    Jeremiah,<br>
    <br>
    Your  question is not quite on the mark because what I've described
    is downstream from the calculation of room loads where techniques
    such as the Weighting Factor or the Heat Balance methods come into
    play.   Before I get to that issue, though, I want to point out that
    the "Adjust Loads" procedure I described is done automatically by
    DOE-2 and totally invisible to the User;  I did so only to explain
    why<span> Bhartendu</span> (the original poster) was not seeing any
    conduction loads through the ceiling.  <br>
    <br>
    Now, back to this "Adjust Loads" procedure, there is no simulation
    program I know of that solves simultaneously for the heat flows and
    the zone temperature.  DOE-2 does it in the two-step way that others
    and I have just described. When you said "compared to the Heat
    Balance Method", I assume you're thinking of EnergyPlus.  So, how
    does EnergyPlus meet this problem?  Whereas DOE-2 does one year of
    LOADS and then one year of SYSTEMS, EnergyPlus does them in the same
    time step, but also sequentially. Therefore,  EnergyPlus calculates
    the heat flows using the zone temperature from the previous time
    step which are then used in its HVAC simulation without adjustment.
    This should be okay when zone temperatures don't change, but what
    about at morning start-up when temperatures could change by 5-10 F
    within one hour?  I've always wondered whether that's why EnergyPlus
    gives much lower heating loads in mild California climates than does
    DOE-2?  As far as which procedure is "more realistic", I can't say.<br>
    <br>
    Joe<br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <br>
    On 8/19/2013 9:57 PM, Jeremiah Crossett wrote:
    <blockquote
cite="mid:CAPsP_xTjc9wbNCwBn7ZA_9o=TE5KMfg0Sm5QGGvc7n3xVFqugA@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div class="gmail_default" style="font-family:
          tahoma,sans-serif; font-size: small; color: rgb(51, 51, 51);">Joe, Just
          wondering,  given your expertise how would you compare this to
          the heat balance method.., and what do you think is more
          realistic? </div>
        <div class="gmail_extra"><br clear="all">
          <div>
            <div><font color="#336666"><i><br>
                </i></font></div>
            <div><b><span style=""><font color="#336666" size="1"><b
                      style="font-family: Verdana,sans-serif;"><br>
                    </b></font></span></b></div>
            <div>
              <div style="text-align: center;"><b><span style=""><font
                      color="#000099" size="1"><b style="font-family:
                        Verdana,sans-serif;">Jeremiah D. Crossett</b><span
                        style="font-family: Verdana,sans-serif;">  </span><font
                        face="Verdana, sans-serif">| Senior </font><font
                        face="Verdana, sans-serif">Analyst</font><font
                        face="Verdana, sans-serif">  |  Phase Change
                        Energy Solutions</font></font></span></b></div>
              <b>
                <div style="text-align: center;"><b><span style=""><font
                        size="1"><font color="#000099" face="Verdana,
                          sans-serif">120 E. Pritchard St.  | Asheboro,
                          NC 27203  | Mobile <a moz-do-not-send="true"
                            href="tel:503-688-8951" value="+15036888951"
                            target="_blank">503-688-8951</a></font></font></span></b></div>
                <span style="color: rgb(153, 153, 153);">
                  <div style="text-align: center;"><b
                      style="background-color: transparent;"><b
                        style="font-family: Verdana,sans-serif;
                        font-size: 8pt;"><a moz-do-not-send="true"
                          href="http://www.phasechange.com"
                          target="_blank">www.phasechange.com</a> </b></b></div>
                </span></b></div>
            <div>
              <div style="text-align: center;">  <img
                  moz-do-not-send="true"
                  src="http://i.imgur.com/Sldxf.jpg"></div>
              <b><b style="font-family: Verdana,sans-serif;"><font
                    color="#0000fe"><br>
                  </font></b></b></div>
            <div><b style="color: rgb(0, 0, 254); font-size: 13px;
                font-family: Verdana,sans-serif;"><b><span
                    style="font-size: 10pt;"><br>
                  </span></b></b></div>
            <div><font color="#0000fe" face="Verdana, sans-serif"><span
                  style="font-weight: 800;"><br>
                </span></font></div>
          </div>
          <br>
          <br>
          <div class="gmail_quote">On Mon, Aug 19, 2013 at 6:14 PM, Joe
            Huang <span dir="ltr"><<a moz-do-not-send="true"
                href="mailto:yjhuang@whiteboxtechnologies.com"
                target="_blank">yjhuang@whiteboxtechnologies.com</a>></span>
            wrote:<br>
            <blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt
              0.8ex; border-left: 1px solid rgb(204, 204, 204);
              padding-left: 1ex;">
              <div text="#000000" bgcolor="#ffffff"> Just to repeat what
                David and Rodrigo have already sad, DOE-2 calculates
