<div>Thank you again Brendan.</div>
<div> </div>
<div>I will apply DCV for my proposed building and ASHRAE 62.1 minimum for Baseline.</div>
<div>And can I apply the <strong>same</strong> min OA flow for both proposed and baseline, for the systems in which DCV is required by the standard(6.4.3.9)? </div>
<div> </div>
<div>Thank you!</div>
<div><strong></strong> </div>
<div> </div>
<div class="gmail_quote">2013/7/23 Hall, Brendan <span dir="ltr"><<a href="mailto:BHall@karpinskieng.com" target="_blank">BHall@karpinskieng.com</a>></span><br>
<blockquote style="BORDER-LEFT:#ccc 1px solid;MARGIN:0px 0px 0px 0.8ex;PADDING-LEFT:1ex" class="gmail_quote">
<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt">When applying DCV where it’s not required, the baseline should be set constant at the 62.1 minimum and the proposed should be set as designed. If you aren’t seeing any savings, make sure you have the cfm per person and the cfm per area set at the zone level. That is what is used to vary the amount of OA needed at the system level based on the occupancy schedule. There are a couple ways to input DCV but that is the one that seems to work most consistently for me. Hope that helps.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';FONT-SIZE:11pt">Brendan Hall, PE, LEED AP </span><span style="FONT-FAMILY:'Calibri','sans-serif';FONT-SIZE:8pt">BD+C</span><span style="FONT-FAMILY:'Calibri','sans-serif';FONT-SIZE:11pt"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';FONT-SIZE:11pt">Engineer, Mechanical<u></u><u></u></span></p>
<p class="MsoNormal"><span style="FONT-FAMILY:'Arial','sans-serif';COLOR:red;FONT-SIZE:13.5pt">karpinski<br></span><span style="FONT-FAMILY:'Arial','sans-serif';COLOR:#1f497d;FONT-SIZE:7.5pt">ENGINEERING</span><span style="FONT-FAMILY:'Arial','sans-serif';COLOR:#1f497d;FONT-SIZE:10pt"><br>
3135 Euclid Avenue<br>Cleveland, OH 44115<br></span><span style="FONT-FAMILY:'Arial','sans-serif';COLOR:red;FONT-SIZE:10pt">P</span><span style="FONT-FAMILY:'Arial','sans-serif';COLOR:#1f497d;FONT-SIZE:10pt"> <a href="tel:216.391.3700" target="_blank"><span style="COLOR:blue">216.391.3700</span></a> Ext 3111<br>
</span><span style="FONT-FAMILY:'Arial','sans-serif';COLOR:red;FONT-SIZE:10pt">E</span><span style="FONT-FAMILY:'Arial','sans-serif';COLOR:navy;FONT-SIZE:10pt"> </span><u><span style="FONT-FAMILY:'Arial','sans-serif';COLOR:blue;FONT-SIZE:10pt"><a title="mailto:myuhasz@karpinskieng.com" href="mailto:bhall@karpinskieng.com" target="_blank"><span style="COLOR:blue">bhall@karpinskieng.com</span></a></span></u><span style="FONT-FAMILY:'Arial','sans-serif';COLOR:blue;FONT-SIZE:10pt"><br>
</span><span style="FONT-FAMILY:'Arial','sans-serif';COLOR:red;FONT-SIZE:10pt">W </span><u><span style="FONT-FAMILY:'Arial','sans-serif';COLOR:blue;FONT-SIZE:10pt">www.<a title="http://www.karpinskieng.com/" href="http://www.karpinskieng.com/" target="_blank"><span style="COLOR:blue">karpinskieng.com</span></a></span></u><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="FONT-FAMILY:'Calibri','sans-serif';COLOR:#1f497d;FONT-SIZE:11pt"><u></u> <u></u></span></p>
<div style="BORDER-BOTTOM:medium none;BORDER-LEFT:medium none;PADDING-BOTTOM:0in;PADDING-LEFT:0in;PADDING-RIGHT:0in;BORDER-TOP:#b5c4df 1pt solid;BORDER-RIGHT:medium none;PADDING-TOP:3pt">
<p class="MsoNormal"><b><span style="FONT-FAMILY:'Tahoma','sans-serif';FONT-SIZE:10pt">From:</span></b><span style="FONT-FAMILY:'Tahoma','sans-serif';FONT-SIZE:10pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>DongEun Kim<br>
<b>Sent:</b> Tuesday, July 23, 2013 3:55 AM<br><b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] DCV application (Baseline minimum OA)<u></u><u></u></span></p>
</div>
<div>
<div class="h5">
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal">Hi All!<u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">I am currently involved in a LEED project and the building applies DCV system.<u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">My question is, can I apply the same 'OA cfm/person' for the Baseline building?<u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">This might seem to be a silly question as we all know ASHRAE 90.1 Appx.G requires proposed and baseline building to<u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">have same 'minimum OA.' <u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">But I remember reading some people say they had LEED Review comment that says, when proposed has DCV, baseline should have its minimum OA as determined by ASHRAE 62.1.<u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">This is an important issue in that when I follow above review comment and put minimum OA per ASHRAE 62.1, there's almost no saving achieved from applying DCV. :(<u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">Any comments equester?<u></u><u></u></p></div>
<div>
<p class="MsoNormal"> <u></u><u></u></p></div>
<div>
<p class="MsoNormal">Kim<u></u><u></u></p></div></div></div></div></div></blockquote></div><br>