<div>Hi eQuesters!</div>
<div> </div>
<div>I am modeling a Laboratory building with Fume Hoods (Climate zone 4A).</div>
<div> </div>
<div>Even though Supply Air is 100% Outside Air, the AHU  for the laboratory space doesn't have Energy Recovery because, as the Fumehood </div>
<div> </div>
<div>operates, there won't be much exhaust air to recover heat from.</div>
<div> </div>
<div>Question is.. What about the Baseline?  Should I install Energy Recovery for the Baseline?</div>
<div> </div>
<div>Per ASHRAE 90.1  Appx.G 3.1.2.10, the baseline Laboratory AHUs should be installed with Energy Recovery (SA>2400L/s & OA 70%).</div>
<div> However, there are two 'Exceptions(see below)' that makes me wonder whether I should apply Energy Recovery for the Baseline.</div>
<div> </div>
<div><strong>b.</strong> Systems exhausting <u>toxic, flammables, or corrosive fumes</u> or paint of dust. This exception shall only be used if exhaust air energy recovery is not used in the proposed design.---> <strong>I assume laboratory exhaust air fits into the underlined characteristics.</strong></div>

<div> </div>
<div><strong>f.</strong> Where the largest exhaust source is less than 75% of the design outdoor airflow. This exception shall only be used is exhaust air energy recovery is not used in the proposed design.--> <strong>As the main exhaust happens through Fume Hood, the AHU will seldom get the exhaust air more than 75% of OA.</strong></div>

<div><strong></strong> </div>
<div>What do you think equesters?</div>
<div> </div>
<div>Any comment will be greatly appreciated!</div>
<div> </div>
<div>Thank you.</div>
<div> </div>
<div>Kim</div>