<html xmlns:v="urn:schemas-microsoft-com:vml" xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns:m="http://schemas.microsoft.com/office/2004/12/omml" xmlns="http://www.w3.org/TR/REC-html40">
<head>
<meta http-equiv="Content-Type" content="text/html; charset=us-ascii">
<meta name="Generator" content="Microsoft Word 12 (filtered medium)">
<style><!--
/* Font Definitions */
@font-face
{font-family:Wingdings;
panose-1:5 0 0 0 0 0 0 0 0 0;}
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Tahoma;
panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
{font-family:TimesNewRomanPS-BoldMT;}
@font-face
{font-family:TimesNewRomanPSMT;}
@font-face
{font-family:TimesNewRomanPS-ItalicMT;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman","serif";
color:black;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
p
{mso-style-priority:99;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman","serif";
color:black;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
{mso-style-priority:99;
mso-style-link:"Balloon Text Char";
margin:0in;
margin-bottom:.0001pt;
font-size:8.0pt;
font-family:"Tahoma","sans-serif";
color:black;}
span.BalloonTextChar
{mso-style-name:"Balloon Text Char";
mso-style-priority:99;
mso-style-link:"Balloon Text";
font-family:"Tahoma","sans-serif";
color:black;}
span.EmailStyle20
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle21
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle22
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle23
{mso-style-type:personal-reply;
font-family:"Calibri","sans-serif";
color:#1F497D;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
</head>
<body bgcolor="white" lang="EN-US" link="blue" vlink="purple">
<div class="WordSection1">
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">My understanding is that for a 90.1-2007 outside air is modeled at the same CFM even if it’s beyond ASHRAE 62.1 requirements with no energy penalty. However,
this is no longer true in 90.1-2010 where the baseline is to follow ASRAE 62.1. <o:p>
</o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Also, I thought there was a ruling or interpretation to 62.1 that only allowed the elimination of the occupant portion of the ventilation to be shut off during
unoccupied hours, but the area based outside air needs to be maintained at night to handle off-gassing. I believe the 90.1 folks are still discussing how to incorporate this ruling into the standard.
<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">If you don’t have more DCV than the baseline, just use show in a calculation the total CFM and fraction of outside air for each AHU and show them the total
is approximately the same. There is some latitude here for rounding errors and the like as some complex buildings may be off by a few percent. If your proposed outside cfm is slightly greater than your baseline outside cfm, then you should definitely be ok
as your model will be conservative. <o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Hope that helps,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Fred<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<div>
<table class="MsoNormalTable" border="0" cellpadding="0" width="474" style="width:355.5pt">
<tbody>
<tr>
<td width="169" valign="top" style="width:126.9pt;padding:.75pt .75pt .75pt .75pt">
<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><b><span style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#660000;text-transform:uppercase">Fred Betz</span></b><b><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#333333">
</span></b><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#333333">PhD.,
</span><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#333333">LEED AP ®BD&C</span><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#333333"><br>
</span><span style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#333333;text-transform:uppercase">Sustainable Systems Analyst</span><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#333333"><o:p></o:p></span></p>
</td>
<td width="10" valign="top" style="width:7.6pt;padding:.75pt .75pt .75pt .75pt">
<p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#333333"> </span><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#333333"><o:p></o:p></span></p>
</td>
<td width="287" valign="top" style="width:215.0pt;padding:.75pt .75pt .75pt .75pt">
<p class="MsoNormal" style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><b><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#660000">AEI</span></b><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#333333"> |
AFFILIATED ENGINEERS, INC. <br>
5802 Research Park Blvd. | Madison, WI 53719<br>
<br>
</span><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#660000">P: 608.236.1175 | F: 608.238.2614</span><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#333333"> <br>
</span><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#660000"><a href="mailto:fbetz@aeieng.com"><span style="color:#660000;text-decoration:none">fbetz@aeieng.com</span></a> |
<b><a href="http://www.aeieng.com/"><span style="color:#660000;text-decoration:none">www.aeieng.com</span></a></b></span><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#333333"> </span><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#333333"><o:p></o:p></span></p>
</td>
</tr>
</tbody>
</table>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
</div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext"> Kevin Kyte [mailto:KKyte@watts-ae.com]
<br>
<b>Sent:</b> Thursday, September 19, 2013 2:59 PM<br>
<b>To:</b> Reba Schaber; Jim Dirkes; equest-users@lists.onebuilding.org; 'bldg-sim@lists.onebuilding.org'<br>
<b>Cc:</b> 'bldg-rate@lists.onebuilding.org'<br>
<b>Subject:</b> Re: [Bldg-sim] usgbc response to outdoor air question<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Ok, so I received this comment. The one with the provide ASHRAE minimums in the Baseline for spaces with DCV. I understand this is a generic comment - Ok.
