<div dir="ltr">Set the fan schedule value to "0" - this tells the fan to run in an unoccupied fashion, i.e. off under most conditions.<div><br></div><div>Then under System Parameters > Fans > Night Cycle Control select Cycle on Any.  This will tell the system to use the fan whenever the thermostat setpoint is not being met, but otherwise it will remain off.</div>
<div><br></div><div style>-Robby</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Tue, Mar 5, 2013 at 1:08 PM, Jay M <span dir="ltr"><<a href="mailto:fd111441@hotmail.com" target="_blank">fd111441@hotmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div><div dir="ltr">
Hi all,<br><br>How do i set the fan schedule to only be on when cooling or heating demands are required?<br><br>In DD edit,   fan schedule... I can only put  "0" or "1"... if i put "0"  then  the system is off and never Cools or Heats when heating or cooling is needed.<br>
<br>When  I put "1"   the fan is always on even when no heating or cooling is needed.<br><br>As a result for some hours I would get the fan running when the AC/Heater is off.<br><br>I am currently forced to put "1" for all hours for fan schedule...<br>
<br>this ensures   my AC/Heater will heat/cool the room when it is needed. But during idle hours... the Fan is using power to run  according to "fan power consumption" output...<br><br><br>What value should i put in the fan schedule besides "0" or "1" to fix this problem?<br>
<br><br><br>Thanks!<br><br><br>                                       </div></div>