<div style="line-height:1.7;color:#000000;font-size:14px;font-family:arial">Hi Nick,<div>Thank you so much for your patience!</div><div>I really like your answer!</div><div>Esmi<br><br><br><br><br><div></div><div id="divNeteaseMailCard"></div><br>ÔÚ 2013-04-23 00:40:51£¬"Nick Caton" <ncaton@smithboucher.com> Ð´µÀ£º<br> <blockquote id="isReplyContent" style="PADDING-LEFT: 1ex; MARGIN: 0px 0px 0px 0.8ex; BORDER-LEFT: #ccc 1px solid">



<style></style>


<div class="WordSection1">
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">This is something I haven¡¯t ever fully resolved for myself actually¡­ eQuest contains a set of DOE-2.2 manual volumes, found under the eQuest ¡°Help¡± menu. 
<o:p></o:p></span></p>
<p class="MsoNormal"><img width="298" height="253" id="Picture_x0020_5" src="cid:7c67475c$1$13e3c54ccd3$Coremail$e2fye2$163.com"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">I believe the first 4 volumes are the ¡°core¡± DOE2.2 volumes, and the other volumes have been appended over time as eQuest/DOE2 have developed in more recent
 years.  <i><u>I¡¯m not clear on</u></i> whether these in sum are any more or less ¡°complete¡± than past or present manuals for the underlying DOE2 simulation engine itself.  I am pretty sure some parts of this are compiled by & for eQuest specifically (Volume
 5: Compliance Analysis in particular jumps to mind).<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">More specifically to Esmireta¡¯s follow up query, you can find the entry I cited on Chiller Energy Consumption, and explore the associated inputs further, in
 a few ways:<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">First, navigate to ¡°DOE-2 Help¡± from the Help context menu.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><img width="431" height="245" id="Picture_x0020_3" src="cid:607e28d2$2$13e3c54ccd4$Coremail$e2fye2$163.com"></span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">From here, you can navigate to the previously appended chiller energy consumption entry.  Here¡¯s a better citation for those who aren¡¯t seeing images in my
 emails:  Volume 2 > HVAC Components > CHILLER > Chiller Energy Consumption.  You can also read up on all the associated BDL inputs by highlighting the branch elements following in the tree view:<o:p></o:p></span></p>
<p class="MsoNormal"><img width="1002" height="910" id="Picture_x0020_2" src="cid:7aaa247b$3$13e3c54ccd5$Coremail$e2fye2$163.com"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Second, while working in eQuest and particularly after the wizards, you can also right-click most input fields to pull up a context-sensitive index of sorts
 to lead you to appropriate entries in the DOE2 manuals ¨C this is the primary way I access & navigate the supporting documentation in practice:<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><img width="1044" height="569" id="Picture_x0020_4" src="cid:38414627$4$13e3c54ccd5$Coremail$e2fye2$163.com"></span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Regards,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">~Nick<o:p></o:p></span></p>
<div>
<p class="MsoNormal"><b><span style="font-size:11.0pt;font-family:"Stylus BT","sans-serif";color:#2D4D5E"><br>
<br>
<o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt;font-family:"Stylus BT","sans-serif";color:#2D4D5E"><o:p> </o:p></span></b></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><img width="119" height="37" id="Picture_x0020_1" src="cid:4564c74b$5$13e3c54ccd6$Coremail$e2fye2$163.com" alt="cid:489575314@22072009-0ABB"></span><b><span style="font-size:11.0pt;font-family:"Stylus BT","sans-serif";color:#2D4D5E"><o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt;font-family:"Stylus BT","sans-serif";color:#2D4D5E"><o:p> </o:p></span></b></p>
<p class="MsoNormal"><b><span style="font-family:"Stylus BT","sans-serif";color:#2D4D5E">NICK CATON, P.E.<o:p></o:p></span></b></p>
<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Calibri","sans-serif";color:#CC9900">SENIOR ENGINEER<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Calibri","sans-serif";color:#CC9900"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">Smith & Boucher Engineers</span><span style="font-size:7.5pt;color:#CC9900"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">25501 west valley parkway, suite 200<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">olathe, ks 66061<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">direct 913.344.0036<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">fax 913.345.0617<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><a href="www.smithboucher.com" title="blocked::www.smithboucher.com"><span style="font-size:10.0pt">www.smithboucher.com</span></a></span><u><span style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:blue">
</span></u><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>
</div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext"> <a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Joe Huang<br>
<b>Sent:</b> Monday, April 22, 2013 10:40 AM<br>
<b>To:</b> Esmireta<br>
<b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] How to set the COP of a chiller as constant in eQuest?<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">I was referring to the DOE-2 Supplement, Version 2.1E, produced by LBNL in 1993 (LBL-34947).  I have not looked at the help function of eQUEST, so I can't tell how detailed is it.<br>
