    I took a quick look at your files, and noticed that the occupancy
    was input in different ways between the two models (AREA/PERSON in
    one and NUMBER-OF-PEOPLE in the other). Also, two spaces have
    PEOPLE-SCHEDULE defined in one case, and not in the other.   I
    assume that NUMBER-OF-PEOPLE override AREA/PERSON, but am not sure. 
    I suggest that you look at the LOADS reports in the *.SIM files and
    see what are the actual occupancy and occupancy schedule that are
    being modeled. Please note that occupancy affects other operations
    as well, such as the amount of outside air, etc. <br>
    <br>
    Joe<br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <br>
    On 17/09/2013 2:01 PM, Morteza Kasmai wrote:
    <blockquote
cite="mid:CABaPZUdP2E+akB9R4XVtqdTwJusOnCLe++CNDr4pzkvJBNtUpw@mail.gmail.com"
      type="cite">
      <meta http-equiv="Context-Type" content="text/html;
        charset=ISO-8859-1">
      <div>
        <div>
          <p><span>Dear All,</span></p>
          <p><span>Something strange is
              happening in this proposed model. When I change the total
              building occupancy
              from eQuest default numbers (321) to real numbers that I
              have for the actual
              design (361), total building energy consumption increases
              tremendously (from $135,741
              to $144,114). However, when I increase the occupancy in
              the baseline model
              (with System 6), the total building energy consumption
              does not increase too
              much. Please refer to the attached files (INP and PD2
              files of proposed model with
              different building occupancy).</span><br>
          </p>
          <p><span>I would appreciate
              your comments on this issue,</span><br>
          </p>
          <p><span>Morteza</span></p>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <br>
        <div>
          <div><img moz-do-not-send="true"><br>
            <div>
              <div>
                <div><br>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>