<div dir="ltr"><div><div>I have a question about the hourly loads documented in Volume 4: Libraries & Reports > Reports > Hourly-Report and REPORT-BLOCK:<br><br></div>If I compare monthly sums for BUILDING-LOADS Variable 19 "Building cooling load (sensible)" to the monthly sensible cooling energy values in Report SS-I, I do not get agreement. However, the sensible load monthly sums do agree with the <i>total</i> cooling energy (sum of sensible and latent columns) in Report SS-I. <br>
<br>This makes me think that Variable 19 is mistakenly reporting the total cooling load. Has anyone seen this before? Relevant files are attached.<br><br></div><div>Thanks,<br>Eric<br></div><div><br>Eric Wilson<br>Engineer, Residential Buildings Research Group<br>