<div dir="ltr"><div>Nevermind, I was confused because I was actually looking at SYSTEMS/BUILDING-HVAC Total cooling load (Btu/hr).<br><br></div><div>Eric<br><br></div><div><div><div class="gmail_extra"><div class="gmail_quote">
On Wed, Sep 4, 2013 at 9:48 AM, Eric Wilson <span dir="ltr"><<a href="mailto:ericjhwilson@gmail.com" target="_blank">ericjhwilson@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
<div dir="ltr"><div><div>I have a question about the hourly loads documented in Volume 4: Libraries & Reports > Reports > Hourly-Report and REPORT-BLOCK:<br><br></div>If I compare monthly sums for BUILDING-LOADS Variable 19 "Building cooling load (sensible)" to the monthly sensible cooling energy values in Report SS-I, I do not get agreement. However, the sensible load monthly sums do agree with the <i>total</i> cooling energy (sum of sensible and latent columns) in Report SS-I. <br>
<br>This makes me think that Variable 19 is mistakenly reporting the total cooling load. Has anyone seen this before? Relevant files are attached.<br><br></div><div>Thanks,<br>Eric<span class=""><font color="#888888"><br>
</font></span></div><span class=""><font color="#888888"><div><br>Eric Wilson<br>Engineer, Residential Buildings Research Group<br>
National Renewable Energy Laboratory<br><a href="tel:303-275-4676" value="+13032754676" target="_blank">303-275-4676</a><br><a href="mailto:eric.wilson@nrel.gov" target="_blank">eric.wilson@nrel.gov</a><br></div></font></span></div>
</blockquote></div><br></div></div></div></div>