<div dir="ltr">Neil,<div><br></div><div>Thanks for the very insightful response. The system I'm trying to model is a packaged air cooled/free cooling chiller. I will have to dig deeper into the specs to see if it works partially or just as eQuest models it.</div>
<div>When setting the parameters for my CT how should I set the range and approach so that when ambient temp hits -5C then free cooling takes over?</div><div><br></div><div>Regards</div><div><br></div><div>Sebastian</div>
</div><div class="gmail_extra"><br><br><div class="gmail_quote">On Thu, Feb 6, 2014 at 1:07 AM, Neil Bulger <span dir="ltr"><<a href="mailto:nbulger@integralgroup.com" target="_blank">nbulger@integralgroup.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">The water side economizer chiller should be thought of as a secondary-cooling device on a CHW loop and will cause many head aches if used by itself without any actual chiller object.  On a CHW loop, actual chillers are the only elements that can be used to autosize a CHW loop and any attached CW loop. Without one, loops will not size and the model will crash.<div>


<br></div><div>The error you posted is only a partial story so it is hard to know the full problem. My guess is you have the WSE chiller on a dedicated cooling tower loop, possibly called DEFAULT-CW, and there is no other chiller attached to this CW loop. In this case, the CW loop will not size itself upon simulation because eQuest does not see the WSE as a primary source of cooling. <b>You can manually size the loop, any pump, and the cooling tower and the model should run.</b></div>


<div><br></div><div>In a larger picture of accounting for WSE, eQuest can only really capture a non-integrated water side economizing (WSE). This setup and control scheme means that the WSE heat exchanger will only operate if the cooling tower and HX are able to handle the full cooling load. In several scenarios, this is a very rare occurrence given standard CHW supply temperatures and the low wetbulb temperature required to make this for free.</div>


<div><br></div><div>It is possible to design a system where a WSE heat exchanger only handles part of the load and pre-cools the return water before it goes to the chillers which handles the remainder. However, it is impossible to model such a system in eQuest. EnergyPlus and IES are the best bet for something like this and even then, it can be tricky to capture the full benefit. It would likely be easiest to post process the eQuest hourly outputs of the cooling load if you have a true fully integrated WSE.</div>


<div><br></div><div>Happy eQuesting!</div><div class="gmail_extra"><br clear="all"><div><div dir="ltr"><p style="margin:0px"><span lang="EN-CA" style="font-size:10pt;font-family:Arial,sans-serif"><b><font color="#444444">Neil Bulger, PE</font></b><font color="#7f7f7f"> </font></span><span style="font-size:small;color:rgb(127,127,127);font-family:Arial,sans-serif">|</span><span style="font-size:10pt;color:rgb(127,127,127);font-family:Arial,sans-serif"> </span><font color="#7f7f7f" face="Arial, sans-serif" style="font-size:small">Energy Modeling Team Manager</font><br>


</p><p><b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(127,127,127)">Integral Group </span></b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(127,127,127)">| 427 13th Street | Oakland CA USA 94612<br>


T <a href="tel:510.663.2070%20x235" value="+15106632070" target="_blank">510.663.2070 x235</a><br></span><span style="color:rgb(127,127,127);font-family:Arial,sans-serif;font-size:10pt">c <a href="tel:707.363.3954" value="+17073633954" target="_blank">707.363.3954</a></span></p>
<p><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(127,127,127)"><a href="http://www.integralgroup.com/" style="color:rgb(17,85,204)" target="_blank"><span style="color:rgb(127,127,127)">integralgroup.com</span></a> | <a href="mailto:nbulger@integralgroup.com" style="color:rgb(17,85,204)" target="_blank"><span style="color:rgb(127,127,127)">nbulger@integralgroup.com</span></a></span></p>


<p><span lang="EN-GB" style="font-size:6pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"> </span><b style="font-size:13px"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(176,188,34)">Trust</span></b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(51,51,51)"> </span><span style="font-size:12pt;font-family:Arial,sans-serif;color:rgb(176,188,34)">|</span><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(51,51,51)"> </span><b style="font-size:13px"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(118,118,98)">Nurture</span></b><b style="font-size:13px"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(51,51,51)"> </span></b><span style="font-size:12pt;font-family:Arial,sans-serif;color:rgb(51,51,51)">|</span><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(0,164,228)"> <b>Inspire</b></span></p>


