<div dir="ltr"><div><div><div><div><div>Some more references<br><br></div>1. See attached " A Bridge too far' from the ASHRAE Journal, Oct 2007. (This is freely available on the internet)<br><br></div>2. Also read the ASHRAE Journal July 2012 issue  <span><img alt="" src="https://www.ashrae.org/Image%20Library/Unassigned/pdf_icon.png?code=8517e669-8d75-4897-a8c5-2ca99ef62a65"> <a href="https://www.ashrae.org/File%20Library/docLib/Journal%20Documents/2012July/060-068_buildingsciences.pdf">Thermal Bridge Redux</a>.
            <em>Joseph W. Lstiburek.</em> P. 60. July. (Will require ASHRAE login info)<br><br></span></div><div><span>3. There was a presentation in the 2012 ASHRAE Energy Modeling Conference Atlanta that detailed out the impact of extended slabs and the effective R-values. Although I do not have details of that presentation, maybe someone does.<br>
</span></div><div><span><br></span></div><span>Regards<br></span></div><span><br></span></div><span>Ramya Shivkumar<br></span></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Mon, Nov 4, 2013 at 4:55 PM, Mike Hupel <span dir="ltr"><<a href="mailto:mhupel@aegiseng.ca" target="_blank">mhupel@aegiseng.ca</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div link="blue" vlink="purple" lang="EN-CA"><div><p class="MsoNormal"><span style="color:#1f497d">Great report ..... thanks.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p><div><p class="MsoNormal"><b><span style="color:#1f497d"><u></u> <u></u></span></b></p><p class="MsoNormal"><b><span style="font-size:12.0pt;font-family:"Arial Narrow","sans-serif";color:#1f497d">Michael Hupel</span></b><span style="font-size:8.0pt;font-family:"Arial Narrow","sans-serif";color:#1f497d">, B.Tech, CEM, LEED</span><span style="font-size:8.0pt;font-family:"Arial Narrow","sans-serif";color:#1f497d">®</span><span style="font-size:8.0pt;font-family:"Arial Narrow","sans-serif";color:#1f497d">AP</span><span style="color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:8.0pt;font-family:"Arial Narrow","sans-serif";color:#1f497d">Senior Mechanical Designer<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial Narrow","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><i><span style="font-size:12.0pt;font-family:"Arial Narrow","sans-serif";color:#002060">Aegis Engineering Inc.<u></u><u></u></span></i></b></p><p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Arial Narrow","sans-serif";color:#1f497d">56 Pennsylvania Ave. Suite 18<u></u><u></u></span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Arial Narrow","sans-serif";color:#1f497d">Concord, ON L4K 3V9<u></u><u></u></span></b></p><p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Arial Narrow","sans-serif";color:#1f497d"><a href="tel:%28905%29%20761-1264%20ext.%2024" value="+19057611264" target="_blank">(905) 761-1264 ext. 24</a><u></u><u></u></span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Arial Narrow","sans-serif";color:#1f497d"><a href="tel:%28905%29%20761-6949" value="+19057616949" target="_blank">(905) 761-6949</a> fax<u></u><u></u></span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Arial Narrow","sans-serif";color:#1f497d"><a href="tel:%28647%29%20702-3316" value="+16477023316" target="_blank">(647) 702-3316</a> cell<u></u><u></u></span></b></p>
<p class="MsoNormal"><span style="font-size:10.0pt;color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:18.0pt;font-family:Webdings;color:#1f497d">P</span><span style="font-size:7.5pt;color:#1f497d"> </span><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d">P</span><span style="font-size:10.0pt;color:#1f497d">lease don't print this e-mail unless you really need to.<u></u><u></u></span></p>
<p class="MsoNormal"><b><i><span style="font-size:14.0pt;color:#002060"><u></u> <u></u></span></i></b></p><p class="MsoNormal"><span style="font-size:8.0pt;font-family:"Times New Roman","serif";color:#1f497d" lang="EN-US">This message may contain information that is confidential and/or protected by law.  If the reader of this message is not the intended recipient, you are hereby notified that any dissemination, distribution, copying or communication of this message is strictly prohibited.  If you have received this communication in error, please contact the sender immediately and delete the message.  Please note that although we will take all commercially reasonable efforts to prevent viruses from being transmitted from our systems, it is the responsibility of the recipient to check for and prevent adverse action by viruses on its own systems.</span><span style="font-size:8.0pt;color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:8.0pt;color:#1f497d"><u></u> <u></u></span></p></div><p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p><div><div style="border:none;border-top:solid #b5c4df 1.0pt;padding:3.0pt 0cm 0cm 0cm">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"" lang="EN-US">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"" lang="EN-US"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Bishop, Bill<br>
