I second Patrick, typically I just provide screen grabs of the baseline model and send it off.<div><br><div><div><p style="margin:0px;font-size:13px;color:rgb(34,34,34);font-family:arial,sans-serif;background-color:rgb(255,255,255)">

<b style="font-size:13px"><span lang="EN-CA" style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(127,127,127)">Neil Bulger </span></b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(127,127,127)">| CEPE | Project Engineer</span></p>

<p><b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(127,127,127)">Integral Group </span></b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(127,127,127)">| 427 13th Street | Oakland CA USA 94612<br>

T <a value="+15106632070" style="color:rgb(17,85,204)">510.663.2070 x</a>235</span><span lang="EN-CA" style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(127,127,127)"></span></p><p><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(127,127,127)"><a href="http://www.integralgroup.com/" style="color:rgb(17,85,204)" target="_blank"><span style="color:rgb(127,127,127)">integralgroup.com</span></a> | <a href="mailto:nbulger@integralgroup.com" style="color:rgb(17,85,204)" target="_blank"><span style="color:rgb(127,127,127)">nbulger@integralgroup.com</span></a></span></p>

<p><span lang="EN-GB" style="font-size:6pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"> </span><b style="font-size:13px"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(176,188,34)">Trust</span></b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(51,51,51)"> </span><span style="font-size:12pt;font-family:Arial,sans-serif;color:rgb(176,188,34)">|</span><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(51,51,51)"> </span><b style="font-size:13px"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(118,118,98)">Nurture</span></b><b style="font-size:13px"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(51,51,51)"> </span></b><span style="font-size:12pt;font-family:Arial,sans-serif;color:rgb(51,51,51)">|</span><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(0,164,228)"> <b>Inspire</b></span></p>

<p><span style="color:rgb(176,188,34);font-family:Arial,sans-serif;font-size:8pt">Please consider the environment before printing this email.</span></p><p></p></div>
<br><br><div class="gmail_quote">On Wed, Apr 10, 2013 at 1:19 PM, Patrick J. O'Leary, Jr. <span dir="ltr"><<a href="mailto:poleary1969@gmail.com" target="_blank">poleary1969@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">


  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    i typically just do screen caps when setting up my baseline model. 
    it's quick, painless, and makes mothers very happy ... and is done
    early ...<br>
    <br>
    yeah, one would think there would be a details of hvac systems
    output report showing the direct inputs, but there's not.  unless
    you're good at creating custom reports & can create one that
    pulls input data from the hvac section?  if that's even data
    possible for equest to pull ...<br>
    <br>
    or you could parse the info from the .sim file keying on just the =
    system name, heat-sizing-rati & cool-sizing-rati variables.<br>
    <br>
    "PSZ-1" = SYSTEM          <br>
       TYPE             = PSZ<br>
       HEAT-SOURCE      = FURNACE<br>
       ZONE-HEAT-SOURCE = NONE<br>
       BASEBOARD-SOURCE = NONE<br>
       SIZING-RATIO     = 1.15<br>
       HEAT-SIZING-RATI = 1.25<br>
       COOL-SIZING-RATI = 1.15<br>
      etc ........<div><div class="h5"><br>
    <br>
    <br>
    On 4/10/13 1:04 PM, Nick Caton wrote:
    </div></div><blockquote type="cite"><div><div class="h5">
      
      
      