<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">However, LEED IEQ Credit 2 is not being pursued and the ASHRAE minimum ventilation requirements are what is being Proposed for in each space that has DCV.
<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Does this not mean that the Baseline ventilation rate and the Proposed ventilation rate will still be equal?<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Not sure how to respond other than to simply say what is stated here.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Calibri","sans-serif";color:#1F497D">Thanks,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Calibri","sans-serif";color:#1F497D">Kevin<o:p></o:p></span></p>
</div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext"> Reba Schaber [<a href="mailto:Rschaber@PHMECH.com">mailto:Rschaber@PHMECH.com</a>]
<br>
<b>Sent:</b> Tuesday, November 15, 2011 9:42 PM<br>
<b>To:</b> Jim Dirkes; <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>; 'bldg-sim@lists.onebuilding.org'<br>
<b>Subject:</b> Re: [Bldg-sim] usgbc response to outdoor air question<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">RE:
<i>“. . . can’t find) anything in 621.1 which says that unoccupied ventilation should be zero.”<o:p></o:p></i></span></p>
<p class="MsoNormal"><i><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></i></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">I think this requirement comes from the mandatory provisions of 90.1.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal" style="text-autospace:none"><b><span style="font-size:10.0pt;font-family:TimesNewRomanPS-BoldMT;color:windowtext">6.4.3.4.3 Shutoff Damper Controls.
</span></b><span style="font-size:10.0pt;font-family:TimesNewRomanPSMT;color:windowtext">Both
</span><i><span style="font-size:10.0pt;font-family:TimesNewRomanPS-ItalicMT;color:windowtext">outdoor<o:p></o:p></span></i></p>
<p class="MsoNormal" style="text-autospace:none"><i><span style="font-size:10.0pt;font-family:TimesNewRomanPS-ItalicMT;color:windowtext">air
</span></i><span style="font-size:10.0pt;font-family:TimesNewRomanPSMT;color:windowtext">supply and exhaust systems shall be equipped with motorized<o:p></o:p></span></p>
<p class="MsoNormal" style="text-autospace:none"><span style="font-size:10.0pt;font-family:TimesNewRomanPSMT;color:windowtext">dampers that will automatically shut when the systems or<o:p></o:p></span></p>
<p class="MsoNormal" style="text-autospace:none"><span style="font-size:10.0pt;font-family:TimesNewRomanPSMT;color:windowtext">spaces served are not in use. Ventilation
</span><i><span style="font-size:10.0pt;font-family:TimesNewRomanPS-ItalicMT;color:windowtext">outdoor air
</span></i><span style="font-size:10.0pt;font-family:TimesNewRomanPSMT;color:windowtext">dampers<o:p></o:p></span></p>
<p class="MsoNormal" style="text-autospace:none"><span style="font-size:10.0pt;font-family:TimesNewRomanPSMT;color:windowtext">shall be capable of automatically shutting off during preoccupancy<o:p></o:p></span></p>
<p class="MsoNormal" style="text-autospace:none"><span style="font-size:10.0pt;font-family:TimesNewRomanPSMT;color:windowtext">building warm-up, cool down, and
</span><i><span style="font-size:10.0pt;font-family:TimesNewRomanPS-ItalicMT;color:windowtext">setback,
</span></i><span style="font-size:10.0pt;font-family:TimesNewRomanPSMT;color:windowtext">except<o:p></o:p></span></p>
<p class="MsoNormal" style="text-autospace:none"><span style="font-size:10.0pt;font-family:TimesNewRomanPSMT;color:windowtext">when
</span><i><span style="font-size:10.0pt;font-family:TimesNewRomanPS-ItalicMT;color:windowtext">ventilation
</span></i><span style="font-size:10.0pt;font-family:TimesNewRomanPSMT;color:windowtext">reduces energy costs (e.g., night purge) or<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:TimesNewRomanPSMT;color:windowtext">when ventilation must be supplied to meet code requirements.</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Thoughts??<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Reba<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">
<a href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a> [<a href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Jim Dirkes<br>
<b>Sent:</b> Monday, October 17, 2011 9:32 AM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>; 'bldg-sim@lists.onebuilding.org'<br>
<b>Subject:</b> Re: [Bldg-sim] usgbc response to outdoor air question<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Dear Patrick,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Thank you for sharing this GBCI response! It is very informative and, while I won’t admit that I’ve been modeling anything incorrectly, I