<b>Sent:</b> November-04-13 4:42 PM<br><b>To:</b> David Griffin; 'Coleman, Kevin'; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a></span></p><div><div class="h5">
<br><b>Subject:</b> Re: [Equest-users] Slab extending through wall<u></u><u></u></div></div><p></p></div></div><div><div class="h5"><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal"><span style="color:#1f497d" lang="EN-US">Here’s a timely report on effective R-values of assemblies with slab/balcony thermal bridges:<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d" lang="EN-US"><a href="http://www.rdhbe.com/database/files/library/Balcony_and_Slab_Edge_Thermal_Bridges___1___R_values_and_Energy_Code_Canada__Sept_24_13.pdf" target="_blank">The Importance of Slab Edge and Balcony Thermal Bridges</a><u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d" lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span style="color:#1f497d" lang="EN-US">Regards,<u></u><u></u></span></p><p class="MsoNormal"><span style="color:#1f497d" lang="EN-US">Bill<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d" lang="EN-US"><u></u> <u></u></span></p><div><p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Franklin Gothic Medium","sans-serif"" lang="EN-US">William Bishop, PE, BEMP, BEAP, LEED AP </span></b><b><span style="font-size:10.0pt;font-family:"Franklin Gothic Medium","sans-serif";color:#006600" lang="EN-US">|</span></b><b><span style="font-size:10.0pt;font-family:"Franklin Gothic Medium","sans-serif"" lang="EN-US"> Pathfinder Engineers & Architects LLP<u></u><u></u></span></b></p>
</div><table style="width:391.85pt;border-collapse:collapse" border="0" cellpadding="0" cellspacing="0" width="653"><tbody><tr style="height:14.4pt"><td style="width:277.4pt;padding:0cm 5.4pt 0cm 5.4pt;height:14.4pt" width="462">
<p class="MsoNormal"><b><span style="font-size:9.0pt;font-family:"Arial","sans-serif"">Senior Energy Engineer<u></u><u></u></span></b></p></td><td rowspan="6" style="width:114.45pt;padding:0cm 5.4pt 0cm 5.4pt;height:14.4pt" width="191">
<p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Arial","sans-serif""><img alt="webCertified_logo_colorRGB72DPI.jpg" height="83" border="0" width="123"><u></u><u></u></span></p></td></tr>
<tr style="height:4.9pt"><td style="width:277.4pt;padding:0cm 5.4pt 0cm 5.4pt;height:4.9pt" valign="top" width="462"><p class="MsoNormal"><span style="font-size:5.0pt;font-family:"Arial","sans-serif""><u></u> <u></u></span></p>
</td></tr><tr style="height:10.5pt"><td style="width:277.4pt;padding:0cm 5.4pt 0cm 5.4pt;height:10.5pt" nowrap valign="bottom" width="462"><p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#1f497d">134 South Fitzhugh Street</span><span style="font-size:9.0pt;font-family:"Times New Roman","serif";color:#1f497d">                 </span><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#1f497d">Rochester, NY 14608<u></u><u></u></span></p>
</td></tr><tr style="height:13.3pt"><td style="width:277.4pt;padding:0cm 5.4pt 0cm 5.4pt;height:13.3pt" valign="top" width="462"><p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#1f497d">T: <a href="tel:%28585%29%20325-6004" value="+15853256004" target="_blank">(585) 325-6004</a> </span><span style="font-size:9.0pt;font-family:"Arial","sans-serif"">Ext. 114</span><span style="font-size:12.0pt;font-family:"Times New Roman","serif";color:#1f497d">            </span><span style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#1f497d">F: <a href="tel:%28585%29%20325-6005" value="+15853256005" target="_blank">(585) 325-6005</a></span><span style="font-size:9.0pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p>
</td></tr><tr style="height:10.5pt"><td style="width:277.4pt;padding:0cm 5.4pt 0cm 5.4pt;height:10.5pt" valign="top" width="462"><p class="MsoNormal"><span style="color:#1f497d"><a href="mailto:wbishop@pathfinder-ea.com" target="_blank"><span style="font-size:9.0pt;font-family:"Arial","sans-serif"">bbishop@pathfinder-ea.com</span></a></span><span style="font-size:9.0pt;font-family:"Arial","sans-serif"">           </span><span style="color:#1f497d"><a href="http://www.pathfinder-ea.com/" target="_blank"><span style="font-size:9.0pt;font-family:"Arial","sans-serif"">www.pathfinder-ea.com</span></a></span><span style="font-size:9.0pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p>
</td></tr><tr style="height:26.3pt"><td style="width:277.4pt;padding:0cm 5.4pt 0cm 5.4pt;height:26.3pt" valign="top" width="462"><p class="MsoNormal"><span style="font-size:14.0pt;font-family:Webdings;color:green">P</span><span style="font-size:14.0pt;font-family:"Times New Roman","serif";color:green">   </span><span style="font-size:7.5pt;font-family:"Times New Roman","serif";color:green">Sustainability – the forest AND the trees.</span><span style="font-size:18.0pt;font-family:Webdings;color:green"> </span><span style="font-size:14.0pt;font-family:Webdings;color:green">P</span><span style="font-size:14.0pt;color:green">   </span><span style="font-size:14.0pt;color:green">   </span><span style="font-size:14.0pt;font-family:Webdings;color:green"> </span><span style="color:#1f497d"><u></u><u></u></span></p>
