<div dir="ltr">I can only answer one of your questions, but that is that selecting "No" on your isolation valve is the equivalent of having a three way valve. Per the DOE-2 Help file: <div><br></div><div>NO The unit does not have an isolation valve. Full
flow occurs whenever the loop pump is active.<br></div><div><br></div><div style>I would guess that DOE-2 is not accounting for increased compressor energy at lower flows. If you look at the Performance Curves under the Unitary Power tab there is no curve that uses condenser flow as an input.</div>
<div style><br></div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Fri, Mar 1, 2013 at 3:33 PM, Aaron Powers <span dir="ltr"><<a href="mailto:caaronpowers@gmail.com" target="_blank">caaronpowers@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">Hey All, Happy Friday,<div><br></div><div>I am trying to get a better feel for the control options available for variable flow through a geothermal ground loop attached to water-cooled heat pump units. Any comments would be greatly appreciated.</div>
<div><br></div><div>In eQuest, there appears to be only an option for an isolation valve at the system level with no option to select 3-way or 2-way valves. This makes sense because allowing for variable condenser flow would make the eir curves with respect to entering condenser temperature invalid. By selecting an isolation valve, I would expect that on an hourly basis, the valve can either be fully open or fully closed. With this in mind, I would expect the annual pump consumption to be equal for "Head Setpoint Control" = "Fixed At Coils" and "Head Setpoint Control" = "Valve Reset". However, I see that there is lower consumption with the "Valve Reset" strategy, which leads me to believe that DOE2 is treating the valves as two-way. Also, an hourly report of the condenser water flow through any unit shows that the flow is not always 0 or the design flow but is often at an intermediate value.</div>
<div><br></div><div>Here are my questions: Can anyone confirm that DOE2 is assuming a two-way valve by default? If so, how does DOE2 control the valves? Is there a hidden keyword that would allow for a three-way valve? Does DOE2 account for higher compressor consumption at reduced condenser flows?</div>
<div><br></div><div>Thanks,</div><div>Aaron</div></div>