    <div class="moz-cite-prefix">Personally I would have made the same
      conversion from efficiency to HIR. I'm not aware of a conversion
      that will take an efficiency of 77% and get you an HIR of 1.21.<br>
      <br>
      I think the best course of action would be to contact the review
      team directly. They are fairly responsive to questions, and it
      helps avoid the guessing game.<br>
      <br>
      I think your other option would be to writeup your confusion while
      addressing the comments. You could explain the potential impact on
      the model with the two values. It is unlikely the reviewer would 
      deny the whole credit if they don't like the input, they may just
      adjust your results. <br>
      <br>
      This is the kind of grey area that you can waste hours and hours
      and not really accomplish anything. <br>
      <br>
      - Steve<br>
      <br>
      On 7/5/2013 7:32 AM, vamshi ranga wrote:<br>
    </div>
    <blockquote
cite="mid:CAKLY+AbZr8c8JuDdZnbhu-EVzUFAfpULE8rg6B6S0T9eZZX0yQ@mail.gmail.com"
      type="cite">
      <div dir="ltr">Dear All,
        <div><br>
        </div>
        <div style="">Could any help me out with the issue. Is it like,
          this site is only meant for doubts related to eQUEST? (I asked
          the related doubt 2 months back also, but could not get any
          answer. On the same we got the LEED reviewer comment). If so,
          requested to suggest me the sites where I can ask the doubts
          related to ASHRAE.</div>
        <div style=""><br>
        </div>
        <div style="">Your valuable time is appreciated.</div>
        <div style=""><br>
        </div>
        <div style="">Thanks,</div>
        <div style="">Vamshi.</div>
      </div>
      <div class="gmail_extra"><br>
        <br>
        <div class="gmail_quote">On Wed, Jul 3, 2013 at 1:01 PM, vamshi
          ranga <span dir="ltr"><<a moz-do-not-send="true"
              href="mailto:vamshiranga@gmail.com" target="_blank">vamshiranga@gmail.com</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div dir="ltr">Dear All,
              <div><br>
              </div>
              <div>Thank you very much for your time. It was very useful
                information and good learning for me. I would be
                following the conservative approach as suggested by Nick
                for boiler HIR modeling.</div>
              <div><br>
              </div>
              <div>I also would be requiring your esteemed assistance on
                the Query No. 2. Which is the major issue for the LEED
                Reviewer.</div>
              <div><br>
              </div>
              <div>As queried by Ms. Ramya Shivkumar, there is no MPR
                issue and the reviewer does not have any problem of
                modeling two building together. The issue is about which
                system needs to be modeled and interpretation of section
                G 3.1.1 as queried in my previous mail.</div>
              <div><br>
              </div>
              <div>Thanks,</div>
              <div>Vamshi.</div>
            </div>
            <div class="HOEnZb">
              <div class="h5">
                <div class="gmail_extra"><br>
                  <br>
                  <div class="gmail_quote">On Tue, Jul 2, 2013 at 11:39
                    PM, Daniel Knapp <span dir="ltr"><<a
                        moz-do-not-send="true"
                        href="mailto:danielk@arborus.ca" target="_blank">danielk@arborus.ca</a>></span>
                    wrote:<br>
                    <blockquote class="gmail_quote" style="margin:0 0 0
                      .8ex;border-left:1px #ccc solid;padding-left:1ex">Just
                      to followup with a little more clarity, my hope
                      was that the modellers have access to the boiler
                      specs with fuel input and heat output information
                      that they can use to define the eQuest HIR.  If
                      all they have is the combustion efficiency then
                      yes, they are in the 90.1 no-man's land of how to
                      arrive at an overall thermal efficiency given only
                      the combustion efficiency.<br>
                      <div>
                        <div><br>
                          On 2013-07-02, at 1:54 PM, Daniel Knapp <<a
                            moz-do-not-send="true"
                            href="mailto:danielk@arborus.ca"
                            target="_blank">danielk@arborus.ca</a>>
                          wrote:<br>
                          <br>
                          > Hi Nick,<br>
                          ><br>
                          > I agree entirely with what you're saying
                          here and have read through the attached
                          discussion with great interest.  I sincerely
                          appreciate your contributions in not only
                          thinking this issue out in great detail but
                          also in making the effort to share your
                          thoughts with the group.<br>
                          ><br>
                          > To be clear, I wasn't meaning to downplay
                          your response which I think is helpful to the
                          question at hand.  In regards to this specific
                          question posed by the modeller, my
                          interpretation of the reviewer comment was
                          that the reviewer was speaking to the