                conduction loads in a two step process. In LOADS, a
                constant reference temperature is specified, which DOE-2
                uses to calculate the amount of heat flow through the
                surfaces. This is the LOADS loads summarized in the LS-E
                and LS-F reports.  In SYSTEMS, DOE-2 calculates the true
                temperature of the zone based on the loads passed from
                LOADS, as well as the actions of the HVAC system.  In
                the course of this calculation, the heat flows ("loads")
                from LOADS are adjusted, but this is not done surface by
                surface, but in total using the so-called "Zone
                Conductance" times the difference between the actual
                zone temperature and the reference temperature used in
                LOADS.  At this point, heat flows through internal walls
                are also considered, using the  difference between this
                hour's zone temperature and the previous hour's zone
                temperature of the adjacent space, e.g., the Attic or
                Plenum.  If you are interested in this number, I believe
                it can be extracted in an hourly report.  <br>
                <br>
                In reference to Rodrigo's question, I don't see any
                benefit in forcing a heat flow between the room and the
                attic by using different reference temperatures.   You
                will simply get a constant heat flow at that temperature
                difference throughout the simulation. In reality, attics
                are generally colder than the room in the winter and
                warmer than the room in the summer, so the derived heat
                flow with this temperature difference doesn't get you
                any closer to reality, in my opinion.<br>
                <br>
                Joe<br>
                <pre cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a moz-do-not-send="true" href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank">yjhuang@whiteboxtechnologies.com</a>
<a moz-do-not-send="true" href="http://weather.whiteboxtechnologies.com" target="_blank">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) <a moz-do-not-send="true" href="tel:%28925%29388-0265" value="+19253880265" target="_blank">(925)388-0265</a>
(c) <a moz-do-not-send="true" href="tel:%28510%29928-2683" value="+15109282683" target="_blank">(510)928-2683</a>
"building energy simulations at your fingertips"
</pre>
                <div>
                  <div> <br>
                    On 8/19/2013 12:05 PM, David Wood wrote:
                    <blockquote type="cite">
                      <div>
                        <div>
                          <div>Hi All,<br>
                            <br>
                          </div>
                          The LS-C report comes from the LOADS
                          simulation portion of DOE 2.2. The plenum
                          reference temperature used in LOADS is
                          adjusted in the SYSTEMS portion of the program
                          and the loads in the spaces adjacent to the
                          plenum are corrected <br>
                          correspondingly.<br>
                          <br>
                        </div>
                        Dave Wood<br>
                      </div>
                      <div><br>
                        <br>
                        <div>On Thu, Aug 8, 2013 at 8:58 AM, Rodrigo
                          Cerqueira <span><<a moz-do-not-send="true"
                              href="mailto:rodrigo.cerqueira@mra.qc.ca"
                              target="_blank">rodrigo.cerqueira@mra.qc.ca</a>></span>
                          wrote:<br>
                          <blockquote>
                            <div lang="FR-CA">
                              <div>
                                <p><span lang="EN-US">Hi, </span></p>
                                <p> <span lang="EN-US">This happens
                                    because the load calculation is made
                                    with a fixed temperature (see
                                    picture). All the spaces, include
                                    plenum zones, have the same
                                    temperature by default (70°F). So,
                                    all roof load appears in the plenum
                                    spaces. To considerate the roof
                                    load, you have to change this
                                    temperature in plenum spaces and a
                                    part of roof load will appear like
                                    "internal surface conduction". But
                                    I'm not sure if this is a good
                                    practice. </span><span>Maybe
                                    someone else has an opinion about
                                    that. </span></p>
                                <p><span>   </span></p>
                                <p><span><img moz-do-not-send="true"></span><span>
                                  </span></p>
                                <p><span>   </span></p>
                                <p><b><span>Rodrigo Cerqueira, </span></b><span>ing.

