<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    <div class="moz-cite-prefix">Dante,<br>
      <br>
      How are you modeling the two types of windows in eQUEST and
      EnergyPlus?  If you're using the Simple Window Model in both
      programs, the difference may be due to different assumptions about
      the solar heat characteristics in their Simple Window Models. 
      Without seeing the inputs, I can only guess, but it looks like
      with EnergyPlus the only change is in the U-value, which as you
      say has a small effect due to the small delta Ts, but with eQUEST,
      there may also be changes in the solar heat gain, which would also
      impact the building energy use.<br>
      <br>
      Joe<br>
      <br>
      Joe Huang    <br>
      White Box Technologies, Inc.<br>
      346 Rheem Blvd., Suite 108D<br>
      Moraga CA 94556<br>
      <a class="moz-txt-link-abbreviated"
        href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a><br>
      <a class="moz-txt-link-freetext"
        href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a><br>
      <a class="moz-txt-link-freetext"
        href="http://www.whiteboxtechnologies.com">http://www.whiteboxtechnologies.com</a><br>
      (o) (925)388-0265<br>
      (c) (510)928-2683<br>
      "building energy simulations at your fingertips"<br>
      <br>
      On 5/22/2013 9:33 AM, Dante Garcia wrote:<br>
    </div>
    <blockquote
cite="mid:017FFF8E071C8C4A80F977C5763EF3C4BD6AA073@EXCH-MBX-01.css.local"
      type="cite">
      <meta http-equiv="Context-Type" content="text/html;
        charset=us-ascii">
      <meta name="Generator" content="Microsoft Word 14 (filtered
        medium)">
      <div class="WordSection1">
        <p class="MsoNormal"><span lang="EN-US">Hi all,</span></p>
        <p class="MsoNormal"><span lang="EN-US">I am new using eQuest, I
            made a model in the DDWizard.</span></p>
        <p class="MsoNormal"><span lang="EN-US">When I use a high
            performance glass U-value = 0.31, I got less efficiency than
            when I modeled using an U-value =0.70, and the difference is
            about 4%, using enegyPlus, that is the program that I have
            been using for a year show me differences in less than 0.5%
            selecting diferents U-value because the range of
            temperatures is between 15-29 in a whole year in my country)</span></p>
        <p class="MsoNormal"><span lang="EN-US"> </span></p>
        <p class="MsoNormal"><span lang="EN-US">PDta: This is my first
            model using eQuest (I have another model that a friend gave
            me, I change the wheater and model with both performance of
            glasses and I got same result, So, I think that the problem
            is in my model)</span></p>
        <p class="MsoNormal"><span lang="EN-US"> </span></p>
        <p class="MsoNormal"><span lang="EN-US">Someone ran into with
            this problem?</span></p>
        <p class="MsoNormal"><span lang="EN-US">Any help will be
            appreciate,</span></p>
        <p class="MsoNormal"><span lang="EN-US"> </span></p>
        <p class="MsoNormal"><span lang="EN-US">I have been using the
            sim file to figure out the problem but I could not find
            indoor temperatures in each space.</span></p>
        <p class="MsoNormal"><span lang="EN-US"> </span></p>
        <p class="MsoNormal"><b><span lang="ES">Dante Garcia
            </span></b></p>
        <p class="MsoNormal"><b><span lang="ES">LEED Green Associate</span></b></p>
        <p class="MsoNormal"><b><span lang="ES"> </span></b></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>