<p><span style="color:rgb(176,188,34);font-family:Arial,sans-serif;font-size:8pt">Please consider the environment before printing this email.</span></p><p></p></div></div>
<br><br><div class="gmail_quote"><div><div class="h5">On Wed, Feb 5, 2014 at 1:34 PM, Sebastian Carrizo <span dir="ltr"><<a href="mailto:juan.carrizo@alumni.carleton.ca" target="_blank">juan.carrizo@alumni.carleton.ca</a>></span> wrote:<br>


</div></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div><div class="h5"><div dir="ltr">Thanks for the quick responses. After setting the parameters to match my design conditions I keep getting the error <div>


<i><br></i></div><div><i>Tower: Dummy CT on loop DEFAULT-CW is not needed.  No simulation will be performed.   </i></div>
<div><i><br></i></div><div>Any thoughts?</div></div><div><div><div class="gmail_extra"><br><br><div class="gmail_quote">On Wed, Feb 5, 2014 at 3:52 PM, Paul Riemer <span dir="ltr"><<a href="mailto:Paul.Riemer@dunhameng.com" target="_blank">Paul.Riemer@dunhameng.com</a>></span> wrote:<br>



<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div lang="EN-US" link="blue" vlink="purple"><div><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Some of these have an economizer functionality that can operate instead of or in series with the compressors.  I was excited about this once but the first pass showed it wouldn’t payoff for my project.  If your situation shows promise, you need a detailed model, and if an eQUEST waterside economizer will not give you the series functionality, then I wonder if you could model the modes as separate air cooled chillers in eQUEST with custom curves for each and staging based on outdoor air or seasonal dates.  Good luck.<u></u><u></u></span></p>



<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> <u></u><u></u></span></p><div><p class="MsoNormal" style="text-autospace:none"><b><span style="font-size:9.0pt;font-family:"Verdana","sans-serif";color:#5f574f">Paul Riemer, PE, LEED AP BD+C</span></b><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> <u></u><u></u></span></p>



<p class="MsoNormal"><b><span style="font-family:"Verdana","sans-serif";color:#c00000">DUNHAM</span></b><span style="font-size:11.0pt;font-family:"Verdana","sans-serif";color:#c00000"><u></u><u></u></span></p>



</div><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><div><div style="border:none;border-top:solid #b5c4df 1.0pt;padding:3.0pt 0in 0in 0in">



<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Bishop, Bill<br>



<b>Sent:</b> Wednesday, February 05, 2014 2:33 PM<br><b>To:</b> Sebastian Carrizo; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> Re: [Equest-users] Free cooling Chiller on eQuest<u></u><u></u></span></p>



</div></div><div><div><p class="MsoNormal"><u></u> <u></u></p><div><p class="MsoNormal">Sebastian,<u></u><u></u></p><p class="MsoNormal">It sounds like you’re talking about a water-side economizer, which can be modeled as a WATER-ECONOMIZER, one of the chiller types in eQUEST.<u></u><u></u></p>



<p class="MsoNormal">Regards,<u></u><u></u></p><p class="MsoNormal">Bill<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal"><b>William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP<u></u><u></u></b></p>



<table border="0" cellspacing="0" cellpadding="0" width="653" style="width:489.75pt"><tbody><tr><td width="462" style="width:346.5pt;padding:0in 0in 0in 0in"><p class="MsoNormal"><b>Senior Energy Engineer<u></u><u></u></b></p>



</td><td width="191" rowspan="6" style="width:143.25pt;padding:0in 0in 0in 0in"><p class="MsoNormal"><img width="123" height="83" src="cid:image001.jpg@01CF2280.584EC7F0" alt="webCertified_logo_colorRGB72DPI.jpg"><u></u><u></u></p>



</td></tr><tr><td width="462" valign="top" style="width:346.5pt;padding:0in 0in 0in 0in"><p class="MsoNormal"><u></u> <u></u></p></td></tr><tr><td width="462" nowrap valign="bottom" style="width:346.5pt;padding:0in 0in 0in 0in">



