<div class="moz-cite-prefix">Thanks Bill,<br>
<br>
I verified that the references you gave lead to the result of the
calculation in the spreadsheet, but if the theoretical calculation
below has any validity at all, the assumed fan efficiency in 90.1
is about 8%. I used a fan static pressure rise of .5 in. H2O. <br>
<br>
So, this fan efficiency seems a little low to me.<br>
<br>
You said "Fan efficiency is from ASHRAE 90.1, Table 10.8 as
described in G3.1.2.9." but Table 10.8 is Fan Motor efficiency,
which is about 85%. I have no problem with that, but to use the
theoretical fan power equation I need the Fan efficiency. Do you
have any idea what fan efficiency is assumed in 90.1?<br>
<br>
I also notice that the fan power calculation in 90.1 does not
include a pressure rise component, which I find odd. Is the
pressure rise across the fan assumed somewhere? From the checks
described above, it appears to be about .5 in. H2O. Does this
seem reasonable?<br>
<br>
<br>
<br>
Your thoughts?<br>
<br>
<br>
<br>
<pre class="moz-signature" cols="72">Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
</pre>
On 3/25/2013 8:01 AM, Bishop, Bill wrote:<br>
</div>
<blockquote
cite="mid:90D829482BDEDB4CB264DE5060592B1910465FEE@lightning.pathfinderengineers.com"
type="cite">
<meta http-equiv="Content-Type" content="text/html;
charset=ISO-8859-1">
<meta name="Generator" content="Microsoft Word 12 (filtered
medium)">
<!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
<style><!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Tahoma;
panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
{font-family:Consolas;
panose-1:2 11 6 9 2 2 4 3 2 4;}
@font-face
{font-family:"Franklin Gothic Medium";
panose-1:2 11 6 3 2 1 2 2 2 4;}
@font-face
{font-family:Webdings;
panose-1:5 3 1 2 1 5 9 6 7 3;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman","serif";
color:black;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
pre
{mso-style-priority:99;
mso-style-link:"HTML Preformatted Char";
margin:0in;
margin-bottom:.0001pt;
font-size:10.0pt;
font-family:"Courier New";
color:black;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
{mso-style-priority:99;
mso-style-link:"Balloon Text Char";
margin:0in;
margin-bottom:.0001pt;
font-size:8.0pt;
font-family:"Tahoma","sans-serif";
color:black;}
p.MsoListParagraph, li.MsoListParagraph, div.MsoListParagraph
{mso-style-priority:34;
margin-top:0in;
margin-right:0in;
margin-bottom:0in;
margin-left:.5in;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman","serif";
color:black;}
span.HTMLPreformattedChar
{mso-style-name:"HTML Preformatted Char";
mso-style-priority:99;
mso-style-link:"HTML Preformatted";
font-family:Consolas;
color:black;}
span.BalloonTextChar
{mso-style-name:"Balloon Text Char";
mso-style-priority:99;
mso-style-link:"Balloon Text";
font-family:"Tahoma","sans-serif";}
span.EmailStyle22
{mso-style-type:personal;
font-family:"Calibri","sans-serif";
color:#1F497D;}
span.EmailStyle23
{mso-style-type:personal-reply;
font-family:"Calibri","sans-serif";
color:#1F497D;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
/* List Definitions */
@list l0
{mso-list-id:1707102763;
mso-list-type:hybrid;
mso-list-template-ids:1923138334 67698703 67698713 67698715 67698703 67698713 67698715 67698703 67698713 67698715;}
@list l0:level1
{mso-level-tab-stop:none;
mso-level-number-position:left;
text-indent:-.25in;}
@list l0:level2
{mso-level-number-format:alpha-lower;
mso-level-tab-stop:none;
mso-level-number-position:left;
text-indent:-.25in;}
@list l0:level3
{mso-level-number-format:roman-lower;
mso-level-tab-stop:none;
mso-level-number-position:right;
text-indent:-9.0pt;}
@list l0:level4
{mso-level-tab-stop:none;
mso-level-number-position:left;
text-indent:-.25in;}
@list l0:level5
{mso-level-number-format:alpha-lower;
mso-level-tab-stop:none;
mso-level-number-position:left;
text-indent:-.25in;}
@list l0:level6
{mso-level-number-format:roman-lower;
mso-level-tab-stop:none;
mso-level-number-position:right;
text-indent:-9.0pt;}
@list l0:level7
{mso-level-tab-stop:none;
mso-level-number-position:left;
text-indent:-.25in;}
@list l0:level8
{mso-level-number-format:alpha-lower;
mso-level-tab-stop:none;
mso-level-number-position:left;
text-indent:-.25in;}
@list l0:level9
{mso-level-number-format:roman-lower;
mso-level-tab-stop:none;
mso-level-number-position:right;
text-indent:-9.0pt;}
ol
{margin-bottom:0in;}
ul
{margin-bottom:0in;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Robert,<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">I’m
sure Nick is typing furiously as I write this, but I’ll
probably finish before him.<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Taking
a quick look at the spreadsheet that Nick attached to his
email, it calculates baseline fan power using the method
described in Appendix G and 6.5.3.1.1. Fan efficiency is
included in the P<sub>fan</sub> calculation per G3.1.2.9.<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Fan
efficiency is from ASHRAE 90.1, Table 10.8 as described in
G3.1.2.9.<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Regards,<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Bill<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Franklin
