<div dir="ltr">The eSimForums has a section dedicated to expressions that is pretty helpful and if you have any further questions I'd recommend making a post on there. There's a small group of people who seem to respond to questions in a fairly timely manner over there. Link: <a href="http://www.esimforums.com/equest/viewforum.php?f=70">http://www.esimforums.com/equest/viewforum.php?f=70</a>. Specifically, I made a post on there of the commonly used BDL commands that I use in writing expressions: <a href="http://www.esimforums.com/equest/viewtopic.php?f=70&t=139">http://www.esimforums.com/equest/viewtopic.php?f=70&t=139</a>.<div>
<br></div><div>To answer your specific question, to reference a space command from the zone you'll want to make use of the Local Reference command (#LR). The question marks in your formula could be replaced by #LR("SPACE","NUMBER-OF-PEOPLE") and #LR("SPACE","AREA").</div>
<div><br></div><div style>Also, it appears you're missing the distribution efficiency factor from ASHRAE 62.1 in your calculations. Typically this value is 0.8.</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">
On Wed, Apr 3, 2013 at 8:05 PM, Joshua W. Chapman <span dir="ltr"><<a href="mailto:chapmanjw@gmail.com" target="_blank">chapmanjw@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Hi All,<br>
<br>
Does anyone know how to create DOE 2.2 formulas to have Equest calculate<br>
outside air accordingly? I am typically modeling multi-family projects. As<br>
such my models all have MANY single zone split systems (over 400). Per<br>
ASHRAE 62.1, Outside Air = OA-FLOW/PER * NUMBER-OF-PEOPLE + OA-FLOW/AREA *<br>
AREA. However equest only uses the larger of OA-FLOW/PER * NUMBER-OF-PEOPLE<br>
or OA-FLOW/AREA * AREA. I have tried to create a formula and input it into<br>
the field OUTSIDE-AIR-FLOW but I am not very familiar with DOE 2.2 syntax.<br>
<br>
AREA is a SPACE property. NUMBER-OF-PEOPLE is a SPACE property.<br>
OUTSIDE-AIR-FLOW, OA-FLOW/PER and OA-FLOW/AREA are all ZONE properties.<br>
<br>
How would I write a ZONE formula for OUTSIDE-AIR-FLOW that calls the<br>
corresponding SPACE values for AREA and NUMBER-OF-PEOPLE? I am sure it has<br>
to do with Parent/Child relationships in Equest/DOE 2.2. Is the Space the<br>
parent or child of the zone? Is the space a parent or child of the polygon?<br>
<br>
= #L("OA-FLOW/PER")* ?? + #L("OA-FLOW/AREA")*??<br>
<br>
Please help.<br>
<br>
Joshua W. Chapman PE, LEED AP<br>
Scot Engineering Inc.<br>
<br>