<div dir="ltr">Robby,<div>Sorry about that, for some reason your original message didn't make it into my inbox, but I found it in the archives. Capitalizing the global parameter seemed to do the trick.  </div><div><br>
</div><div>Thanks for the tip!</div><div><br></div><div>John</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Thu, Dec 12, 2013 at 9:51 AM, Robby Oylear <span dir="ltr"><<a href="mailto:robbyoylear@gmail.com" target="_blank">robbyoylear@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">Did you try my suggestion?  Capitalizing your global parameter fixing your issue.</div><div class="gmail_extra">
<br><br><div class="gmail_quote"><div><div class="h5">On Thu, Dec 12, 2013 at 8:23 AM, J R <span dir="ltr"><<a href="mailto:john.reed.other@gmail.com" target="_blank">john.reed.other@gmail.com</a>></span> wrote:<br>

</div></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div><div class="h5"><div dir="ltr">Hi David,<div>Thanks for the quick response.  I reset my global parameter to numeric, and entered the input expression as you specified, but I'm now getting the following error message:</div>

<div>"Expression Parsing Error: Invalid function name 'SYSTEM' 5"</div>
<div><br></div><div>Any thoughts?</div><div><br></div><div>Thanks,</div><div><br></div><div>John</div></div><div><div><div class="gmail_extra"><br><br><div class="gmail_quote">On Wed, Dec 11, 2013 at 2:29 PM, David Griffin <span dir="ltr"><<a href="mailto:dgriffin@etcgrp.com" target="_blank">dgriffin@etcgrp.com</a>></span> wrote:<br>


<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">





<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">John,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">Try using an expression like the following which uses a ‘numeric’ global parameter rather than a ‘symbol’.<u></u><u></u></span></p>



<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">if(#PA("Enthalpy Wheel On/Off ")=1)<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">then<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">#SI("YES","SYSTEM","RECOVER-EXHAUST")<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">else<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">#SI("NO","SYSTEM","RECOVER-EXHAUST")<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">endif<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">This expression is a work around to some issues I’ve found in eQuest using ‘symbol’ global parameters. Just set the global parameter to 1 and change it to anything
 else in the parametric run to change the value or vice versa. Let me know how it goes.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">Thanks,<u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d"><u></u> <u></u></span></b></p>
<p class="MsoNormal" style="margin-left:4.5pt"><b><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">David W. Griffin II<u></u><u></u></span></b></p>
<p class="MsoNormal" style="margin-left:4.5pt"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">Energy Analyst<u></u><u></u></span></p>
<p class="MsoNormal" style="margin-left:4.5pt"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">ETC Group, LLC<u></u><u></u></span></p>
<p class="MsoNormal" style="margin-left:4.5pt"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d"><a href="tel:801-278-1927%20x%20128" value="+18012781927" target="_blank">801-278-1927 x 128</a><u></u><u></u></span></p>



<p class="MsoNormal" style="margin-left:4.5pt"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d">Cell <a href="tel:480-736-2945" value="+14807362945" target="_blank">480-736-2945</a><u></u><u></u></span></p>



<p class="MsoNormal" style="margin-left:4.5pt"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d"><a href="mailto:dgriffin@etcgrp.com" target="_blank">dgriffin@etcgrp.com</a><u></u><u></u></span></p>



<p class="MsoNormal" style="margin-left:4.5pt"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d"><a href="http://www.etcgrp.com" target="_blank">www.etcgrp.com</a><u></u><u></u></span></p>



<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#17365d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d"><img width="112" height="27" alt="Copy of ETC_LogoOnly2_rgb_sm.png"></span><span style="font-size:6.0pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p>



<p class="MsoNormal" style="margin-left:4.5pt"><b><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#17365d">Energy Engineering for a Sustainable Future</span></b><span style="font-size:6.0pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p>



