    DOE-2 modifies the COOL-EIR using several curves COOL-EIR-FT as a
    function of outdoor conditions and COOL-EIR-FPLR as a function of
    the Part Load Ratio. I suppose you could set those to be constant.
    Another way would be to just take the Cooling Load from the SS-D
    report and divide that by your constant COP.  But my question would
    be, why do you want to do that ?<br>
    <br>
    Joe<br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <br>
    On 4/16/2013 6:55 PM, Esmireta wrote:
    <blockquote
      cite="mid:1c92a31c.2da3.13e15b3f21b.Coremail.e2fye2@163.com"
      type="cite">
      <meta http-equiv="Context-Type" content="text/html; charset=GBK">
      <div>Dear all,
        <div>I wonder how to set the COP of a chiller as constant? after
          I set the chiller type, the electric input ratio type is
          determined, which means the self-made constant curve cannot be
          input.</div>
        <div>Thanks!</div>
        <div>Esmi</div>
      </div>
      <br>
      <br>
      <span title="neteasefooter"><span></span></span>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>