<div dir="ltr"><div>I noticed a number of users on the list indicating they had trouble using Outdoor Reset for baseboard heat control.  I am currently looking into a building that has electric baseboards on (100% or nothing, no thermostatic control) when OAT < 50F and off when OAT >= 50F.  Also, if a compressor runs the baseboard is locked out.</div>
<div><br></div><div>Thermostatic control was underestimating the use of the baseboards, so I set it to Outdoor Reset with a schedule that turned the baseboards on at 100% from -20F to 70F.  Upon doing so, no electric heat outside of the reheat coils in the RTUs showed up on the electric meter.  I then setup an hourly report for a few of the RTUs, just to check (there's 16, I setup 4).  For each RTU, I asked for Temp of air leaving heat coil - hot deck temp (deg F), Total central heat coil output (Btu/hr), and Total baseboard heat coil output (Btu/hr).  As expected, the same value shows up for each hour that OAT <50F for the total baseboard heat coil output.</div>
<div><br></div><div>Regardless of which report I look at, it appears that with Outdoor Reset enabled there is no way to get the baseboard heat to show up on the meter, even though it is actually showing a load.</div><div>
<br></div><div>CSV and screen capture attached for backup purposes.  Can anyone think of something I am missing?</div><div><br clear="all"></div><div><div>Jeremy R. Poling, PE, LEED AP+BDC</div>