<p class="MsoNormal">134 South Fitzhugh Street                 Rochester, NY 14608<u></u><u></u></p></td></tr><tr><td width="462" valign="top" style="width:346.5pt;padding:0in 0in 0in 0in"><p class="MsoNormal"><b><i>T: <a href="tel:%28585%29%20698-1956" value="+15856981956" target="_blank">(585) 698-1956</a>              </i></b>          F: <a href="tel:%28585%29%20325-6005" value="+15853256005" target="_blank">(585) 325-6005</a><u></u><u></u></p>



</td></tr><tr><td width="462" valign="top" style="width:346.5pt;padding:0in 0in 0in 0in"><p class="MsoNormal"><a href="mailto:wbishop@pathfinder-ea.com" target="_blank">bbishop@pathfinder-ea.com</a>             <a href="http://www.pathfinder-ea.com/" target="_blank">www.pathfinder-ea.com</a><u></u><u></u></p>



</td></tr><tr><td width="462" valign="top" style="width:346.5pt;padding:0in 0in 0in 0in"><p class="MsoNormal"><img border="0" width="31" height="28" src="cid:image002.png@01CF2280.584EC7F0" alt="earth for signature">Sustainability – the forest AND the trees.<u></u><u></u></p>



</td></tr></tbody></table><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal"><b>From:</b> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Sebastian Carrizo<br>



<b>Sent:</b> Wednesday, February 05, 2014 3:15 PM<br><b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] Free cooling Chiller on eQuest<u></u><u></u></p>



<p class="MsoNormal"><u></u> <u></u></p><div><p class="MsoNormal">Hi all,<u></u><u></u></p><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">I'm trying to model a packaged air cooled/free cooling chiller in eQuest. I was hoping someone could shed some light as to how one would go about doing this.<u></u><u></u></p>



</div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">Regards,<u></u><u></u></p></div><div><p class="MsoNormal">Sebastian<br clear="all"><u></u><u></u></p><div><p class="MsoNormal"><u></u> <u></u></p>



</div><p class="MsoNormal">-- <u></u><u></u></p><div><blockquote style="margin-top:5.0pt;margin-bottom:5.0pt"><p class="MsoNormal"><b>Juan Sebastian Carrizo</b><u></u><u></u></p><p class="MsoNormal">M.Eng Sustainable Energy | B.Eng Industrial Engineering<u></u><u></u></p>



</blockquote><blockquote style="margin-top:5.0pt;margin-bottom:5.0pt"><p class="MsoNormal">(c) <a href="tel:647-225-2243" value="+16472252243" target="_blank">647-225-2243</a> | <a href="mailto:juan.carrizo@alumni.carleton.ca" target="_blank">juan.carrizo@alumni.carleton.ca</a><u></u><u></u></p>



</blockquote><div><p class="MsoNormal"><u></u> <u></u></p></div><p class="MsoNormal"><u></u> <u></u></p></div></div></div></div></div></div></div></div></blockquote></div><br><br clear="all"><div><br></div>-- <br><div dir="ltr">



<blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"><div style="text-align:left"><b>Juan Sebastian Carrizo</b></div><div style="text-align:left">M.Eng Sustainable Energy | B.Eng Industrial Engineering<br>


</div>
</blockquote><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px">(c) <a href="tel:647-225-2243" value="+16472252243" target="_blank">647-225-2243</a> | <a href="mailto:juan.carrizo@alumni.carleton.ca" target="_blank">juan.carrizo@alumni.carleton.ca</a><br>


</blockquote><div>
<br></div><br></div>
</div>
</div></div><br></div></div>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div></div>
</blockquote></div><br><br clear="all"><div><br></div>-- <br><div dir="ltr"><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"><div style="text-align:left"><b>Juan Sebastian Carrizo</b></div><div style="text-align:left">
M.Eng Sustainable Energy | B.Eng Industrial Engineering<br></div></blockquote><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px">(c) 647-225-2243 | <a href="mailto:juan.carrizo@alumni.carleton.ca" target="_blank">juan.carrizo@alumni.carleton.ca</a><br>
</blockquote><div><br></div><br></div>
</div>