<div dir="ltr"><div>This is an issue of altitude factor. eQuest considers default altitude factor according to the location. Please adjust your supply cfm accordingly.</div><div> </div><div>Gopi</div></div><div class="gmail_extra">
<br><br><div class="gmail_quote">On Wed, Jan 29, 2014 at 6:34 PM, Tom Mickley <span dir="ltr"><<a href="mailto:tmickley@thekcompany.com" target="_blank">tmickley@thekcompany.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div lang="EN-US" vlink="purple" link="blue"><div><p class="MsoNormal">eQuesters,<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">Why does the design flow supply cfm and design ventilation OSA cfm in the summary tab of the system & zone air-side summary report differ from the user defined inputs I use in detailed data edit mode? Is there a way to make it exact without having to lower the inputs for every system to get desired flow rates in the summary report? Changing each system’s flow and making several simulations until I find the right cfm is too time consuming. Does eQuest automatically account for duct leakage that would skew the numbers? If so, how do I change it? Thanks in advance! <u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">Thanks,<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">Tom Mickley<u></u><u></u></p><p class="MsoNormal">Mechanical Engineer CEM<u></u><u></u></p>
<p class="MsoNormal">The K Company<u></u><u></u></p><p class="MsoNormal">Cell 330-760-3994<u></u><u></u></p><p class="MsoNormal">Office 330-773-5125<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p></div></div><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>