    Do you not have a copy of a DOE-2.2 or DOE-2.1E manual?  That would
    make it hard to understand how DOE-2 works.<br>
    DOE-2 has many performance curves, depending on the type of
    equipment. The EIR-FT curves are either bi-linear or bi-quadratic
    functions of the entering wetbulb and outdoor drybulb temperature. 
    The EIR-FPLR curves can be linear, quadratic, or cubic functions of
    the Part Load Ratio (PLR). <br>
    <br>
    By the way,what I said yesterday was in reference to packaged
    SYSTEMS.  If your model contains a PLANT model with a Chiller, then<br>
    the keywords for the chiller performance curves change somewhat.<br>
    <br>
    Joe<br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <br>
    On 4/16/2013 11:09 PM, Esmireta wrote:
    <blockquote
      cite="mid:935b773.6a8c.13e169d22c4.Coremail.e2fye2@163.com"
      type="cite">
      <div style="line-height: 1.7; color: rgb(0, 0, 0); font-size:
        14px; font-family: arial;">Hi Joe,
        <div>In the simulation of a district cooling system, the
          guidance requires a virtual plant with a constant average
          efficiency.</div>
        <div>In the DOE curves, how can I know the meaning of the
          equation and the coefficients in it? It seems there is no
          useful information in the DOE help.</div>
        <div>Thanks!</div>
        <div>Esmi<br>
          <br>
          <br>
          <br>
          <br>
          <br>
          At 2013-04-17
          10:35:35,"Joe Huang" <a class="moz-txt-link-rfc2396E" href="mailto:yjhuang@whiteboxtechnologies.com"><yjhuang@whiteboxtechnologies.com></a>
          wrote:<br>
          <blockquote id="isReplyContent" style="padding-left: 1ex;
            margin: 0px 0px 0px 0.8ex; border-left: 1px solid rgb(204,
            204, 204);"> DOE-2 modifies the COOL-EIR using several
            curves COOL-EIR-FT as a function of outdoor conditions and
            COOL-EIR-FPLR as a function of the Part Load Ratio. I
            suppose you could set those to be constant. Another way
            would be to just take the Cooling Load from the SS-D report
            and divide that by your constant COP.  But my question would
            be, why do you want to do that ?<br>
            <br>
            Joe<br>
            <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
            <br>
            On 4/16/2013 6:55 PM, Esmireta wrote:
            <blockquote
              cite="mid:1c92a31c.2da3.13e15b3f21b.Coremail.e2fye2@163.com"
              type="cite">
              <div>Dear all,
                <div>I wonder how to set the COP of a chiller as
                  constant? after I set the chiller type, the electric
                  input ratio type is determined, which means the
                  self-made constant curve cannot be input.</div>
                <div>Thanks!</div>
                <div>Esmi</div>
              </div>
              <br>
              <br>
              <span title="neteasefooter"><span></span></span>
              <pre wrap=""><fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
            </blockquote>
          </blockquote>
        </div>
      </div>
      <br>
      <br>
      <span title="neteasefooter"><span id="netease_mail_footer"></span></span>
    </blockquote>
  </body>
</html>