<div dir="ltr">Sounds to me like you're working in the wizard mode and somehow only have the .pd2 file in the directory. Try going back into the wizard (assuming you haven't done any detailed edits) and rebuilding the geometry. <div>
<br></div><div>I've only ever seen the error messages you're receiving when for some reason I had an incomplete .inp file.</div><div><br></div><div>Generally when posting random questions about your program not working it helps for you to attach the .pd2 and .inp files for others to take a look, otherwise all we can do is guess.</div>
<div><br></div><div>-Robby</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Thu, Dec 19, 2013 at 12:24 PM, Levin, Abel <span dir="ltr"><<a href="mailto:abel.levin@wyle.com" target="_blank">abel.levin@wyle.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Hi All,<br>
I keep getting this error whenever I try to Simulate Building Performance.<br>
"generateBDLInputFromWizardData()Error: Installing EEM run (Measure component)." Often leading to a crash.<br>
<br>
Which is then followed by....<br>
> INPUT DATA MUST INCLUDE AT LEAST ONE SPACE COMMAND (lLineNum = 1000000)<br>
><br>
> INPUT DATA MUST INCLUDE AT LEAST ONE SYSTEM COMMAND (lLineNum = 1000000)<br>
><br>
> INPUT DATA MUST INCLUDE AT LEAST ONE ZONE COMMAND (lLineNum = 1000000)<br>
<br>
Ive run the model for a month before and then this started happening just recently after I decided to "save as" into a new folder because the original project folder was getting cluttered. However, it now happens to all versions of the model.<br>
<br>
Has anyone encountered this? Maybe saving the file outside of the equest projects directory did it?<br>
<br>
Thanks!<br>
<br>
Abel<br>
<a href="mailto:Abel.levin@wyle.com">Abel.levin@wyle.com</a><br>
<br>
<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</blockquote></div><br></div>