<div dir="ltr"><div><br></div><div><p class="MsoNormal">Dear eQUEST experts,</p><p class="MsoNormal"><br></p>
<p class="MsoNormal">The design model that I’m working at has many thermal zones with adequate cooling and heating capacities (Per final Mechanical documents). Total hours above COOLING THROTTLING RANGE for the project is 82 and total hours below HEATING THROTTLING RANGE is 202. The HVAC systems have economizer and heat recovery. </p>
<p class="MsoNormal"><br></p><p class="MsoNormal">The simulation report shows the
following warnings for almost all the zones. </p><p class="MsoNormal">I would appreciate it if you would tell me what caused these warnings an how I can solve the issues.</p><p class="MsoNormal"><br></p><p class="MsoNormal">
Morteza</p></div><div><br></div><br clear="all"><div><div> **WARNING**********************************************************************</div><div> SYSTEM ECCNSys1 (PSZ) (G.NW2) may have inadequate cooling capability</div>
<div> Check COOLING-CAPACITY and MIN-SUPPLY-T for consistency</div></div><div><br></div><div><br></div><div><div> **WARNING**********************************************************************</div><div> ZONE ADMISouth Perim Zn (G.S6) </div>
<div> might have insufficient heating capability.</div><div> Check that the SYSTEM or ZONE HEATING-CAPACITY plus this</div><div> ZONEs BASEBOARD-RATING is adequate to maintain the ZONE</div>
<div> specified DESIGN-HEAT-T for the calculated peak ZONE load</div><div> (see LS-A or LS-B for the ZONE peak load.)</div></div><div><br></div><div><div> **WARNING**********************************************************************</div>
<div> Energy-recovery ventilator: ECCSSys2 (PSZ) (G.ENE3) has</div><div> condensation on the exhaust outlet. First occurrence: 1 2 7</div><div> OA T&W: 31.9 0.0031 Return T&W: 52.2 0.0034</div>
</div><div><br></div><div><div> **WARNING**********************************************************************</div><div> Energy-recovery ventilator: ECCNSys1 (PSZ) (G.SSE6) has</div><div> frost on the exhaust outlet. First occurrence: 1 7 7</div>
<div> OA T&W: 26.0 0.0023 Return T&W: 59.2 0.0027</div></div><div><br></div><div><br></div><div><br></div><div><br></div>-- <br><div dir="ltr"><i><span style="color:rgb(0,102,0)">Morteza Kasmaei</span></i><br style="color:rgb(0,102,0)">
<span style="color:rgb(0,102,0)">Architect, LEED® AP BD+C<br></span></div>
</div>