<html>
<body>
<font size=3>Catalina,<br>
I am not sure about the Wizard mode, I haven't used it that much.  I
tend to use the Detailed edit mode or direct edit in the .inp file.
<br><br>
At 06:14 PM 3/14/2013, you wrote:<br>
<blockquote type=cite class=cite cite="">Chris, where can  set this
up in the wizard mode?<br>
 <br>
<b>From:</b> Chris Jones
[<a href="mailto:cj@enersave.ca" eudora="autourl">
mailto:cj@enersave.ca</a>] <br>
<b>Sent:</b> Thursday, March 14, 2013 5:51 PM<br>
<b>To:</b> Caballero, Catalina; equest-users@lists.onebuilding.org<br>
<b>Subject:</b> Re: [Equest-users] FW: Roof conduction (Pitch Roof)<br>
 <br>
The SPACE definition should defined ZONE-TYPE = PLENUM, not
UNCONDITIONED.  The ZONE definition should be TYPE = PLENUM, again
not UNCONDITIONED.<br><br>
Note PLENUMs can also be defined with the SPACE definition as ZONE-TYPE =
CONDITIONED in the case of an atrium being used as a return air plenum
with lights, occupants, etc.  <br><br>
<br><br>
<br><br>
<br>
Good morning,<br>
 <br>
For my model, when I go to report LS-C, Is not showing any roof
conduction, not really sure why since I have a pitch roof  as
unconditioned attic/plenum, therefore there should be heat transfer from
the outside to the attic and from the attic to the interior space.<br>
 <br>
How should I correct this?<br>
 <br>
Thanks.<br>
 <br>
Catalina Caballero, AIA. Assoc., LEED GA.<br>
<b>Johnson, Avedano, Lopez, Rodriguez & Walewski<br>
Engineering Group, Inc.</b> <br>
2510 NW 97th Avenue, Suite 220, Miami, Florida 33172<br>
Tel. (305) 594-0660 Ext. 217 Fax (305) 594-0907<br>
Visit us online: <a href="http://www.jalrw.com/">www.jalrw.com</a><br>
 <br>
<img src="cid:7.1.0.9.2.20130315064611.05c70db0@enersave.ca.1" width=210 height=78 alt="JALRW Logo">
<br>
<b>HVAC - Electrical - Plumbing - Fire Protection<br>
Sustainable Development - Commissioning<br>
</b>    <br>
This email and any files transmitted with it are confidential and are
intended solely for the use of the individual or entity to which they are
addressed. If you are not the intended recipient or the person
responsible for delivering the email to the intended recipient, be
advised that you have received this email in error and that any use,
dissemination, forwarding, printing, or copying of this email is strictly
prohibited.<br>
 <br>
 <br><br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
 <br>
To unsubscribe from this mailing list send  a blank message to
<a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br>
</font></blockquote></body>
</html>