or adjust your cfm & related values by dividing by the altitude
multiplier factor on input so they come out what you expect them to
be. i.e. 1000 cfm/1.09 = input, output = 1000 cfm. you also need
to check your kw outputs in the sv-a report(s) to make sure they're
correct, if not divide the kw/cfm input by the altitude multiplier
on input.<br>
<br>
On 1/29/14 7:04 AM, Lincoln Lam wrote:
<blockquote cite="mid:001b01cf1cfb$0fb171d0$2f145570$@LS-Energy.com"
type="cite">
<meta http-equiv="Content-Type" content="text/html;
charset=ISO-8859-1">
<meta name="Generator" content="Microsoft Word 14 (filtered
medium)">
<style><!--
/* Font Definitions */
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Tahoma;
panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
span.EmailStyle17
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:windowtext;}
span.EmailStyle18
{mso-style-type:personal-reply;
font-family:"Calibri","sans-serif";
color:windowtext;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal">Tom,<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">If you go to the Project & Site tab and
right-click on Site Data > Properties, go to Altitude and
make the value 0.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Lincoln<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Lincoln Lam<o:p></o:p></p>
<p class="MsoNormal">CEM, CEA, LEED® AP<o:p></o:p></p>
<p class="MsoNormal">Senior Energy Engineer<o:p></o:p></p>
<p class="MsoNormal">L&S Energy Services, Inc.<o:p></o:p></p>
<p class="MsoNormal">9 Regent Street, Unit 704<o:p></o:p></p>
<p class="MsoNormal">Jersey City, NJ 07302<o:p></o:p></p>
<p class="MsoNormal">(201) 484-7944<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<div>
<div style="border:none;border-top:solid #B5C4DF
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">
<a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
[<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>] <b>On
Behalf Of </b>Tom Mickley<br>
<b>Sent:</b> Wednesday, January 29, 2014 8:05 AM<br>
<b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Design Supply Air CFM/OSA
CFM<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">eQuesters,<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Why does the design flow supply cfm and
design ventilation OSA cfm in the summary tab of the system
& zone air-side summary report differ from the user
defined inputs I use in detailed data edit mode? Is there a
way to make it exact without having to lower the inputs for
every system to get desired flow rates in the summary report?
Changing each system’s flow and making several simulations
until I find the right cfm is too time consuming. Does eQuest
automatically account for duct leakage that would skew the
numbers? If so, how do I change it? Thanks in advance! <o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Thanks,<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Tom Mickley<o:p></o:p></p>
<p class="MsoNormal">Mechanical Engineer CEM<o:p></o:p></p>
<p class="MsoNormal">The K Company<o:p></o:p></p>
<p class="MsoNormal">Cell 330-760-3994<o:p></o:p></p>
<p class="MsoNormal">Office 330-773-5125<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
</body>
</html>