Gothic Medium","sans-serif"">William
Bishop, PE, BEMP, LEED AP
</span></b><b><span
style="font-size:10.0pt;font-family:"Franklin
Gothic
Medium","sans-serif";color:#006600">|</span></b><b><span
style="font-size:10.0pt;font-family:"Franklin
Gothic Medium","sans-serif""> Pathfinder
Engineers & Architects LLP<o:p></o:p></span></b></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Arial","sans-serif"">Senior
Energy Engineer<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:5.0pt;font-family:"Arial","sans-serif""><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#1F497D">134
South Fitzhugh Street</span><span
style="font-size:9.0pt;color:#1F497D">
</span><span
style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#1F497D">Rochester,
NY 14608<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#1F497D">T:
(585) 325-6004
</span><span
style="font-size:9.0pt;font-family:"Arial","sans-serif"">Ext.
114</span><span style="color:#1F497D">
</span><span
style="font-size:9.0pt;font-family:"Arial","sans-serif";color:#1F497D">F:
(585) 325-6005</span><span
style="font-size:9.0pt;font-family:"Arial","sans-serif""><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><a
moz-do-not-send="true"
href="mailto:wbishop@pathfinder-ea.com"><span
style="font-size:9.0pt;font-family:"Arial","sans-serif"">wbishop@pathfinder-ea.com</span></a></span><span
style="font-size:9.0pt;font-family:"Arial","sans-serif"">
</span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><a
moz-do-not-send="true"
href="http://www.pathfinder-ea.com/"><span
style="font-size:9.0pt;font-family:"Arial","sans-serif"">www.pathfinder-ea.com</span></a></span><span
style="font-size:9.0pt;font-family:"Arial","sans-serif""><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:14.0pt;font-family:Webdings;color:green">P</span><span
style="font-size:14.0pt;color:green">
</span><span style="font-size:7.5pt;color:green">Sustainability
– the forest AND the trees.</span><span
style="font-size:18.0pt;font-family:Webdings;color:green">
</span><span
style="font-size:14.0pt;font-family:Webdings;color:green">P</span><span
style="font-size:14.0pt;font-family:"Calibri","sans-serif";color:green"> </span><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>
</div>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">
<a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
[<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>RobertWichert<br>
<b>Sent:</b> Monday, March 25, 2013 10:52 AM<br>
<b>To:</b> Nick Caton;
<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Baseline Fan power
calculation<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<div>
<p class="MsoNormal">I believe I have written about this in
the past, but since this seems to be on-topic, I'll bring it
up again.<br>
<br>
The theoretical fan power equation, Fan BHP = (cfm x static
press "w.c.) / (6356 x fan efficiency) can be used to
calculate the theoretical fan BHP, but you need the fan
efficiency. This seems to be NOT the way the BHP is being
calculated by the spreadsheet that was attached previously.<br>
<br>
Is there a reason for that?<br>
<br>
Was there an assumed fan efficiency used in the spreadsheet,
and was it based on anything particular, or just a
conservative assumption?<br>
<br>
<br>
Thanks!<br>
<br>
<br>
<br>
<br>
<o:p></o:p></p>
<pre>Robert Wichert P.Eng. LEED AP BD&C<o:p></o:p></pre>
<pre>+1 916 966 9060<o:p></o:p></pre>
<pre>FAX +1 916 966 9068<o:p></o:p></pre>
<pre><o:p> </o:p></pre>
<pre><o:p> </o:p></pre>
<pre><o:p> </o:p></pre>
<pre><o:p> </o:p></pre>
<pre><o:p> </o:p></pre>
<pre><o:p> </o:p></pre>
<pre><o:p> </o:p></pre>
<pre>===============================================<o:p></o:p></pre>
<p class="MsoNormal">On 3/25/2013 7:34 AM, Nick Caton wrote:<o:p></o:p></p>
</div>
<blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Hi
Vamshi,</span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> </span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">I
advise carefully reviewing the footnotes under Table
6.5.3.1.1A, which include procedure for determining
baseline fan power adjustments.</span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> </span><o:p></o:p></p>
<p class="MsoListParagraph"
style="text-indent:-.25in;mso-list:l0 level1 lfo2"><!--[if !supportLists]--><span
style="mso-list:Ignore">1.<span style="font:7.0pt
"Times New Roman"">
</span></span><!--[endif]--><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">P<sub>fan</sub>
represents the sum power of all fans in a given baseline
system (with exception to baseline systems #6/#8, fan
powered VAV boxes).</span><o:p></o:p></p>
<p class="MsoListParagraph"
style="text-indent:-.25in;mso-list:l0 level1 lfo2"><!--[if !supportLists]--><span
style="mso-list:Ignore">2.<span style="font:7.0pt
"Times New Roman"">
</span></span><!--[endif]--><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Again,
there is not a separate supply/return power calculation
(see answer #1). You can however account for adjustments
present in separate airstreams from the proposed design.
