<div>Those are good questions.</div>
<div><br>
</div>
<div>Answer to 1st question = yes</div>
<div><br>
</div>
<div>Answer to second is the following:</div>
<div><br>
</div>
<div>To be practical about this and simplify the modeling, we create a constant efficiency air cooled chiller to simulate the default DESv2.0 plant.</div>
<div><br>
</div>
<div>The EIR is entered equal to 0.839 kw/ton, which equates to 4.4 COP + 5% losses.</div>
<div><br>
</div>
<div>This represents the energy usage of the plant chillers, plant pumps, and cooling tower.</div>
<div><br>
</div>
<div>We further create and apply performance curves that keep the EIR the same versus load and temperatures. In other words, Avg EIR = Max EIR = Min EIR = the EIR we enter into eQuest.</div>
<div><br>
</div>
<div>It's easier to do this with an air cooled chiller because then you don't have to worry about a cooling tower and tower water pump in the model.</div>
<div><br>
</div>
<div>This approach is simple and it works. I've used it on several LEED projects involving district chilled water systems.</div>
<div><br>
</div>
<div>We probably give up some savings with this approach, but it's a lot of work to correctly model the actual performance of an actual CHW system in accordance with DESv2.0. If this isn't in our modeling scope of work, we use the stipulated efficiency route.</div>
<div><br>
</div>
<div>Hope this helps.</div>
<div><br>
</div>
<div>P.S. The stipulated efficiency approach does not work out well when modeling heating water and steam systems because the default efficiency numbers for those systems are pretty bad. That's not the case with chilled water, at least if you are comparing
to a Baseline based on air cooled equipment. If the building was big enough to require chilled water as a baseline, this approach will not work that well, and you would have to pivot to a new approach. Comparing the stipulated efficiency against a App G Baseline
water cooled chiller plant would probably result in little to no savings in the cooling equipment category.<br>
<br>
<div>Thanks!</div>
<div><br>
</div>
<div>Regards,</div>
<div><br>
</div>
<div>JAH</div>
</div>
<div><br>
On Apr 5, 2013, at 1:51 PM, "Adam S" <<a href="mailto:adam.scherba@gmail.com">adam.scherba@gmail.com</a>> wrote:<br>
<br>
</div>
<blockquote type="cite">
<div>
<div dir="ltr">Do you interpret the USGBC guidance for baseline district energy systems to be 4.4 COP + 5% losses averaged over the year? Meaning that the chiller in your model should be modeled with a better EIR so that the average annual COP calculated using
the PS-C report is 4.4?
<div><br>
</div>
<div style="">Their use of the term "average efficiency" seems a bit vague.</div>
<div style=""><br>
</div>
<div style="">Thanks,</div>
</div>
<div class="gmail_extra"><br clear="all">
<div>-Adam</div>
<br>
<br>
<div class="gmail_quote">On Fri, Mar 29, 2013 at 3:24 AM, James Hess <span dir="ltr">
<<a href="mailto:JHess@tmecorp.com" target="_blank">JHess@tmecorp.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">I definitely agree with that suggestion, versus reinventing the wheel. Our experience with the RMI tool is that it works. There seems to be a quirk regarding
a little shifting due to DST, but that’s a very small thing in the grand scheme of things. I want to say we tested it and the annual average value coming out of eQuest was ~ 99.3% of the average input value. Close enough!
</span><span style="font-size:11.0pt;font-family:Wingdings;color:#1f497d">J</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Also, I don’t know if you are modeling the other buildings because a GBCI reviewer said you had to do that (assuming this is a LEED project) in order to ensure
that correct part load ratios on the chillers operating profile are appropriately accounted for. I got that sort of comment on a recent project and my response was something to the effect of … I could do that, but since we aren’t getting paid by the owner
to model buildings outside of the project scope just to make the chiller modeling more accurate, instead I will just use the default efficiency allowed by the DESv2.0 guidelines for water cooled chiller plants
</span><span style="font-size:11.0pt;font-family:Wingdings;color:#1f497d">à</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> 4.4 COP + 5% losses = ~ 0.839 kW/ton on average.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">That saved a lot of time with that change because if you do that, you don’t have to model any other buildings served by the system. If you are comparing against
air cooled equipment for the Baseline, you still get a decent amount of savings. I probably left some savings on the table because the plant had high efficiency VFD water cooled chillers, and VFDs on the pumps and cooling tower. I’m positive that the annual
efficiency was much better than 0.839 kW/ton, but (the way I look at this) we have to balance the level of effort on energy modeling versus the fees we are getting for the modeling.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Hope this helps!