                                    jr, M.Ing.<b> </b></span></p>
                                <p><b><span>Simulation énergétique </span></b></p>
                                <p><span>   </span></p>
                                <p><span><img moz-do-not-send="true"
                                      alt="signatureCouriel"> </span></p>
                                <p><span>   </span></p>
                                <p><span>   </span></p>
                                <p><span>   </span></p>
                                <div>
                                  <p><b><span lang="FR">De :</span></b><span
                                      lang="FR"> <a
                                        moz-do-not-send="true"
                                        href="mailto:equest-users-bounces@lists.onebuilding.org"
                                        target="_blank">equest-users-bounces@lists.onebuilding.org</a>
                                      [mailto:<a moz-do-not-send="true"
href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
                                      <b>De la part de</b> Bhartendu
                                      Awasthi<br>
                                      <b>Envoyé :</b> 8 août 2013 06:35<br>
                                      <b>À :</b> <a
                                        moz-do-not-send="true"
                                        href="mailto:equest-users@lists.onebuilding.org"
                                        target="_blank">equest-users@lists.onebuilding.org</a>;
                                      <a moz-do-not-send="true"
                                        href="mailto:bldg-sim@lists.onebuilding.org"
                                        target="_blank">bldg-sim@lists.onebuilding.org</a><br>
                                      <b>Objet :</b> [Equest-users] Roof
                                      Conduction Load </span></p>
                                </div>
                                <p>   </p>
                                <div>
                                  <p>Hi All, </p>
                                  <div>
                                    <p>   </p>
                                  </div>
                                  <div>
                                    <pre><span>I am doing an energy simulation model in eQuest. I noticed that the load through roof conduction in LS-C is zero where as in LS-B (for plenum space) it is showing some load.</span><span>    </span></pre>
                                    <pre><span>     </span></pre>
                                    <pre><span>As per my understanding this load should appear in LS-C also.</span><span>    </span></pre>
                                    <pre><span>Also, if I reduce the U value of the roof, the load through roof reduces and can be accounted in LS-B only (plenum space).</span><span>    </span></pre>
                                    <pre><span>     </span></pre>
                                    <pre><span>Refer attached LS-C and LS-B reports.</span><span>    </span></pre>
                                    <pre><span>Any help will be appreciated.</span><span>    </span></pre>
                                    <pre><span>     </span></pre>
                                    <pre><span>     </span></pre>
                                    <pre><span>Thanks & Regards</span><span>    </span></pre>
                                    <pre><span>     </span></pre>
                                    <pre><span>Bhartendu Awasthi</span><span>    </span></pre>
                                  </div>
                                </div>
                              </div>
                            </div>
                            <br>
_______________________________________________<br>
                            Bldg-sim mailing list<br>
                            <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
                              target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
                            To unsubscribe from this mailing list send
                             a blank message to <a
                              moz-do-not-send="true"
                              href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"
                              target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
                            <br>
                          </blockquote>
                        </div>
                        <br>
                        <br>
                        <br>
                        -- <br>
                        <div>
                          <div><span><span><span></span></span><span><span></span></span><span><span>Regards,<br>
                                </span></span></span></div>
                          <div><span><span><span></span><br>
                                David S. Wood<br>
                                Principal<br>
                                Wood, Byk & Associates<br>
                                office:    <a moz-do-not-send="true"
                                  href="tel:610.347.0710"
                                  value="+16103470710" target="_blank">610.347.0710</a><br>
                              </span></span></div>
                          <span><span>mobile:  <a
                                moz-do-not-send="true"
                                href="tel:610.247.1208"
                                value="+16102471208" target="_blank">610.247.1208</a></span></span><br>
                        </div>
                      </div>
                      <pre><fieldset></fieldset>
_______________________________________________
Bldg-sim mailing list
<a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a moz-do-not-send="true" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
                    </blockquote>
                  </div>
                </div>
              </div>
              <br>
              _______________________________________________<br>
              Bldg-sim mailing list<br>
              <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
                target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
              To unsubscribe from this mailing list send  a blank
              message to <a moz-do-not-send="true"
                href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"
                target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
              <br>
            </blockquote>
          </div>
          <br>
        </div>
      </div>
    </blockquote>
  </body>
</html>