      
      <div>
        <p class="MsoNormal">Hi folks,<u></u><u></u></p>
        <p class="MsoNormal"><u></u> <u></u></p>
        <p class="MsoNormal">I have a seemingly simple LEED comment
          which has been causing me to chase my tail this afternoon.  I
          feel like this should be really easy to document in a
          crystal-clear fashion, but I must be missing something:<u></u><u></u></p>
        <p class="MsoNormal"><u></u> <u></u></p>
        <p class="MsoNormal"><b>The Task:  <u></u><u></u></b></p>
        <p class="MsoNormal">Document with clarity that the baseline
          system cooling and heating capacities are using the 1.15 and
          1.25 (respectively) capacity sizing ratios as prescribed in
          90.1 Appendix G.<u></u><u></u></p>
        <p class="MsoNormal"><u></u> <u></u></p>
        <p class="MsoNormal">Intuitively, I have a sense we should be
          able to simply and directly reference one or a series of the
          *.SIM reports to substantiate the systems are oversized by the
          appropriate factors.  After spending some time digging through
          the reports and associated help documentation however, I’m
          empty-handed and do not think the actual ratio inputs
          (COOL-SIZING-RATI / HEAT-SIZING-RATI) are reported.<u></u><u></u></p>
        <p class="MsoNormal"><u></u> <u></u></p>
        <p class="MsoNormal">Further, I tried <u>deriving</u> the
          oversizing ratio between a system’s annual PEAK  (re: report
          SS-P) and calculated system capacity (report SV-A) as
          reported… but the math doesn’t quite work out!  It’s the right
          ballpark, but I don’t think I can write the difference off as
          a rounding error…<u></u><u></u></p>
        <p class="MsoNormal"><b><u></u> <u></u></b></p>
        <p class="MsoNormal"><b>The Solution(?):  <u></u><u></u></b></p>
        <p class="MsoNormal">For now, I can just provide screen grabs
          illustrating the inputs in eQuest’s spreadsheet view with
          relative ease, but if this is possible to document by
          assembling/referencing one or more additional reports for
          future models I’d prefer to adopt that in practice and avoid
          the same question down the road.  If I have some
          misunderstanding or new nuance to learn about the reports that
          would be worthwhile as well =).<i><u></u><u></u></i></p>
        <p class="MsoNormal"><u></u> <u></u></p>
        <p class="MsoNormal">Any suggestions/experience?<u></u><u></u></p>
        <p class="MsoNormal"><u></u> <u></u></p>
        <p class="MsoNormal">Thanks in advance!<u></u><u></u></p>
        <p class="MsoNormal"><u></u> <u></u></p>
        <p class="MsoNormal">~Nick<u></u><u></u></p>
        <p class="MsoNormal"><u></u> <u></u></p>
        <p class="MsoNormal"><span style="color:#1f497d"><img alt="cid:489575314@22072009-0ABB" height="37" width="119"></span><b><span><u></u><u></u></span></b></p>
        <p class="MsoNormal"><b><span><u></u> <u></u></span></b></p>
        <p class="MsoNormal"><b><span>NICK CATON,
              P.E.<u></u><u></u></span></b></p>
        <p class="MsoNormal"><span style="font-size:7.5pt;color:#cc9900">SENIOR
            ENGINEER<u></u><u></u></span></p>
        <p class="MsoNormal"><span style="font-size:7.5pt;color:#cc9900"><u></u> <u></u></span></p>
        <p class="MsoNormal"><span style="font-size:10.0pt;color:#2d4d5e">Smith & Boucher
            Engineers</span><span><u></u><u></u></span></p>
        <p class="MsoNormal"><span style="font-size:10.0pt;color:#2d4d5e">25501 west valley
            parkway, suite 200<u></u><u></u></span></p>
        <p class="MsoNormal"><span style="font-size:10.0pt;color:#2d4d5e">olathe, ks 66061<u></u><u></u></span></p>
        <p class="MsoNormal"><span style="font-size:10.0pt;color:#2d4d5e">direct <a href="tel:913.344.0036" value="+19133440036" target="_blank">913.344.0036</a><u></u><u></u></span></p>
        <p class="MsoNormal"><span style="font-size:10.0pt;color:#2d4d5e">fax <a href="tel:913.345.0617" value="+19133450617" target="_blank">913.345.0617</a><u></u><u></u></span></p>
        <p class="MsoNormal"><span style="color:#1f497d"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size:10.0pt;color:blue">www.smithboucher.com</span></a></span><u><span style="font-size:10.0pt;color:blue">
            </span></u><span style="color:#1f497d"><u></u><u></u></span></p>
        <p class="MsoNormal"><u></u> <u></u></p>
      </div>
      <br>
      <fieldset></fieldset>
      <br>
      </div></div><pre>_______________________________________________
Equest-users mailing list
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </div>