    Belal,<br>
    <br>
    I took a look at your text weather file. If  it's clean, i.e., all
    the elements are there for every hour,  then the main difficulties
    are to calculate the following parameters that are needed in the
    DOE-2/eQUEST *.BIN format, as well as to convert all the parameters
    from SI to IP:<br>
    <br>
       calculate wet-bulb temperature from the dry-bulb and relative
    humidity<br>
       calculate the humidity ratio <br>
       calculate the enthalpy of air <br>
    <br>
    You would also have to add a constant air pressure based on the
    location's elevation, and then leave the rain and snow flags as 0's,
    but those aren't really used anyway.<br>
    <br>
    There used to be a dummy Fortran subroutine called OTHER that a user
    could modify and then compile with the DOE-2 weather processor
    program (also in Fortran), wthr.f,<br>
    but I've known of only a handful of people who's actually tried to
    use it all the years I was at LBNL.   By now, I actually prefer to
    write my own program rather than struggling<br>
    with the syntax of wthr.f<br>
    <br>
    Since I do this type of stuff (process weather data) all the time, I
    could probably convert this file for you to eQUEST in less than an
    hour, but I would have to charge you.<br>
    Let me know if you're interested.<br>
    <br>
    Joe<br>
       <br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <br>
    On 3/12/2013 4:51 PM, Belal Khalid Abboushi wrote:
    <blockquote
cite="mid:CAJ6rF0ZLtEq2MLCASmau4ozv9BG7ALd+Ah2eG0bobD-KwNN11A@mail.gmail.com"
      type="cite">
      <meta http-equiv="Context-Type" content="text/html;
        charset=ISO-8859-1">
      <div>Hi all,
        <div><br>
        </div>
        <div>I have a weather file in txt and would like to use the same
          file in equest. Is there a way i can convert it to bin so i
          can use it in eQuest? the weather file (txt) is attached. </div>
        <div><br>
        </div>
        <div>Thanks all,<br>
          <div><br>
          </div>
          -- <br>
          <div>
            <div> <br>
            </div>
            <div> Kind regards, </div>
            <div> Belal Abboushi </div>
            <div> <br>
            </div>
            <div> <br>
            </div>
            <div> <br>
            </div>
            <div> <br>
            </div>
            <div><span> <b>Belal K. Abboushi</b> </span></div>
            <span>
              <div> M.Sc.Arch Candidate - Design & Energy
                Conservation </div>
            </span> <span>
              <div>
                College of Architecture, Planning, and Landscape
                Architecture</div>
            </span>
            <div><span>The University of Arizona </span><span>- U.S.A.</span></div>
          </div>
        </div>
      </div>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>