<div dir="ltr">Hi All,<div><br></div><div style>Section G3.1.1 (b), says,</div><div style><br></div><div style><div>If the baseline HVAC system type is 5, 6, 7, or 8, use separate single-zone systems conforming with the requirements of System 3 or System 4 (depending on building heating source) for any spaces that have occupancy or process loads or schedules that differ significantly from the rest of the building. <b>Peak thermal loads that differ by 10 Btu/h⋅ft2 or more</b> from the average of other <b>spaces served by the system or schedules that differ by more than 40 equivalent full load hours per week</b> from other spaces served by the system are considered to differ significantly. Examples where this exception may be applicable include, but are not limited to, computer server rooms, natatoriums, and continually occupied security areas.</div>
<div><b><br></b></div><div style>1. Is the term "Peak thermal loads" referring to loads caused by envelope, occupancy, infiltration and equipment only? or it also includes loads caused "fresh air" also?</div>
<div style>2. From which report of SIM file, we can get data related to "difference of 40 equivalent full load hours"</div><div style>3. Considering that internal loads in two different spaces are on 50% for one space and on 100% for other space, Can we assign one air side system of type 7 for two spaces? or the space which is running at 50% be assigned with system type 3?</div>
<div style><br></div><div style>Thanks in advance for the help.</div><div style><br></div><div style>Thank you,</div><div style>Vamshi.</div></div></div>