<div dir="ltr">I'm not sure I follow your interpretation on G3.1.3.14.  The supply air temperature setpoint is constant at the design condition regardless of whether you reset airflow or temperature first.  At the design condition there will be no reset occurring because you're by definition, at design.  I've always interpreted that whole section of G3.1.3.14 to be referring to the terminal unit fans only.  <div>
<br></div><div>TEMPERATURE-FIRST makes the most sense to me for accomplishing G3.1.3.12, but I may be biased as in a marine climate resetting temperature up increases economizer hours dramatically.</div><div><br></div><div>
-Robby</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Thu, Nov 21, 2013 at 10:28 AM, Bishop, Bill <span dir="ltr"><<a href="mailto:bbishop@pathfinder-ea.com" target="_blank">bbishop@pathfinder-ea.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">





<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="color:#1f497d">I also created an input file template for System 6 which could be used for System 8 with some modification. Comments/mods are welcomed.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">$ *********************************************************<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">$ **                                                     **<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">$ **                Performance Curves                   **<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">$ **                                                     **<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">$ *********************************************************<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">"G3.1.3.15 VAV Fan Curve fPLR" = CURVE-FIT      
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   TYPE             = CUBIC<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   INPUT-TYPE       = COEFFICIENTS<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   COEFFICIENTS     = ( 0.0013, 0.147, 0.9506, -0.0998 )<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   ..<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">$ *********************************************************<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">$ **                                                     **<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">$ **               HVAC Systems / Zones                  **<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">$ **                                                     **<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">$ *********************************************************<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">SET-DEFAULT FOR ZONE            <u></u>
<u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   TYPE = CONDITIONED<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   MIN-FLOW-RATIO   = 0.3           $ Per G3.1.3.14<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   ZONE-FAN-KW/FLOW = 0.00035       $ Per G3.1.3.14<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   ZONE-FAN-RATIO   = 0.5           $ Per G3.1.3.14<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   TERMINAL-TYPE    = PARALLEL-PIU  $ For all zones served by Sys 6 or Sys 8<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   ..<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">SET-DEFAULT FOR SYSTEM          <u></u>
<u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   TYPE             = PIU           $ For Baseline System 6 and System 8<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   HEAT-SOURCE      = ELECTRIC      $ Per Table G3.1.1B and User's Manual p.G-23<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   ZONE-HEAT-SOURCE = ELECTRIC      $ Per Table G3.1.1B and User's Manual p.G-23<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   HEAT-SIZING-RATI = 1.25          $ Per G3.1.2.2<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   COOL-SIZING-RATI = 1.15          $ Per G3.1.2.2<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   COOL-SOURCE      = ELEC-DX           $ Per Table G3.1.1B<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   MAX-SUPPLY-T     = 92            $ Per G3.1.2.8 (20F above room heat T-Stat<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   HEAT-SET-T       = 62            $ = COOL-MAX-RESET-T plus 1F<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   MIN-SUPPLY-T     = 56            $ Per G3.1.2.8 (20F below room cool T-Stat<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   COOL-CONTROL     = WARMEST       $ Per G3.1.3.12<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   ECONO-LIMIT-T    = 70            $ Per G3.1.2.7 and Table G3.1.2.6B by climate zone<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   ECONO-LOCKOUT    = YES           $ (Seems like a reasonable baseline default)<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   COOL-MIN-RESET-T = 56            $ = MIN-SUPPLY-T<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   RESET-PRIORITY   = AIRFLOW-FIRST $ Per G3.1.3.12 and G3.1.3.14<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   COOL-MAX-RESET-T = 61            $ Per G3.1.3.12 (5F above MIN-SUPPLY-T)<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   OA-CONTROL       = OA-TEMP       $ Per G3.1.2.6 and Table G3.1.2.6A<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   FAN-CONTROL      = FAN-EIR-FPLR                    $ Per G3.1.3.15<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   NIGHT-CYCLE-CTRL = CYCLE-ON-ANY                    $ Per G3.1.2.4<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   FAN-EIR-FPLR     = "G3.1.3.15 VAV Fan Curve fPLR"  $ Per G3.1.3.15<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   REHEAT-DELTA-T   = 36            $ = MAX-SUPPLY-T minus MIN-SUPPLY-T<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">   ..<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal"><span style="color:#1f497d">   $ Bill<u></u><u></u></span></p>
</div>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<div>
<div style="border:none;border-top:solid #b5c4df 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Bishop, Bill<br>
<b>Sent:</b> Thursday, November 21, 2013 1:14 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Appendix G Baseline Systems 6 and 8 - supply air temperature controls?<u></u><u></u></span></p>
</div>
</div><div><div class="h5">
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">ASHRAE Standard 90.1, G3.1.3.12 requires cooling supply air temperature reset for Systems 5 through 8.<u></u><u></u></p>
<p class="MsoNormal">G3.1.3.14 requires “supply air temperature setpoint shall be constant at the design condition” for Systems 6 and 8.<u></u><u></u></p>
<p class="MsoNormal">How should we interpret this and model it in eQUEST (for Systems 6 and 8)?<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">If the “design condition” in G3.1.3.14 means “peak design flow rate”, I suggest the following cooling control settings:<u></u><u></u></p>
<p style="margin-left:.75in">
<u></u><span>-<span style="font:7.0pt "Times New Roman"">         
</span></span><u></u>   COOL-CONTROL     = WARMEST<u></u><u></u></p>
<p style="margin-left:.75in">
<u></u><span>-<span style="font:7.0pt "Times New Roman"">         
</span></span><u></u>   COOL-MIN-RESET-T = 56                    $ (assumes 76F cooling T-stat; 56F MIN-SUPPLY-T for 20F difference per G3.1.2.8)<u></u><u></u></p>
<p style="margin-left:.75in">
<u></u><span>-<span style="font:7.0pt "Times New Roman"">         
</span></span><u></u>   RESET-PRIORITY   = AIRFLOW-FIRST<u></u><u></u></p>
<p style="margin-left:.75in">
<u></u><span>-<span style="font:7.0pt "Times New Roman"">         
</span></span><u></u>   COOL-MAX-RESET-T = 61                   $ (5F reset per G3.1.3.12; assumes 76F cooling T-stat)<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Using a RESET-PRIORITY of “TEMP-FIRST” resets the supply air temperature
<i>before</i> the airflow, which does not satisfy the G3.1.3.14 requirement.<u></u><u></u></p>
<p class="MsoNormal">Using a RESET-PRIORITY of “TEMP-FIRST” or “SIMULTANEOUS” does not satisfy the G3.1.3.12 requirement, since temperature is reset well  before minimum cooling load conditions are reached.<u></u><u></u></p>