<p class="MsoNormal" style="margin-left:4.5pt"><span style="font-size:6.0pt;font-family:"Arial","sans-serif"">1997 South 1100 East, Salt Lake City, UT 84106-4471
<u></u><u></u></span></p>
<p class="MsoNormal" style="margin-right:0in;margin-bottom:12.0pt;margin-left:4.5pt">
<span style="font-size:6.0pt;font-family:"Arial","sans-serif"">-------------------------------------------------------------------------------------------------------------------
<br>
CONFIDENTIALITY NOTICE This e-mail transmission, and any documents, files or previous e-mail messages attached to it may contain confidential information that is legally privileged.  If you are not the intended recipient or the person responsible for delivering
 it to the intended recipient, you are hereby notified that any disclosure, copying, distribution or use of any of the information contained in or attached to this transmission is strictly prohibited.  If you have received this transmission in error, please
 immediately notify us by telephone at <a href="tel:%28801%29%20278-1927" value="+18012781927" target="_blank">(801) 278-1927</a> and destroy the original transmission and its attachments without reading them. Thank you.<u></u><u></u></span></p>



</div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Arial","sans-serif";color:#17365d"><u></u> <u></u></span></p>
<div style="border:none;border-top:solid #b5c4df 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> J R [mailto:<a href="mailto:john.reed.other@gmail.com" target="_blank">john.reed.other@gmail.com</a>]
<br>
<b>Sent:</b> Wednesday, December 11, 2013 10:07 AM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Changing words with global parameters / parametric runs?<u></u><u></u></span></p>
</div><div><div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal">Hi Everybody,<u></u><u></u></p>
<div>
<p class="MsoNormal">First off, as a relatively new eQUEST user, the past discussions in the archives has been immensely helpful in troubleshooting issues, so thanks to everybody for responding to questions from eQUEST rookies like myself.  Now, for the new
 questions:<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">I've developed a model in detailed mode that I would like to make some parametric runs for to run alternative scenarios. For numeric inputs, I haven't run into any issues, but I'm wondering if there's a way to change words using global
 parameters too. Specifically, I'd like to add an enthalpy wheel in the parametric run by adjusting the yes/no option under my AHU's heat recovery 1 tab: "ERV device installed" Yes/No dropdown. These are the steps I've taken.<u></u><u></u></p>



</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<ul type="disc">
<li class="MsoNormal">
Create new global parameter: "Enthalpy Wheel On/Off"<u></u><u></u></li></ul>
<ul type="disc">
<ul type="circle">
<li class="MsoNormal">
Parameter type: "New Symbol"<u></u><u></u></li><li class="MsoNormal">
Parameter value: "No"<u></u><u></u></li></ul>
</ul>
<ul type="disc">
<li class="MsoNormal">
Right click device Installed dropdown: User Input Expression - I tried two different expressions:<u></u><u></u></li></ul>
<ul type="disc">
<ul type="circle">
<li class="MsoNormal">
#SI(#PA("Enthalpy Wheel On/Off"),"SYSTEM","RECOVER-EXHAUST")<u></u><u></u></li></ul>
</ul>
<ul type="disc">
<ul type="circle">
<ul type="square">
<li class="MsoNormal">
Error Message: Expression Evaluation Error: BDL Symbol 'No' not found<u></u><u></u></li></ul>
</ul>
</ul>
<ul type="disc">
<ul type="circle">
<li class="MsoNormal">
#parameter("Enthalpy Wheel On/Off")<u></u><u></u></li></ul>
</ul>
<ul type="disc">
<ul type="circle">
<ul type="square">
<li class="MsoNormal">
Invalid symbol assignment (symbol table index = 0)<u></u><u></u></li></ul>
</ul>
</ul>
<ul type="disc">
<li class="MsoNormal">
If the above error were solved, my next step would be to create a parametric run, component type: symbolic global parameter, and change the value to "yes".<u></u><u></u></li></ul>
<p class="MsoNormal">I have no doubt that I'm using the wrong language for what I'm trying to accomplish, but don't know what other approach to take.  Any advice would be greatly appreciated.<u></u><u></u></p>



</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">Also, on a more general note, does anybody have a good resource they could share that is more or less an eQUEST detailed mode guide? I've found the intro, wizard, and DOE2 guides on the eQUEST site, but it seems like there is a lot of functionality
 with the program in detailed mode that isn't really explained anywhere.<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">Thanks in advance for your help!<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">John<u></u><u></u></p>
</div>
</div>
</div></div></div>
</div>

</blockquote></div><br></div>
</div></div><br></div></div>_______________________________________________<br>