</span><span style="font-size:11.0pt;font-family:Wingdings;color:#1f497d">J</span><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Regards,<u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:8.0pt;font-family:"Calibri","sans-serif";color:#339966"><u></u> <u></u></span></b></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#339966">JAH<u></u><u></u></span></b></p>
<p class="MsoNormal"><b><span style="font-size:8.0pt;font-family:"Calibri","sans-serif";color:#339966"><u></u> <u></u></span></b></p>
<p class="MsoNormal"><b><i><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#339966">James A. Hess, PE, CEM, BEMP</span></i></b><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><br>
Energy Engineer<br>
TME, Inc.<br>
Little Rock, AR<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Mobile:
<a href="tel:%28501%29%20351-4667" value="+15013514667" target="_blank">(501) 351-4667</a><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Javed Iqbal<br>
<b>Sent:</b> Thursday, March 28, 2013 1:55 PM<br>
<b>To:</b> Kimberly Wiebe<br>
<b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] CHW loop process load<u></u><u></u></span></p>
<div>
<div class="h5">
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="font-family:"Georgia","serif";color:#333399">You should use RMI tool to generate schedule which will eventually gives you schedule in INP format.</span><u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Georgia","serif";color:#333399">Here is the link to download it..</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><span style="font-family:"Georgia","serif";color:#333399"><a href="http://www.rmi.org/Content/Files/EMIT1.4.zip" target="_blank">http://www.rmi.org/Content/Files/EMIT1.4.zip</a></span><u></u><u></u></p>
<div>
<p class="MsoNormal">On Thu, Mar 28, 2013 at 1:41 PM, Kimberly Wiebe <<a href="mailto:Kimberly.Wiebe@burohappold.com" target="_blank">Kimberly.Wiebe@burohappold.com</a>> wrote:<u></u><u></u></p>
<div>
<div>
<p class="MsoNormal"><span lang="EN-GB" style="font-size:10.0pt;font-family:"Arial","sans-serif"">Hello,
</span><u></u><u></u></p>
<p class="MsoNormal"><span lang="EN-GB" style="font-size:10.0pt;font-family:"Arial","sans-serif""> </span><u></u><u></u></p>
<p class="MsoNormal"><span lang="EN-GB" style="font-size:10.0pt;font-family:"Arial","sans-serif"">I am modelling a central cooling plant that serves many buildings on an college campus. For some buildings I am building the geometry and inputting internal gains.
For other buildings I have annual 8760 cooling load profiles. If I want to add these annual cooling load profiles to the CHW loop as process loads, would I have to make 365 day schedules (and 52 weeks)? If so I will write some sort of text generator out of
an excel file and paste in the .inp, but before I do want to see if there was any other way.</span><u></u><u></u></p>
<p class="MsoNormal"><span lang="EN-GB" style="font-size:10.0pt;font-family:"Arial","sans-serif""> </span><u></u><u></u></p>
<p class="MsoNormal"><span lang="EN-GB" style="font-size:10.0pt;font-family:"Arial","sans-serif"">Thank you,
</span><u></u><u></u></p>
<p class="MsoNormal"><span lang="EN-GB" style="font-size:10.0pt;font-family:"Arial","sans-serif"">Kim</span><u></u><u></u></p>
<p class="MsoNormal"><span lang="EN-GB" style="font-size:10.0pt;font-family:"Arial","sans-serif""> </span><u></u><u></u></p>
<p class="MsoNormal"><b><span style="font-size:8.0pt;font-family:"Arial","sans-serif"">Kim Wiebe</span></b><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:8.0pt;font-family:"Arial","sans-serif"">Direct:
<a href="tel:%2B1%20310%20945%204813" value="+13109454813" target="_blank">+1 310 945 4813</a></span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:8.0pt;font-family:"Arial","sans-serif""><a href="mailto:kimberly.wiebe@burohappold.com" target="_blank">kimberly.wiebe@burohappold.com</a></span><u></u><u></u></p>
<p class="MsoNormal"><span lang="EN-GB"> </span><u></u><u></u></p>
</div>
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><u></u><u></u></p>
</div>
<p class="MsoNormal"><br>
<br clear="all">
<u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<p class="MsoNormal">-- <u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal" align="center" style="text-align:center"><span style="font-family:"Verdana","sans-serif";background:#3333ff"><u></u> <u></u></span></p>
<p class="MsoNormal" align="center" style="text-align:center"><span style="font-family:"Georgia","serif";color:#333399;background:white">Javed Iqbal, LEED AP, CEA</span><span style="background:#3333ff"><u></u><u></u></span></p>
<p class="MsoNormal" align="center" style="text-align:center"><span style="font-family:"Georgia","serif";color:#333399;background:white">Energy Analyst </span><span style="background:#3333ff"><u></u><u></u></span></p>
<p class="MsoNormal" align="center" style="text-align:center"><span style="color:#3366ff;background:#3333ff"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#3366ff;background:#3333ff"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#3366ff;background:#3333ff"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="background:#3333ff"><u></u> <u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
</div>
</div>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br>
</blockquote>
</div>
<br>
</div>
</div>
</blockquote>
</body>
</html>