<u>am</u> going to change a couple of things </span><span style="font-size:11.0pt;font-family:Wingdings;color:#1F497D">J</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">In particular, I have heard on several occasions that the Increased Ventilation credit was a clear case of “IEQ vs. energy”; you make a decision to trade one
against the other. After reading the GBCI response below and then double-checking with ASHRAE 90.1, I find that they are consistent with each other and effectively allow no penalty for the increased energy caused by increased ventilation. Very curious, considering
there is no science which demonstrates a health benefit for outdoor airflows greater than that required by ASHRAE 62.1!<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">The other item is that I failed to notice (and still can’t find) anything in 621.1 which says that unoccupied ventilation should be zero. I guess that is OK,
but is also curious, since a portion of the ventilation calcs in 62.1 include consideration for off-gassing materials (which are always present.)<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">All in all, I’m smarter than I was as a result of your post, so it’s a good day! Thanks again.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal" align="center" style="text-align:center"><b><span style="font-size:13.5pt;font-family:"Calibri","sans-serif";color:#1F497D">The Building Performance Team<br>
</span></b><b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">James V. Dirkes II, P.E., BEMP , LEED AP<br>
</span></b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">1631 Acacia Drive NW<br>
Grand Rapids, MI 49504<br>
616 450 8653<o:p></o:p></span></p>
</div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">
<a href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a> [<a href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Patrick J. O'Leary, Jr.<br>
<b>Sent:</b> Monday, October 17, 2011 11:46 AM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>;
<a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> [Bldg-sim] usgbc response to outdoor air question<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">back in september there was a thread about what the outdoor air rate in a baseline simulation should be compared to a proposed simulation, specifically when one is adding 30% more outdoor air to meet the ieqc2 requirement and earn 1 leed
point. there were differences of opinions about the flow rates between baseline and proposed being either the same (as required in 90.1 app g) or the baseline being the calculated per 62.1 and the proposed being as designed.<br>
<br>
so i submitted a support request to the usgbc and the reply i received is below, but in short the response is that unless you're using dcv optionally the outdoor air rates in the baseline and proposed energy simulations for eac1 should be the same. the response
below gives the standard responses to differing outdoor air rate scenarios.<br>
<br>
regards,<br>
patrick<o:p></o:p></p>
<p>[Fwd: Case 00531150: General LEED Questions<o:p></o:p></p>
<p>-------- Original Message --------<o:p></o:p></p>
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0">
<tbody>
<tr>
<td nowrap="" valign="top" style="padding:0in 0in 0in 0in">
<p class="MsoNormal" align="right" style="text-align:right"><b>Subject: <o:p></o:p></b></p>
</td>
<td style="padding:0in 0in 0in 0in">
<p>Case 00531150: General LEED Questions [ ref:00D49UeD.5004GN692:ref ]<o:p></o:p></p>
</td>
</tr>
<tr>
<td nowrap="" valign="top" style="padding:0in 0in 0in 0in">
<p class="MsoNormal" align="right" style="text-align:right"><b>Date: <o:p></o:p></b></p>
</td>
<td style="padding:0in 0in 0in 0in">
<p>Mon, 17 Oct 2011 06:54:51 +0000 (GMT)<o:p></o:p></p>
</td>
</tr>
<tr>
<td nowrap="" valign="top" style="padding:0in 0in 0in 0in">
<p class="MsoNormal" align="right" style="text-align:right"><b>From: <o:p></o:p></b></p>
</td>
<td style="padding:0in 0in 0in 0in">
<p>"No reply GBCI" <a href="mailto:no-reply@gbci.org"><no-reply@gbci.org></a> <a href="mailto:no-reply@gbci.org">
<no-reply@gbci.org></a><o:p></o:p></p>
</td>
</tr>
<tr>
<td nowrap="" valign="top" style="padding:0in 0in 0in 0in">
<p class="MsoNormal" align="right" style="text-align:right"><b>To: <o:p></o:p></b></p>
</td>
<td style="padding:0in 0in 0in 0in">
<p>patrick@<o:p></o:p></p>
</td>
</tr>
</tbody>
</table>
<p><o:p> </o:p></p>
<p class="MsoNormal">Dear Patrick,<br>
<br>
Thank you for contacting the Green Building Certification Institute. <br>
<br>