<br>
Joe<br>
<br>
<o:p></o:p></p>
<pre>Joe Huang<o:p></o:p></pre>
<pre>White Box Technologies, Inc.<o:p></o:p></pre>
<pre>346 Rheem Blvd., Suite 108D<o:p></o:p></pre>
<pre>Moraga CA 94556<o:p></o:p></pre>
<pre><a href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a><o:p></o:p></pre>
<pre><a href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a><o:p></o:p></pre>
<pre>(o) (925)388-0265<o:p></o:p></pre>
<pre>(c) (510)928-2683<o:p></o:p></pre>
<pre>"building energy simulations at your fingertips"<o:p></o:p></pre>
<p class="MsoNormal"><br>
On 4/21/2013 9:49 PM, Esmireta wrote: <o:p></o:p></p>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">Hi Joe,
<o:p></o:p></span></p>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">Thanks for your reply!<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">Is the DOE-2.2 manual the DOE help in the eQuest?<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">Esmi<br>
<br>
<br>
<br>
<br>
<br>
At 2013-04-18 03:17:00,"Joe Huang" <a href="mailto:yjhuang@whiteboxtechnologies.com"><yjhuang@whiteboxtechnologies.com></a> wrote:<br>
<br>
<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">Do you not have a copy of a DOE-2.2 or DOE-2.1E manual?  That would make it hard to understand how DOE-2 works.<br>
DOE-2 has many performance curves, depending on the type of equipment. The EIR-FT curves are either bi-linear or bi-quadratic functions of the entering wetbulb and outdoor drybulb temperature.  The EIR-FPLR curves can be linear, quadratic, or cubic functions
 of the Part Load Ratio (PLR). <br>
<br>
By the way,what I said yesterday was in reference to packaged SYSTEMS.  If your model contains a PLANT model with a Chiller, then<br>
the keywords for the chiller performance curves change somewhat.<br>
<br>
Joe<br>
<br>
<o:p></o:p></span></p>
<pre>Joe Huang<o:p></o:p></pre>
<pre>White Box Technologies, Inc.<o:p></o:p></pre>
<pre>346 Rheem Blvd., Suite 108D<o:p></o:p></pre>
<pre>Moraga CA 94556<o:p></o:p></pre>
<pre><a href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a><o:p></o:p></pre>
<pre><a href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a><o:p></o:p></pre>
<pre>(o) (925)388-0265<o:p></o:p></pre>
<pre>(c) (510)928-2683<o:p></o:p></pre>
<pre>"building energy simulations at your fingertips"<o:p></o:p></pre>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif""><br>
On 4/16/2013 11:09 PM, Esmireta wrote: <o:p></o:p></span></p>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">Hi Joe,
<o:p></o:p></span></p>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">In the simulation of a district cooling system, the guidance requires a virtual plant with a constant average efficiency.<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">In the DOE curves, how can I know the meaning of the equation and the coefficients in it? It seems there is no useful information in the DOE help.<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">Thanks!<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">Esmi<br>
<br>
<br>
<br>
<br>
<br>
At 2013-04-17 10:35:35,"Joe Huang" <a href="mailto:yjhuang@whiteboxtechnologies.com"><yjhuang@whiteboxtechnologies.com></a> wrote:<br>
<br>
<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">DOE-2 modifies the COOL-EIR using several curves COOL-EIR-FT as a function of outdoor conditions and COOL-EIR-FPLR as a function of the Part Load Ratio. I suppose you could
 set those to be constant. Another way would be to just take the Cooling Load from the SS-D report and divide that by your constant COP.  But my question would be, why do you want to do that ?<br>
<br>
Joe<br>
<br>
<o:p></o:p></span></p>
<pre>Joe Huang<o:p></o:p></pre>
<pre>White Box Technologies, Inc.<o:p></o:p></pre>
<pre>346 Rheem Blvd., Suite 108D<o:p></o:p></pre>
<pre>Moraga CA 94556<o:p></o:p></pre>
<pre><a href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a><o:p></o:p></pre>
<pre><a href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a><o:p></o:p></pre>
<pre>(o) (925)388-0265<o:p></o:p></pre>
<pre>(c) (510)928-2683<o:p></o:p></pre>
<pre>"building energy simulations at your fingertips"<o:p></o:p></pre>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif""><br>
On 4/16/2013 6:55 PM, Esmireta wrote: <o:p></o:p></span></p>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">Dear all,
<o:p></o:p></span></p>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">I wonder how to set the COP of a chiller as constant? after I set the chiller type, the electric input ratio type is determined, which means the self-made constant curve cannot
 be input.<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">Thanks!<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif"">Esmi<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif""><br>
<br>
<br>
<o:p></o:p></span></p>
<pre><o:p> </o:p></pre>
<pre>_______________________________________________<o:p></o:p></pre>
<pre>Equest-users mailing list<o:p></o:p></pre>
<pre><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><o:p></o:p></pre>
<pre>To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></pre>
</div>
</div>
<p class="MsoNormal"><span style="font-size:10.5pt;font-family:"Arial","sans-serif""><br>
<br>
<br>
<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><br>
<br>
<br>
<o:p></o:p></p>
</div>


</blockquote></div></div><br><br><span title="neteasefooter"><span id="netease_mail_footer"></span></span>