<div dir="ltr">Correct, -1 does not allow the fan to run for any reason.  I'm fairly sure the reason his system is not running at all is that when you give the fan schedule a value of 0, it considers that to be "night time" or unoccupied.  If you don't allow the system to cycle on under Night Cycle Control then it will stay off, even with a value of zero.<div>
<br></div><div style>-Robby</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Tue, Mar 5, 2013 at 1:21 PM, John Aulbach <span dir="ltr"><<a href="mailto:jra_sac@yahoo.com" target="_blank">jra_sac@yahoo.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div><div style="font-size:12pt;font-family:times new roman,new york,times,serif"><div><span>Others please correct me, but as I recall, -1 is the only ALWAYS OFF input. 0<var></var> has the fan off unless the setback temperature settings are succedded.</span></div>

<div style="font-size:16px;font-style:normal;background-color:transparent;font-family:times new roman,new york,times,serif"><span></span> </div>
<div style="font-size:16px;font-style:normal;background-color:transparent;font-family:times new roman,new york,times,serif"><span>TRY -999. This is what is used in Optimim Star-Stop. It may work in your case.</span></div>

<div style="font-size:16px;font-style:normal;background-color:transparent;font-family:times new roman,new york,times,serif"><span></span> </div>
<div style="font-size:16px;font-style:normal;background-color:transparent;font-family:times new roman,new york,times,serif"><span>John Aulbach</span></div>
<div><br></div>
<div style="FONT-FAMILY:times new roman,new york,times,serif;FONT-SIZE:12pt">
<div style="FONT-FAMILY:times new roman,new york,times,serif;FONT-SIZE:12pt">
<div dir="ltr"><font face="Arial">
<div style="BORDER-BOTTOM:#ccc 1px solid;BORDER-LEFT:#ccc 1px solid;PADDING-BOTTOM:0px;LINE-HEIGHT:0;MARGIN:5px 0px;PADDING-LEFT:0px;PADDING-RIGHT:0px;min-height:0px;FONT-SIZE:0px;BORDER-TOP:#ccc 1px solid;BORDER-RIGHT:#ccc 1px solid;PADDING-TOP:0px" readonly>
</div><b><span style="FONT-WEIGHT:bold">From:</span></b> Jay M <<a href="mailto:fd111441@hotmail.com" target="_blank">fd111441@hotmail.com</a>><br><b><span style="FONT-WEIGHT:bold">To:</span></b> "<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>" <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>> <br>
<b><span style="FONT-WEIGHT:bold">Sent:</span></b> Tuesday, March 5, 2013 1:08 PM<br><b><span style="FONT-WEIGHT:bold">Subject:</span></b> [Equest-users] How do I set Fan schedule To only meet loads?<br></font></div><div>
<div class="h5"><br>
<div>


<div>
<div dir="ltr">Hi all,<br><br>How do i set the fan schedule to only be on when cooling or heating demands are required?<br><br>In DD edit,   fan schedule... I can only put  "0" or "1"... if i put "0"  then  the system is off and never Cools or Heats when heating or cooling is needed.<br>
<br>When  I put "1"   the fan is always on even when no heating or cooling is needed.<br><br>As a result for some hours I would get the fan running when the AC/Heater is off.<br><br>I am currently forced to put "1" for all hours for fan schedule...<br>
<br>this ensures   my AC/Heater will heat/cool the room when it is needed. But during idle hours... the Fan is using power to run  according to "fan power consumption" output...<br><br><br>What value should i put in the fan schedule besides "0" or "1" to fix this
 problem?<br><br><br><br>Thanks!<br><br><br></div></div></div><br></div></div>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br><br></div></div></div></div><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>