<div dir="ltr"><div>Dear Patrick,</div><div> </div><div>Thanks for your response. I actually had set my schedule to OA Exhaust DT when get these results. The delta T I used was "0" so that the system would benefit from every bit of temperature difference. </div>
<div> </div><div>Thanks,</div><div>Best Regards,</div><div>S. Andolsun</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Thu, Nov 14, 2013 at 2:32 PM, Patrick J. O'Leary, Jr. <span dir="ltr"><<a href="mailto:poleary1969@gmail.com" target="_blank">poleary1969@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    how are you controlling the erv/energy recovery?  the default is for
    it to run when the supply fan runs.  this will cost you more in
    energy than it saves.  set the control method based on a delta T
    between the exhaust air and the outside air you'll see the savings
    in cooling mode.  in my climate zone (2b/southern arizona) the best
    delta t i found is 27 d f.<br>
    <br>
    once you set up the erv to run based on a delta t you can set up
    some parametric runs (set up one & then copy & rename it in
    the .inp file to save time) to try different delta t values without
    having to change each hvac unit every time you want to try a
    different delta t.<div><div class="h5"><br>
    <br>
    On 11/14/13 12:30 PM, Simge Andolsun wrote:
    </div></div><blockquote type="cite"><div><div class="h5">
      <div dir="ltr">
        <div>Dear eQuest users,</div>
        <div> </div>
        <div>In my models, I realized that using energy recovery in the
          cooling season always gives higher cooling energy consumption
          results than turning off the energy recovery and using
          economizer only instead. I tried using OA Heat/Cool with
          Bypass OA or Bypass Exhaust thinking that such configuration
          would capture the best benefit of energy recovery and let the
          outside/exhaust air bypass when economizer is more beneficial.
          Then, I read in the eQuest manuals that this configuration
          still lets the energy recovery run when it is not beneficial
          in warm months and just opens up the economizer dampers to
          compensate for the unnecessary heating of the outside air. So,
          the loss caused by the energy recovery eats up the benefit
          that is provided with the economizer.</div>
        <div> </div>
        <div>Thus, I thought, may be, I should use two separate files to
          maximize the benefit from both the economizer and the energy
          recovery. The first file would be for heating (with OA
          Heating) where the energy recovery would be on whenever it can
          heat the outside air. Then the second file would be for
          cooling where there would be no energy recovery but the
          economizer would be available whenever the outside air is
          favorable for cooling. Finally, I would get heating energy
          consumption from the heating file and the cooling energy
          consumption from the cooling file. </div>
        <div> </div>
        <div>The only thing that stops me from following this approach
          is that I am wondering whether there was a logical reason why
          bypass configurations of eQuest give higher cooling energy
          consumption than the economizer only case. Shouldn't they be
          giving exactly the same cooling energy consumption? Is it
          because part of the outside/exhaust air is being bypassed in
          the bypass configurations instead of fully? or may it be
          because it is known that setting the energy recovery and
          economizer for the best benefit is pretty hard in reality and
          that's why it was assumed that it would not
          function ideally? Or, is there a completely different reason
          that I do not know?</div>
        <div> </div>
        <div>Would you please help me with this question?</div>
        <div>I'd appreciate it very much.</div>
        <div> </div>
        <div>Thanks,</div>
        <div>Best Regards,</div>
        <div>S. Andolsun, PhD</div>
      </div>
      <br>
      <fieldset></fieldset>
      <br>
      </div></div><pre>_______________________________________________
Equest-users mailing list
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </div>

</blockquote></div><br></div>