<div dir="ltr"><div><br></div><div class="gmail_quote">Hi All,<br><div dir="ltr"><div><br></div><div>Section G3.1.1 (b), says,</div><div><br></div><div><div>If the baseline HVAC system type is 5, 6, 7, or 8, use separate single-zone systems conforming with the requirements of System 3 or System 4 (depending on building heating source) for any spaces that have occupancy or process loads or schedules that differ significantly from the rest of the building. <b>Peak thermal loads that differ by 10 Btu/h⋅ft2 or more</b> from the <b>average</b> of other <b>spaces served by the system or schedules that differ by more than 40 equivalent full load hours per week</b> from other spaces served by the system are considered to differ significantly. Examples where this exception may be applicable include, but are not limited to, computer server rooms, natatoriums, and continually occupied security areas.</div>
<div><b><br></b></div><div>1. Is the term "Peak thermal loads" referring to loads caused by envelope, occupancy, lighting infiltration and equipment only? or it also includes loads caused by "fresh air" also?</div>
<div style>2. Is "Thermal loads" referring to Cooling load or Heating load or Sum of both coooling and heating?</div>
<div>3. What does "40 equivalent full load hours" means? For example, I have one room whose schedules are 24hrs and 100% occup, light, equip at the same time I have other rooms, which are 24hrs and 50% occup, light, equip etc. So, I think, 24hrs with 100% should be modeled with System 3(my heating source is boiler). Correct me, if I am wrong</div>
<div><br></div><div>Thanks in advance for the help.</div><div><br></div><div>Thank you,</div><div>Vamshi.</div></div></div>
</div><br></div>