                          modelling of the Proposed design efficiency,
                          i.e. that they were modelling it at 82% due to
                          the combustion efficiency being 82% when they
                          really need to model the Proposed design
                          according to the overall efficiency of the
                          boiler (fuel input vs. heat output) which may
                          be lower than 82%.<br>
                          ><br>
                          > With best regards,<br>
                          > Dan<br>
                          ><br>
                          > —<br>
                          > Daniel Knapp, PhD, P Phys, LEED® AP O+M<br>
                          > <a moz-do-not-send="true"
                            href="mailto:danielk@arborus.ca"
                            target="_blank">danielk@arborus.ca</a><br>
                          ><br>
                          > Arborus Consulting<br>
                          > Energy Strategies for the Built
                          Environment<br>
                          > <a moz-do-not-send="true"
                            href="http://www.arborus.ca" target="_blank">www.arborus.ca</a><br>
                          > 76 Chamberlain Avenue<br>
                          > Ottawa, ON, K1S 1V9<br>
                          > Phone: <a moz-do-not-send="true"
                            href="tel:%28613%29%20234-7178%20ext.%20113"
                            value="+16132347178" target="_blank">(613)
                            234-7178 ext. 113</a><br>
                          > Fax: <a moz-do-not-send="true"
                            href="tel:%28613%29%20234-0740"
                            value="+16132340740" target="_blank">(613)
                            234-0740</a><br>
                          ><br>
                          ><br>
                          ><br>
                          ><br>
                          > On 2013-07-02, at 12:40 PM, Nick Caton
                          <<a moz-do-not-send="true"
                            href="mailto:ncaton@smithboucher.com"
                            target="_blank">ncaton@smithboucher.com</a>>
                          wrote:<br>
                          ><br>
                          >> Hi Daniel!<br>
                          >><br>
                          >> The wrench in the spokes is that 90.1
                          prescribes a combustion efficiency (less
                          flue/jacket losses), without providing any
                          further guidance for how to arrive at an
                          overall thermal efficiency for modeling
                          purposes.<br>
                          >><br>
                          >> It isn't a problem isolated to
                          eQuest/DOE2, but put another way 90.1/LEED
                          only provide part of what we need to define
                          baseline HIR inputs for a comparison to
                          real-world equipment and losses.  A full
                          discussion is within the attached thread if
                          you're interested =).<br>
                          >><br>
                          >> This of course might have nothing to
                          do with Vamshi's reviewer's commentary - I
                          don't think that issue has been made clear
                          just yet...<br>
                          >><br>
                          >> ~Nick<br>
                          >><br>
                          >> NICK CATON, P.E.<br>
                          >> SENIOR ENGINEER<br>
                          >><br>
                          >> Smith & Boucher Engineers<br>
                          >> 25501 west valley parkway, suite 200<br>
                          >> olathe, ks 66061<br>
                          >> direct <a moz-do-not-send="true"
                            href="tel:913.344.0036" value="+19133440036"
                            target="_blank">913.344.0036</a><br>
                          >> fax <a moz-do-not-send="true"
                            href="tel:913.345.0617" value="+19133450617"
                            target="_blank">913.345.0617</a><br>
                          >> <a moz-do-not-send="true"
                            href="http://www.smithboucher.com"
                            target="_blank">www.smithboucher.com</a><br>
                          >><br>
                          >> -----Original Message-----<br>
                          >> From: Daniel Knapp [mailto:<a
                            moz-do-not-send="true"
                            href="mailto:danielk@arborus.ca"
                            target="_blank">danielk@arborus.ca</a>]<br>
                          >> Sent: Tuesday, July 02, 2013 11:13 AM<br>
                          >> To: Nick Caton<br>
                          >> Cc: r s; vamshi ranga; <a
                            moz-do-not-send="true"
                            href="mailto:equest-users@lists.onebuilding.org"
                            target="_blank">equest-users@lists.onebuilding.org</a><br>
                          >> Subject: Re: [Equest-users] Boiler
                          HIR and Section G3.1.1<br>
                          >><br>
                          >> I don't know if this helps, but from
                          the perspective of eQuest/DOE-2, the HIR is
                          the ratio of the fuel heat input to the boiler
                          to the heating capacity at full load.  I.e.
