    or adjust your cfm & related values by dividing by the altitude
    multiplier factor on input so they come out what you expect them to
    be.  i.e. 1000 cfm/1.09 = input, output = 1000 cfm.  you also need
    to check your kw outputs in the sv-a report(s) to make sure they're
    correct, if not divide the kw/cfm input by the altitude multiplier
    on input.<br>
    <br>
    On 1/29/14 7:04 AM, Lincoln Lam wrote:
    <blockquote cite="mid:001b01cf1cfb$0fb171d0$2f145570$@LS-Energy.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 14 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
span.EmailStyle18
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal">Tom,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">If you go to the Project & Site tab and
          right-click on Site Data > Properties, go to Altitude and
          make the value 0.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Lincoln<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Lincoln Lam<o:p></o:p></p>
        <p class="MsoNormal">CEM, CEA, LEED® AP<o:p></o:p></p>
        <p class="MsoNormal">Senior Energy Engineer<o:p></o:p></p>
        <p class="MsoNormal">L&S Energy Services, Inc.<o:p></o:p></p>
        <p class="MsoNormal">9 Regent Street, Unit 704<o:p></o:p></p>
        <p class="MsoNormal">Jersey City, NJ 07302<o:p></o:p></p>
        <p class="MsoNormal">(201) 484-7944<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">
                <a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
                [<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>] <b>On
                  Behalf Of </b>Tom Mickley<br>
                <b>Sent:</b> Wednesday, January 29, 2014 8:05 AM<br>
                <b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> [Equest-users] Design Supply Air CFM/OSA
                CFM<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">eQuesters,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Why does the design flow supply cfm and
          design ventilation OSA cfm in the summary tab of the system
          & zone air-side summary report differ from the user
          defined inputs I use in detailed data edit mode?  Is there a
          way to make it exact without having to lower the inputs for
          every system to get desired flow rates in the summary report? 
          Changing each system’s flow and making several simulations
          until I find the right cfm is too time consuming.  Does eQuest
          automatically account for duct leakage that would skew the
          numbers?  If so, how do I change it?  Thanks in advance!      <o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Thanks,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Tom Mickley<o:p></o:p></p>
        <p class="MsoNormal">Mechanical Engineer CEM<o:p></o:p></p>
        <p class="MsoNormal">The K Company<o:p></o:p></p>
        <p class="MsoNormal">Cell 330-760-3994<o:p></o:p></p>
        <p class="MsoNormal">Office 330-773-5125<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>