<div>I'm having a hard time understanding how the PVVT and PVAVS systems would end up with dramatic differences in heating energy consumption and wanted to know if anyone had ever compared the two before?  </div><div> </div>
<div>I'm calibrating a model for an existing building.  The installed system is one of the common Trane SWUD units with single-stage electric heat and three-stage cooling.  If I model the system as a PVVT system to capture the staging, the energy use in June/July/August is within 5% of actual consumption but is understated by ~25% in the shoulder months and almost 50% in Dec/Jan.  If I model the system as a PVAVS system, heating months are within 5% but cooling months are overstated by ~15%.</div>
<div> </div><div>The only keywords I adjust between the two are the ones that eQuest automatically adjusts when the system type changes.  One possible cause of the problem from what I can see is that the PVVT system requires a control zone and that control zone defines temperature for all of the other zones (resulting in a lot of unmet load hours - up to 88% depending on the control zone selected).  Any thoughts?<br clear="all">
</div><div><div>Jeremy R. Poling, PE, LEED AP+BDC</div>