You ask very good questions related to the relationship between ASHRAE Standards 62.1 and 90.1, and how these standards are applied across multiple LEED Rating System prerequisites and credits.<br>
<br>
The simple answer to your question is that, for systems without demand controlled ventilation, the outdoor air included in EA Credit 1 energy simulations must be the same in the Baseline and Proposed cases. If the project is attempting IEQ Credit 2 Increased
Ventilation, then the values calculated in IEQc2 must be used in the EAc1 Basline and Proposed case energy models. Note that IEQc2 does not limit the project to providing only 30% more outdoor air than AHRAE 62.1 Ventilation Rate Procedure minimums, so higher
amounts are acceptable, as long as they are modeled identically in both the Baseline and Proposed case energy models.<br>
<br>
The following generic LEED Review Comment applies to ventilation systems that do not have demand controlled ventilation:<br>
<br>
It is unclear whether the minimum outside air rates (in CFM) were modeled identically in the Baseline and Proposed case for all zones not having Demand Control Ventilation in the Proposed case. Please confirm that minimum outside airflow (in units of cfm) was
modeled identically in the Baseline and Proposed cases using the proposed case rates. Additionally, please verify that all systems in both the baseline and proposed case are modeled with zero outside air flow when fans are cycled on to meet unoccupied setback
temperatures unless health or safety regulations mandate an alternate minimum flow during unoccupied periods (in which case, the unoccupied outside air rates should be modeled identically in the Baseline and Proposed case).<br>
<br>
The situation becomes a bit more complicated in you have systems that have demand controlled ventilation (often implemented as Carbon Dioxide control of outdoor air or as programmed control of outdoor air based on occupancy sensors.) In this case the Baseline
case energy model must include the minimum outdoor air as determined by the ASHRAE 62.1 Ventilation Rate Procedure calculations for all systems having demand controlled ventilation.
<br>
<br>
The following generic LEED Review Comment applies to ventilation systems that do have demand controlled ventilation:<br>
<br>
Demand control ventilation was modeled for credit in the proposed case. Appendix G allows schedule changes for demand control ventilation as approved by the rating authority (Table G3.1#4(Baseline)). As the LEED Certification rating authority, GBCI requires
that the outside air ventilation rates for the Baseline case be modeled using minimum ASHRAE 62.1-2004 (or 2007 for LEED-NC 2009 projects) rates wherever credit is taken for demand control ventilation in the Proposed case. The proposed case minimum rates at
design conditions should be modeled as designed. Please verify that the Baseline Case model reflects ASHRAE 62.1-2004 (or 2007) minimum rates for any spaces where credit is taken for demand control ventilation, or revise the model accordingly. For all other
spaces, please confirm that minimum outside airflow (in units of cfm) was modeled identically in the Baseline and Proposed cases. Additionally, please verify that all systems in both the baseline and proposed cases are modeled with zero outside air flow when
fans are cycled on to meet unoccupied setback temperatures unless health or safety regulations mandate an alternate minimum flow during unoccupied periods (in which case, the unoccupied outside air rates should be modeled identically in the Baseline and Proposed
case).<br>
<br>
Finally, even though you don't address energy recovery in your question, whether or not you have energy recovery in your ventilation systems may affect how much better (or worse) your Proposed case energy models perform in relation to your Baseline case energy
models. <br>
<br>
The following generic LEED Review Comment addresses energy recovery in EAc1 energy models as it relates to ventilation systems.<br>
<br>
Energy recovery is modeled for credit in the Proposed case. Please provide further information regarding the energy recovery efficiency, verify that outside air is modeled with zero flow in both the Baseline and Proposed cases during unoccupied periods when
fans are cycled on to meet unoccupied setback temperatures unless health or safety regulations mandate an alternate minimum flow during unoccupied periods (in which case, the unoccupied outside air rates should be modeled identically in the Baseline and Proposed
Case), and indicate the bypass mechanism used to bypass the energy recovery during mild conditions.