                          all DOE-2 cares about is how much fuel to
                          assign each unit of heat produced for the
                          building.  If you know what the fuel input and
                          the heating capacity at full load are you may
                          be able to bypass the thorny nature of the
                          combustion efficiency vs. thermal efficiency
                          question?<br>
                          >><br>
                          >> Cheers,<br>
                          >> Dan<br>
                          >><br>
                          >> -<br>
                          >> Daniel Knapp, PhD, P Phys, LEED(r) AP
                          O+M<br>
                          >> <a moz-do-not-send="true"
                            href="mailto:danielk@arborus.ca"
                            target="_blank">danielk@arborus.ca</a><br>
                          >><br>
                          >> Arborus Consulting<br>
                          >> Energy Strategies for the Built
                          Environment <a moz-do-not-send="true"
                            href="http://www.arborus.ca" target="_blank">www.arborus.ca</a><br>
                          >> 76 Chamberlain Avenue<br>
                          >> Ottawa, ON, K1S 1V9<br>
                          >> Phone: <a moz-do-not-send="true"
                            href="tel:%28613%29%20234-7178%20ext.%20113"
                            value="+16132347178" target="_blank">(613)
                            234-7178 ext. 113</a><br>
                          >> Fax: <a moz-do-not-send="true"
                            href="tel:%28613%29%20234-0740"
                            value="+16132340740" target="_blank">(613)
                            234-0740</a><br>
                          >><br>
                          >><br>
                          >><br>
                          >><br>
                          >> On 2013-07-02, at 11:46 AM, Nick
                          Caton <<a moz-do-not-send="true"
                            href="mailto:ncaton@smithboucher.com"
                            target="_blank">ncaton@smithboucher.com</a>>
                          wrote:<br>
                          >><br>
                          >>> Regarding boiler HIR input vs.
                          efficiency... Your reviewer's commentary isn't
                          clear by your description, but you might find
                          the attached recent discussion informative
                          regarding thermal vs. combustion efficiencies.<br>
                          >>><br>
                          >>> The issue of whether it's
                          appropriate to model boiler thermal efficiency
                          (inclusive of flue/jacket losses), and if so
                          exactly how, is to my best understanding a bit
                          of a toss-up right now for 90.1/LEED.  The
                          attached discussion thread takes the issue to
                          the sidewalk's end however, so I hope you can
                          use this to figure out where your reviewer is
                          coming from and how to respond in turn.<br>
                          >>><br>
                          >>> ~Nick<br>
                          >>><br>
                          >>> <image001.jpg><br>
                          >>><br>
                          >>> NICK CATON, P.E.<br>
                          >>> SENIOR ENGINEER<br>
                          >>><br>
                          >>> Smith & Boucher Engineers<br>
                          >>> 25501 west valley parkway, suite
                          200<br>
                          >>> olathe, ks 66061<br>
                          >>> direct <a moz-do-not-send="true"
                            href="tel:913.344.0036" value="+19133440036"
                            target="_blank">913.344.0036</a><br>
                          >>> fax <a moz-do-not-send="true"
                            href="tel:913.345.0617" value="+19133450617"
                            target="_blank">913.345.0617</a><br>
                          >>> <a moz-do-not-send="true"
                            href="http://www.smithboucher.com"
                            target="_blank">www.smithboucher.com</a><br>
                          >>><br>
                          >>> From: <a moz-do-not-send="true"
href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a><br>
                          >>> [mailto:<a moz-do-not-send="true"
href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
                          On Behalf Of r s<br>
                          >>> Sent: Tuesday, July 02, 2013
                          10:27 AM<br>
                          >>> To: vamshi ranga<br>
                          >>> Cc: <a moz-do-not-send="true"
                            href="mailto:equest-users@lists.onebuilding.org"
                            target="_blank">equest-users@lists.onebuilding.org</a><br>
                          >>> Subject: Re: [Equest-users]
                          Boiler HIR and Section G3.1.1<br>
                          >>><br>
                          >>> Hi Vamshi,<br>
                          >>><br>
                          >>> Just wondering, you say two
                          buildings? Was there any MPR issue raised
                          within PIf1 in the review about having only
                          one building per LEED submittal?<br>
                          >>><br>
                          >>> Ramya<br>
                          >>><br>
                          >>><br>
                          >>> On Tue, Jul 2, 2013 at 11:04 AM,
                          vamshi ranga <<a moz-do-not-send="true"
                            href="mailto:vamshiranga@gmail.com"
                            target="_blank">vamshiranga@gmail.com</a>>
                          wrote:<br>
                          >>> Dear All,<br>
                          >>><br>
                          >>> I have following doubts, I would
                          be very grateful for your valuable<br>
                          >>> time,<br>
                          >>><br>
                          >>> 1. We have modeled a boiler with
                          82% combustion efficiency in eQUEST<br>
                          >>> with HIR = 1.219  which is just
                          the inverse of boiler efficiency . But<br>
                          >>> from LEED reviewer, we got
                          comment saying that, HIR of 1.219 is<br>
                          >>> equivalent to 77% efficiency.
