<font size=3>I don't think the behavior of INTERMITTENT changed from
DOE2.1e to DOE2.2.  The DOE2.1e Supplement has the same wording as
the DOE2.2 manual.  <br><br>
I would add some hourly reports - supply cfm, OA ratio, heating energy
and cooling energy.   Run for both CONTINUOUS and
INTERMITTENT.  There may be some differences in the amount of
outdoor air that is being introduced. <br><br>
At 11:20 AM 27/01/2013, RobertWichert wrote:<br>
<blockquote type=cite class=cite cite="">Thanks for the link to the
manuals and such, Chris.<br>
<br>
I am also investigating "intermittent" as it affects EnergyPro,
which claims to use "DOE-2.1E* v119".<br><br>
The issue involves using "INTERMITTENT" and how that affects
heating energy.  Heating energy drops dramatically when
"INTERMITTENT" is invoked.  It drops so far that it does
not seem realistic, although no errors or flags result that I can
find.<br><br>
I have found some references to "INTERMITTENT" causing negative
CFM: 
<a href="http://doe2.com/download/DOE-22/Bugfixes-047h.pdf">
http://doe2.com/download/DOE-22/Bugfixes-047h.pdf</a><br><br>
Question - Do you (or anybody on the list) have any ideas why invoking
"INTERMITTENT" in a program that uses DOE-2.1E*V119 would show
such effects on heating energy (very, very, very low)?????<br><br>
<br>
Thanks for thinking about this!<br><br>
<br><br>
<br><br>
</font><pre>Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068







===============================================
</pre><font face="Courier New, Courier" size=3></font>On 1/27/2013 7:47
AM, Chris Jones wrote:<br>
<blockquote type=cite class=cite cite="">Hello Jay, <br>
Do you have the DOE2.2 Reference manuals?  DOE2.2Vol2-Dictionary.pdf
explains what the INTERMITTENT keyword means.  <br><br>
See page 361 under INDOOR-FAN-MODE.<br><br>
The reference manuals are available for download at <br>
<a href="http://doe2.com/download/doe-22/" eudora="autourl">
http://doe2.com/download/doe-22/</a><br><br>
Download the latest edition of each manual and enjoy!<br><br>
<br>
At 05:29 PM 26/01/2013, Jay M wrote:<br>
<blockquote type=cite class=cite cite="">Hi all,<br><br>
I tried searching for an answer on archives but unable to find an
answer.<br><br>
I in Schematic Mode I set fan to "intermittent"  meaning
HVAC fan is only on when heating/cooling is needed... <br><br>
1) if I set it a value of "1" fan is on alwayst on<br>
2) Set 0 Fan is "off"<br><br>
Since it is in intermittent mode, when i set to 0.... there is never any
cooling.  what am I doing wrong?  Because if i set fan schedule
in Detailed edit mod to 1 the fan is always on and I don't want
that.<br><br>
I want intermittment fan schedule  but it's either 1 or 0 in the fan
schedule...<br><br>
<br>
Thanks!<br>
_______________________________________________</blockquote><br>
>><br>
Christopher Jones, P.Eng.<br>
Suite 1801, 1 Yonge Street<br>
Toronto, ON M5E1W7<br>
Tel. 416-203-7465<br>
Fax. 416-946-1005<br>
email <a href="mailto:cj@enersave.ca">cj@enersave.ca</a><br><br>
<br><br>
<pre>_______________________________________________
Equest-users mailing list
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to
<a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre><font face="Courier New, Courier" size=3></font></blockquote><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" eudora="autourl">
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
<br>
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</blockquote>
<x-sigsep><p></x-sigsep>
>><br>
Christopher Jones, P.Eng.<br>
Suite 1801, 1 Yonge Street<br>
Toronto, ON M5E1W7<br>
Tel. 416-203-7465<br>
Fax. 416-946-1005<br>
email cj@enersave.ca<br>
</body>
</html>