<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Does anyone have an alternative/additional suggestion or interpretation?<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Thanks,<u></u><u></u></p>
<p class="MsoNormal">Bill<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Franklin Gothic Medium","sans-serif"">William Bishop, PE, BEMP, BEAP, LEED AP
</span></b><b><span style="font-size:10.0pt;font-family:"Franklin Gothic Medium","sans-serif";color:#006600">|</span></b><b><span style="font-size:10.0pt;font-family:"Franklin Gothic Medium","sans-serif""> Pathfinder Engineers & Architects LLP<u></u><u></u></span></b></p>

<table border="0" cellspacing="0" cellpadding="0" width="522" style="width:391.85pt;border-collapse:collapse">
<tbody>
<tr style="height:.2in">
<td width="370" style="width:277.4pt;padding:0in 5.4pt 0in 5.4pt;height:.2in">
<p class="MsoNormal"><b><span style="font-size:9.0pt;font-family:"Arial","sans-serif"">Senior Energy Engineer<u></u><u></u></span></b></p>
</td>
<td width="153" rowspan="6" style="width:114.45pt;padding:0in 5.4pt 0in 5.4pt;height:.2in">
<p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Arial","sans-serif""><img width="123" height="83" src="cid:image001.jpg@01CEE6BD.8D212490" alt="webCertified_logo_colorRGB72DPI.jpg"><u></u><u></u></span></p>

</td>
</tr>
<tr style="height:4.9pt">
<td width="370" valign="top" style="width:277.4pt;padding:0in 5.4pt 0in 5.4pt;height:4.9pt">
<p class="MsoNormal"><span style="font-size:5.0pt;font-family:"Arial","sans-serif""><u></u> <u></u></span></p>
</td>
</tr>
<tr style="height:10.5pt">
<td width="370" nowrap valign="bottom" style="width:277.4pt;padding:0in 5.4pt 0in 5.4pt;height:10.5pt">
<p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#1f497d">134 South Fitzhugh Street</span><span style="font-size:9.0pt;font-family:"Times New Roman","serif";color:#1f497d">                
</span><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#1f497d">Rochester, NY 14608<u></u><u></u></span></p>
</td>
</tr>
<tr style="height:13.3pt">
<td width="370" valign="top" style="width:277.4pt;padding:0in 5.4pt 0in 5.4pt;height:13.3pt">
<p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#1f497d">T: <a href="tel:%28585%29%20325-6004" value="+15853256004" target="_blank">(585) 325-6004</a>
</span><span style="font-size:9.0pt;font-family:"Arial","sans-serif"">Ext. 114</span><span style="font-size:12.0pt;font-family:"Times New Roman","serif";color:#1f497d">           
</span><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#1f497d">F: <a href="tel:%28585%29%20325-6005" value="+15853256005" target="_blank">(585) 325-6005</a></span><span style="font-size:9.0pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p>

</td>
</tr>
<tr style="height:10.5pt">
<td width="370" valign="top" style="width:277.4pt;padding:0in 5.4pt 0in 5.4pt;height:10.5pt">
<p class="MsoNormal"><a href="mailto:wbishop@pathfinder-ea.com" target="_blank"><span style="font-size:9.0pt;font-family:"Arial","sans-serif"">bbishop@pathfinder-ea.com</span></a><span style="font-size:9.0pt;font-family:"Arial","sans-serif"">          
</span><a href="http://www.pathfinder-ea.com/" target="_blank"><span style="font-size:9.0pt;font-family:"Arial","sans-serif"">www.pathfinder-ea.com</span></a><span style="font-size:9.0pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p>

</td>
</tr>
<tr style="height:26.3pt">
<td width="370" valign="top" style="width:277.4pt;padding:0in 5.4pt 0in 5.4pt;height:26.3pt">
<p class="MsoNormal"><span style="font-size:14.0pt;font-family:Webdings;color:green">P</span><span style="font-size:14.0pt;font-family:"Times New Roman","serif";color:green">  
</span><span style="font-size:7.5pt;font-family:"Times New Roman","serif";color:green">Sustainability – the forest AND the trees.</span><span style="font-size:18.0pt;font-family:Webdings;color:green">
</span><span style="font-size:14.0pt;font-family:Webdings;color:green">P</span><span style="font-size:14.0pt;color:green">   </span><span style="font-size:14.0pt;color:green">   </span><span style="font-size:14.0pt;font-family:Webdings;color:green">
</span><span style="color:#1f497d"><u></u><u></u></span></p>
</td>
</tr>
</tbody>
</table>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
</div></div></div>
</div>

<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>