<div class="moz-cite-prefix">孙一峰,<br>
Ivan 是不是你的英文名字?<br>
The only difference between the different azimuths is the solar
radiation. <br>
I think you should compare the summary loads report (LS-E by
space, or LS-F for the whole building) for the different
orientations and see how much the solar heat gains, especially
through the windows, change. If you really want to get into it,
you can also print out hourly reports for the solar heat gains,
heating and cooling loads for the ground floor zones. You can
also switch weather files and see what happens. I will send you
by e-mail a different weather file for Wuhan that I've created.<br>
Good luck.<br>
<br>
Joe<br>
<br>
Joe Huang 黄昱<br>
White Box Technologies, Inc.<br>
346 Rheem Blvd., Suite 108D<br>
Moraga CA 94556<br>
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a><br>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a><br>
<a class="moz-txt-link-freetext" href="http://www.whiteboxtechnologies.com">http://www.whiteboxtechnologies.com</a><br>
(o) (925)388-0265<br>
(c) (510)928-2683<br>
"building energy simulations at your fingertips"<br>
<br>
<br>
<br>
On 5/22/2013 7:02 PM, Yf Sun wrote:<br>
</div>
<blockquote
cite="mid:CAPz2vbMq9AqymAnWNfd1NSF_yePQ5zvVvsm4N3DOkftBrnoB6A@mail.gmail.com"
type="cite">
<meta http-equiv="Context-Type" content="text/html; charset=UTF-8">
<div dir="ltr">Hi dear equesters!<br>
<div class="gmail_quote">
<div dir="ltr">
<div>I was doing orientation study on my office module i can
not figure out why i got 26% OF HOURS OUTSIDE OF
THROTTLING RANGE in BEPU report when i set the azimuth at
15 degrees for ground floor, the system worked in
throttling range when azimuth at 10 or 20 degrees! the
weather file i used is CTYW Wuhan (china). </div>
<div><br>
</div>
<div>I attached the model, reports and the weather file. Any
help will be appreciated!<span class="HOEnZb"><br>
<div><br>
</div>
</span></div>
</div>
</div>
<div><br>
</div>
-- <br>
<div dir="ltr">
<div>Best regards<br>
</div>
<div>孙一峰</div>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
</body>
</html>