</td></tr></tbody></table><p class="MsoNormal"><span style="color:#1f497d" lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span style="color:#1f497d" lang="EN-US"><u></u> <u></u></span></p><div><div style="border:none;border-top:solid #b5c4df 1.0pt;padding:3.0pt 0cm 0cm 0cm">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"" lang="EN-US">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"" lang="EN-US"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">mailto:equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>David Griffin<br>
<b>Sent:</b> Monday, November 04, 2013 4:20 PM<br><b>To:</b> 'Coleman, Kevin'; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> Re: [Equest-users] Slab extending through wall<u></u><u></u></span></p>
</div></div><p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US">Kevin,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US">I’m fairly sure eQUEST is not even going to closely approximate the heat loss/gain accurately unless you dial the loads in manually which means you have to calculate them by hand first. I suggest referring to ASHRAE-D-RP-1365 for guidance on estimating the loads. The section you are interested in starts on page 35.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US"><u></u> <u></u></span></p><div><div><p class="MsoNormal"><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US">Thanks,<u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US"><u></u> <u></u></span></b></p><p class="MsoNormal" style="margin-left:4.5pt"><b><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US">David W. Griffin II<u></u><u></u></span></b></p>
<p class="MsoNormal" style="margin-left:4.5pt"><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US">Energy Analyst<u></u><u></u></span></p><p class="MsoNormal" style="margin-left:4.5pt">
<span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US">ETC Group, LLC<u></u><u></u></span></p><p class="MsoNormal" style="margin-left:4.5pt"><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US"><a href="tel:801-278-1927%20x%20128" value="+18012781927" target="_blank">801-278-1927 x 128</a><u></u><u></u></span></p>
<p class="MsoNormal" style="margin-left:4.5pt"><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US">Cell <a href="tel:480-736-2945" value="+14807362945" target="_blank">480-736-2945</a><u></u><u></u></span></p>
<p class="MsoNormal" style="margin-left:4.5pt"><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US"><a href="mailto:dgriffin@etcgrp.com" target="_blank">dgriffin@etcgrp.com</a><u></u><u></u></span></p>
<p class="MsoNormal" style="margin-left:4.5pt"><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US"><a href="http://www.etcgrp.com" target="_blank">www.etcgrp.com</a><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#17365d" lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US"><img alt="Copy of ETC_LogoOnly2_rgb_sm.png" height="27" border="0" width="112"></span><span style="font-size:6.0pt;font-family:"Arial","sans-serif"" lang="EN-US"><u></u><u></u></span></p>
<p class="MsoNormal" style="margin-left:4.5pt"><b><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#17365d" lang="EN-US">Energy Engineering for a Sustainable Future</span></b><span style="font-size:6.0pt;font-family:"Arial","sans-serif"" lang="EN-US"><u></u><u></u></span></p>
<p class="MsoNormal" style="margin-left:4.5pt"><span style="font-size:6.0pt;font-family:"Arial","sans-serif"" lang="EN-US">1997 South 1100 East, Salt Lake City, UT 84106-4471 <u></u><u></u></span></p><p class="MsoNormal" style="margin-right:0cm;margin-bottom:12.0pt;margin-left:4.5pt">
<span style="font-size:6.0pt;font-family:"Arial","sans-serif"" lang="EN-US">------------------------------------------------------------------------------------------------------------------- <br>CONFIDENTIALITY NOTICE This e-mail transmission, and any documents, files or previous e-mail messages attached to it may contain confidential information that is legally privileged.  If you are not the intended recipient or the person responsible for delivering it to the intended recipient, you are hereby notified that any disclosure, copying, distribution or use of any of the information contained in or attached to this transmission is strictly prohibited.  If you have received this transmission in error, please immediately notify us by telephone at <a href="tel:%28801%29%20278-1927" value="+18012781927" target="_blank">(801) 278-1927</a> and destroy the original transmission and its attachments without reading them. Thank you.<u></u><u></u></span></p>
</div></div><p class="MsoNormal"><span style="font-family:"Arial","sans-serif";color:#17365d" lang="EN-US"><u></u> <u></u></span></p><div><div style="border:none;border-top:solid #b5c4df 1.0pt;padding:3.0pt 0cm 0cm 0cm">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"" lang="EN-US">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"" lang="EN-US"> Coleman, Kevin [<a href="mailto:kcoleman@nexant.com" target="_blank">mailto:kcoleman@nexant.com</a>] <br>
<b>Sent:</b> Monday, November 04, 2013 11:56 AM<br><b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] Slab extending through wall<u></u><u></u></span></p>
