<div dir="ltr">Hey All, Happy Friday,<div><br></div><div style>I am trying to get a better feel for the control options available for variable flow through a geothermal ground loop attached to water-cooled heat pump units. Any comments would be greatly appreciated.</div>
<div style><br></div><div style>In eQuest, there appears to be only an option for an isolation valve at the system level with no option to select 3-way or 2-way valves. This makes sense because allowing for variable condenser flow would make the eir curves with respect to entering condenser temperature invalid. By selecting an isolation valve, I would expect that on an hourly basis, the valve can either be fully open or fully closed. With this in mind, I would expect the annual pump consumption to be equal for "Head Setpoint Control" = "Fixed At Coils" and "Head Setpoint Control" = "Valve Reset". However, I see that there is lower consumption with the "Valve Reset" strategy, which leads me to believe that DOE2 is treating the valves as two-way. Also, an hourly report of the condenser water flow through any unit shows that the flow is not always 0 or the design flow but is often at an intermediate value.</div>
<div style><br></div><div style>Here are my questions: Can anyone confirm that DOE2 is assuming a two-way valve by default? If so, how does DOE2 control the valves? Is there a hidden keyword that would allow for a three-way valve? Does DOE2 account for higher compressor consumption at reduced condenser flows?</div>
<div style><br></div><div style>Thanks,</div><div style>Aaron</div></div>