                          Could you please let us know, how to<br>
                          >>> convert combustion efficiency to
                          HIR<br>
                          >>><br>
                          >>> 2. We have two buildings, one is
                          Main Office building (7 day week, 8hr<br>
                          >>> running and Air-Conditioned, Main
                          Office building has 5 to 7% of total<br>
                          >>> two building areas) and the other
                          is Factory+Office building (7 day<br>
                          >>> week, Factory is 24 hr running
                          and Air-Conditioned with 100% of<br>
                          >>> occupancy, lighting and equipment
                          on all the time. While the Factory's<br>
                          >>> Office is 24hr running and
                          Air-Conditioned with 50% of occupancy,<br>
                          >>> lighting and equipment on all the
                          time) which are connected by<br>
                          >>> enclosed bridge (air
                          conditioned). These buildings are modeled<br>
                          >>> together in eQUEST and it comes
                          to be System 7 (Boiler for heating) as<br>
                          >>> per Table G 3.1.1. After reading
                          it for many number of times and to<br>
                          >>> confirm my understanding of the
                          section, doubts are as follows on<br>
                          >>> ASHRAE Appendix G Section G3.1.1<br>
                          >>><br>
                          >>>               - What should be
                          the system type for Main Office building
                          (Conditioned area is around 45000 Sq ft)? and
                          let me know the exception of G3.1.1 if any
                          gets applied<br>
                          >>>               - What should be
                          the system type for factory's Ground Floor
                          Office building? (Area is around 150000 Sq ft)
                          and Does the exception "Schedules that differ
                          by 40 equivalent full load hours" gets
                          applied? since the diversity is 50% for
                          factory's office, if this exception is not
                          applicable, let me know how the equivalent
                          full load hours need to be calculated )<br>
                          >>>               - What should be
                          the system type for Factory's First Floor
                          office building? (This floor is total office,
                          and ground floor factory area is of double
                          height from ground)<br>
                          >>>               - Does the
                          exceptions of Section G 3.1.1 applies at
                          building level or at each system level?
                          Exception "b" says both the things, so there
                          is confusion<br>
                          >>>               - Does the term
                          "Peak thermal loads" in exception "b" consider
                          the load added due to outside air as well?<br>
                          >>><br>
                          >>> Let me know, if you need any
                          further clarification to resolve my doubts.<br>
                          >>><br>
                          >>> Thanks,<br>
                          >>> Vamshi.<br>
                          >>><br>
                          >>>
                          _______________________________________________<br>
                          >>> Equest-users mailing list<br>
                          >>> <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
                            target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
                          >>> To unsubscribe from this mailing
                          list send  a blank message to<br>
                          >>> <a moz-do-not-send="true"
                            href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG"
                            target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
                          >>><br>
                          >>><br>
                          >>> <Mail
                          Attachment.eml>_______________________________________________<br>
                          >>> Equest-users mailing list<br>
                          >>> <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
                            target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
                          >>> To unsubscribe from this mailing
                          list send  a blank message to<br>
                          >>> <a moz-do-not-send="true"
                            href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG"
                            target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
                          >><br>
                          >> <Mail Attachment.eml><br>
                          ><br>
                          <br>
                        </div>
                      </div>
                    </blockquote>
                  </div>
                  <br>
                </div>
              </div>
            </div>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>