<br>
<br>
I hope that helps, but if you have any further questions or concerns, please feel free to use the contact form at
<a href="http://www.gbci.org/contactus">http://www.gbci.org/contactus</a> and select "Follow up to GBCI Response," inputting your case number from this email's subject line.<br>
<br>
Best Regards,<br>
<br>
Dan Katzenberger, P.E., CEM, BEMP, LEED-AP BD+C<br>
<br>
Green Building Certification Institute <br>
2101 L Street NW, Suite 500 <br>
Washington, DC 20037 <br>
800-795-1746 (phone)<br>
202 828-5110 (fax) <br>
<a href="http://www.gbci.org/contactus">www.gbci.org/contactus</a><br>
<br>
The text above represents a staff opinion of a particular issue, and does NOT set any precedent to be upheld during a LEED Certification Review. For official rulings in advance of a LEED Certification Review, customers should utilize the Formal Inquiries process
available in LEED Online that results in a Project Credit Interpretation Ruling (Project CIR) and possibly a LEED Interpretation (formerly CIRs or Public Rulings). Applications for LEED Certification will be thoroughly reviewed based on USGBC Member balloted
and approved LEED Rating Systems, with addenda, and USGBC approved LEED Interpretations, or Project CIRs administered by GBCI, as applicable. Please note that certain inquiries submitted to USGBC are forwarded to GBCI for reply as appropriate.<br>
<br>
<br>
_______________________________<br>
CUSTOMER EMAIL ADDRESS: <br>
patirck@<br>
<br>
CUSTOMER INQUIRY:<br>
I am trying to verify what the minimum outdoor airflow rate required for EAc1 is and am not sure if this requires a CIR.
<br>
<br>
If the Proposed outdoor air ventilation is a minimum of 30% higher than the minimum required by ASHRAE 62 in order to achieve 1 LEED point for credit IEQC2 is the Baseline outdoor air rate also 30% higher than the minimum required by ASHRAE 62? or would the
Baseline outdoor air ventilation rate be the minimum outdoor air rate per ASHRAE 62 calculations.
<br>
<br>
In other words, if ASHRAE 62 requires a minimum of 1,000 CFM of outdoor air, and 1,300 CFM is provided to attain 1 LEED point via IEQC1, is the Baseline outdoor air flow rate 1,000 CFM or 1,300 CFM in the energy simulation?
<br>
<br>
90.1-2007/2004 both say the minimu m outdoor airflow rates shall be the same for both the proposed and baseline building designs, as does the user manual.
<br>
<br>
But this logic seems to reward the Proposed simulation by conditioning the additional outdoor air supplied (300 cfm in the example above) to achieve IEQC1 in the Baseline system as well as the proposed.
<br>
<br>
The logic of using the minimum required in the Baseline case is reflected in EAC1 in the equipment efficiency requirements. Baseline efficiencies are the minimum required, e.g. SEER 13 for packaged units.
<br>
<br>
It is the intent of the requirement that I am not sure is clear. Increasing the outdoor air ventilation rate increases the energy used to condition the outdoor air, so if the intent is to put the onus on Proposed design to show energy reduction/LEED compliance
over the 90.1/62 requirements shouldn't the Baseline outdoor air be the minimum air flow rate per the ASHRAE 62 calculations? This puts the onus on the design team to provide a design that compensates for the increase in energy to meet IEQC2 by providing some
method of processing the increase in outdoor air while still reducing energy consumption.<o:p></o:p></p>
</div>
</body>
</html>