show the results of
              the coldest and warmest days. Would you let me know what
              might be the reason
              for this difference between the two programs? <br>
              <br>
              Thank you very much in advance for your help,<br>
              Best Regards,<br>
              S. Andolsun, Ph.D.</font></span></p>
        <font color="#000000" face="Times New Roman" size="3">
        </font></div>
      </div></div><pre><fieldset></fieldset>
_______________________________________________
Equest-users mailing list
<div><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</div></pre>
    </blockquote>
  </div>

<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>