<div>Hi eQuesters!<br> <br>I am modeling a Laboratory building with Fume Hoods (Climate zone 4A).<br>  <br>Per ASHRAE 90.1-2007 Appx.G 3.1.2.10, the baseline laboratory AHUs should be installed with Energy Recovery (SA>2400L/s & OA 70%).<br>
However, there are 'Exceptions' and one of which says as follow:</div>
<div> </div>
<div><u><strong>h.</strong> Systems serving laboratories wish exhaust rates of 2400 l/s or greater.</u></div>
<div> </div>
<div>Does it really mean that the Baseline AHU is not required to have ERV if the AHU has an exhaust rate(Not return) of 2400 l/s or greater??</div>
<div> </div>
<div>I don't know the reason under that exception(h), but anyhow, that will be beneficial for my proposed model which has ERV(sensible HX) for the laboratory AHUs.</div>
<div> </div>
<div>Any comment on this?</div>
<div> </div>
<div>Thank you !!</div>
<div> </div>
<div>Kim</div>