<div dir="ltr"><div>I see. Thanks for this information. When I model the cooling season separately in another file with economizer and without energy recovery, then I am avoiding having to use these inefficient motors, which saves energy. Can we say that modeling cooling season with no energy recovery is a good idea then? Can you think of any problem that might arise with this approach? Would you please let me know?</div>
<div> </div><div>Thank you very much,</div><div>Best Regards,</div><div> </div><div>Simge Andolsun, PhD.</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Thu, Nov 14, 2013 at 3:13 PM, Patrick J. O'Leary, Jr. <span dir="ltr"><<a href="mailto:poleary1969@gmail.com" target="_blank">poleary1969@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    a delta t of "0" will make it run all of the time.  i.e. erv supply
    fan motor, exhaust motor, and wheel motor.  and these motors aren't
    typically very efficient.<div><div class="h5"><br>
    <br>
    On 11/14/13 1:36 PM, Simge Andolsun wrote:
    <blockquote type="cite">
      <div dir="ltr">
        <div>Dear Patrick,</div>
        <div> </div>
        <div>Thanks for your response. I actually had set my schedule to
          OA Exhaust DT when get these results. The delta T I used was
          "0" so that the system would benefit from every bit of
          temperature difference. </div>
        <div> </div>
        <div>Thanks,</div>
        <div>Best Regards,</div>
        <div>S. Andolsun</div>
      </div>
      <div class="gmail_extra"><br>
        <br>
        <div class="gmail_quote">On Thu, Nov 14, 2013 at 2:32 PM,
          Patrick J. O'Leary, Jr. <span dir="ltr"><<a href="mailto:poleary1969@gmail.com" target="_blank">poleary1969@gmail.com</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;padding-left:1ex;border-left-color:rgb(204,204,204);border-left-width:1px;border-left-style:solid">
            <div text="#000000" bgcolor="#FFFFFF"> how are you
              controlling the erv/energy recovery?  the default is for
              it to run when the supply fan runs.  this will cost you
              more in energy than it saves.  set the control method
              based on a delta T between the exhaust air and the outside
              air you'll see the savings in cooling mode.  in my climate
              zone (2b/southern arizona) the best delta t i found is 27
              d f.<br>
              <br>
              once you set up the erv to run based on a delta t you can
              set up some parametric runs (set up one & then copy
              & rename it in the .inp file to save time) to try
              different delta t values without having to change each
              hvac unit every time you want to try a different delta t.
              <div>
                <div><br>
                  <br>
                  On 11/14/13 12:30 PM, Simge Andolsun wrote: </div>
              </div>
              <blockquote type="cite">
                <div>
                  <div>
                    <div dir="ltr">
                      <div>Dear eQuest users,</div>
                      <div> </div>
                      <div>In my models, I realized that using energy
                        recovery in the cooling season always gives
                        higher cooling energy consumption results than
                        turning off the energy recovery and using
                        economizer only instead. I tried using OA
                        Heat/Cool with Bypass OA or Bypass
                        Exhaust thinking that such configuration would
                        capture the best benefit of energy recovery and
                        let the outside/exhaust air bypass when
                        economizer is more beneficial. Then, I read in
                        the eQuest manuals that this configuration
                        still lets the energy recovery run when it is
                        not beneficial in warm months and just opens up
                        the economizer dampers to compensate for
                        the unnecessary heating of the outside air. So,
                        the loss caused by the energy recovery eats up
                        the benefit that is provided with the
                        economizer.</div>
                      <div> </div>
                      <div>Thus, I thought, may be, I should use two
                        separate files to maximize the benefit from both
                        the economizer and the energy recovery. The
                        first file would be for heating (with OA
                        Heating) where the energy recovery would be on
                        whenever it can heat the outside air. Then the
                        second file would be for cooling where there
                        would be no energy recovery but the economizer
                        would be available whenever the outside air is
                        favorable for cooling. Finally, I would get
                        heating energy consumption from the heating file
                        and the cooling energy consumption from the
                        cooling file. </div>
                      <div> </div>
                      <div>The only thing that stops me from following
                        this approach is that I am wondering whether
                        there was a logical reason why bypass
                        configurations of eQuest give higher cooling
                        energy consumption than the economizer only
                        case. Shouldn't they be giving exactly the same
                        cooling energy consumption? Is it because part
                        of the outside/exhaust air is being bypassed in
                        the bypass configurations instead of fully? or
                        may it be because it is known that setting the
                        energy recovery and economizer for the best
                        benefit is pretty hard in reality and that's
                        why it was assumed that it would not
                        function ideally? Or, is there a completely
                        different reason that I do not know?</div>
                      <div> </div>
                      <div>Would you please help me with this question?</div>
                      <div>I'd appreciate it very much.</div>
                      <div> </div>
                      <div>Thanks,</div>
                      <div>Best Regards,</div>
                      <div>S. Andolsun, PhD</div>
                    </div>
                    <br>
                    <fieldset></fieldset>
                    <br>
                  </div>
                </div>
                <pre>_______________________________________________
Equest-users mailing list
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
              </blockquote>
              <br>
            </div>
          </blockquote>
        </div>
        <br>
      </div>
    </blockquote>
    <br>
  </div></div></div>

</blockquote></div><br></div>