<div dir="ltr">Anytime that you compare to different system types you're opening yourself up to a ton of potential issues just from the differences in how eQUEST models each system.<div><br></div><div>For a VAV system that is using more energy than a packaged single zone type system I'd recommend you look into a few things:</div>
<div>• Night fan cycling - if you've got single duct VAV terminals with reheat, your entire AHU system will have to come on to address night heating hours. Verify that you have a minimum OA schedule so that you're not ventilating the whole building during these hours as well.</div>
<div>• Minimum airflow setpoints - Verify your minimum airflow setpoints at the zone level are correct. This is where most of your reheat energy will come from.</div><div><br></div><div>Those are the two that come to mind immediately, but there may be other potential sources of error. Feel free to attach your building model (.pd2 & .inp files) to the list and maybe someone can look into it for you in more depth.</div>
<div><br></div><div>Hope that helps,</div><div>-Robby</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Tue, Sep 24, 2013 at 9:37 AM, jacob goodman <span dir="ltr"><<a href="mailto:jacobgoodman22@gmail.com" target="_blank">jacobgoodman22@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">Dear eQuest community,<div><br></div><div>I am working on a LEED project and have an issue where my higher efficiency proposed system is using significantly more gas than the baseline system. The proposed system is central AHU with zone VAV terminals fed by 96% AFUE boilers. The Baseline system is Appendix G system type 3 PSZ with 80% efficient gas furnace. I know there are tons of factors that go into this. I noticed that the higher baseline fan energy and higher lighting load are doing some of the work that the furnaces would do, but this doesn't account for the whole difference. Anything that jumps out comparing these two systems would be much appreciated.</div>
<div><br></div><div>since I have no one with greater eQuest knowledge in house, I am open to a few hours consulting with someone at a reasonable hourly rate if you think this could be resolved. </div><div><br></div><div>
Thanks,</div>
<div>Jacob</div></div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>