</div></div><p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span lang="EN-US">I am evaluating a new 10-story hotel design that is proposing glass curtain walls and pre-tensioned concrete floors that project beyond the walls. On 3 sides the projections are minimal (6 inches). However, on one side, the projections extend about 3 ft. <u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span lang="EN-US">For the small projections, I intent to use the following method recommended in the thread below. “In screen 4 of 25 of the DD shell wizard you can specify "Slab Penetrates Wall Plane" (check box).”<u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span lang="EN-US">I am interested in any tips for modeling the thermal impacts of the larger projections. Thoughts? (I plan to use window shading for the light/shading impacts.)<u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span lang="EN-US">I am hopeful that the analysis will help convince the design team to incorporate some insulation and thermal breaks!<u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span lang="EN-US">Thanks in advance!<u></u><u></u></span></p><p class="MsoNormal"><span lang="EN-US">Kevin<u></u><u></u></span></p><p class="MsoNormal">
<span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span lang="EN-US">Brian Fountain bfountain at <a href="http://greensim.com" target="_blank">greensim.com</a> <u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US">Mon Dec 6 11:45:18 PST 2010<u></u><u></u></span></p><p class="MsoNormal"><span lang="EN-US">Previous message: [Equest-users] balcony<u></u><u></u></span></p><p class="MsoNormal"><span lang="EN-US">Next message: [Equest-users] Shading<u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US">Messages sorted by: [ date ] [ thread ] [ subject ] [ author ]<u></u><u></u></span></p><p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span lang="EN-US">In screen 4 of 25 of the DD shell wizard you can specify "Slab <u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US">Penetrates Wall Plane" (check box).  If you do, eQUEST created a new <u></u><u></u></span></p><p class="MsoNormal"><span lang="EN-US">wall type of height equal to your slab thickness and composed of 1' of <u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US">concrete plus any slab edge insulation you specify on the same wiz <u></u><u></u></span></p><p class="MsoNormal"><span lang="EN-US">screen.   That provides a parallel path for the heat transfer from the <u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US">balcony or slab edge.  Not exactly 2D heat transfer modelling -- but at <u></u><u></u></span></p><p class="MsoNormal"><span lang="EN-US">least you aren't ignoring the effect of the slab edge or balcony.<u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><b><span style="font-family:"Cambria","serif";color:#1f497d" lang="EN-US">Kevin Coleman, CEM, LEED AP</span></b><span style="font-family:"Cambria","serif";color:#000066" lang="EN-US">  </span><span style="font-family:"Arial","sans-serif";color:#999999" lang="EN-US">■</span><span style="font-family:"Cambria","serif";color:#000066" lang="EN-US">  </span><b><span style="font-family:"Cambria","serif";color:#999999" lang="EN-US">Project Manager </span></b><b><span style="font-family:"Arial","sans-serif";color:#999999" lang="EN-US">■</span></b><b><span style="font-family:"Cambria","serif";color:#000066" lang="EN-US">   </span></b><b><span style="font-family:"Cambria","serif";color:#1f497d" lang="EN-US">Nexant, Inc.</span></b><b><span style="font-family:"Cambria","serif";color:#000066" lang="EN-US">  </span></b><b><span style="font-family:"Arial","sans-serif";color:#999999" lang="EN-US">■</span></b><b><span style="font-family:"Cambria","serif";color:#999999" lang="EN-US"> Demand Management <u></u><u></u></span></b></p>
<p class="MsoNormal"><span style="color:#999999" lang="EN-US">1232 Fourier Drive, Suite 125</span><span style="color:#000066" lang="EN-US"> </span><span style="font-family:"Arial","sans-serif";color:#999999" lang="EN-US">■</span><span style="color:#999999" lang="EN-US"> Madison, WI 53717 </span><span style="font-family:"Arial","sans-serif";color:#999999" lang="EN-US">■</span><span style="color:#999999" lang="EN-US">  <a href="tel:608.824.1230" value="+16088241230" target="_blank">608.824.1230</a> </span><span style="font-family:"Arial","sans-serif";color:#999999" lang="EN-US">■</span><span style="color:#999999" lang="EN-US"> </span><span style="color:#000066" lang="EN-US"> </span><u><span style="color:blue" lang="EN-US"><a href="mailto:kcoleman@nexant.com" target="_blank">kcoleman@nexant.com</a></span></u><span lang="EN-US"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt" lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:18.0pt;font-family:Webdings;color:green" lang="EN-US">P </span><span style="color:green" lang="EN-US">Please consider the environment before printing this email<b> <u></u><u></u></b></span></p>
<p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p></div></div></div></div><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>