</span><o:p></o:p></p>
<p class="MsoListParagraph"
style="text-indent:-.25in;mso-list:l0 level1 lfo2"><!--[if !supportLists]--><span
style="mso-list:Ignore">3.<span style="font:7.0pt
"Times New Roman"">
</span></span><!--[endif]--><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Probably
not. Review the difference between CFM<sub>S</sub> and
CFM<sub>D</sub> carefully at the cited Table. A CFM
quantity representing the airflow each element encounters
(CFM<sub>D</sub>) should be applied against each pressure
drop adjustment, not an ‘aggregate’ of supply+return. </span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> </span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">You
may also find the attached resource published by 7group
helpful to cement your procedural understanding of how to
arrive at the sum total for “A.”
</span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> </span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Regards,</span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> </span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">~Nick</span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><img
id="Picture_x0020_1"
src="cid:part3.02050505.02050907@wichert.org"
alt="cid:489575314@22072009-0ABB" height="37"
width="119" border="0"></span><o:p></o:p></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt"> </span></b><o:p></o:p></p>
<p class="MsoNormal"><b>NICK CATON, P.E.</b><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Calibri","sans-serif";color:#CC9900">SENIOR
ENGINEER</span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Calibri","sans-serif";color:#CC9900"> </span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">Smith
& Boucher Engineers</span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">25501
west valley parkway, suite 200</span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">olathe,
ks 66061</span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">direct
913.344.0036</span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">fax
913.345.0617</span><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><a
moz-do-not-send="true" href="www.smithboucher.com"
title="blocked::www.smithboucher.com"><span
style="font-size:10.0pt">www.smithboucher.com</span></a></span><u><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:blue">
</span></u><o:p></o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> </span><o:p></o:p></p>
<p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">
<a moz-do-not-send="true"
href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
[<a moz-do-not-send="true"
href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>vamshi ranga<br>
<b>Sent:</b> Monday, March 25, 2013 8:17 AM<br>
<b>To:</b> <a moz-do-not-send="true"
href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Baseline Fan power
calculation</span><o:p></o:p></p>
<p class="MsoNormal"> <o:p></o:p></p>
<p class="MsoNormal">Hi All,<o:p></o:p></p>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal">I have a doubt regarding calculating
fan power as per ASHRAE 90.1-2007.<o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal">My proposed system has, supply return
and exhaust fans separately with kW and cfm mentioned for
each fan.<o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal">So, for calculating baseline fan
power, <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal">1. should I calculate it separately for
each fan type? <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal">2. can I take pressure drop adjustment
both in supply and return fan power calculation?<o:p></o:p></p>
</div>
<div>
<p class="MsoNormal">3. should I sum all the cfms of supply,
return and exhaust and than apply pressure drop
adjustments to aggregated cfm.<o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal">Kindly help me out in solving the
doubt. If you have any example fan power calculations, or
web links those could guide me regarding this, plz do
share them.<o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal">Thanks in advance.<o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal">Regards,<o:p></o:p></p>
</div>
<div>
<p class="MsoNormal">Vamshi.<o:p></o:p></p>
</div>
<p class="MsoNormal"><br>
<br>
<br>
<o:p></o:p></p>
<pre>_______________________________________________<o:p></o:p></pre>
<pre>Equest-users mailing list<o:p></o:p></pre>
<pre><a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><o:p></o:p></pre>
<pre>To unsubscribe from this mailing list send a blank message to <a moz-do-not-send="true" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></pre>
</blockquote>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
</blockquote>
<br>
</body>
</html>