<div>Hi Zheng,</div><div><br></div>The SS-A report will provide you system wise loads summary. This may help to identify the systems and period during which you have unexpected heating.<div>Once you identify the systems you can use the SS-G report to figure out what's happening at individual zone level for the systems affected.</div>
<div><br></div><div>I hope this helps.</div>
<div><br></div><div>Sunil Nair</div><div><br><div class="gmail_quote">On Sat, Jan 19, 2013 at 5:30 AM, Zheng Ling <span dir="ltr"><<a href="mailto:zling@williamsengineering.com" target="_blank">zling@williamsengineering.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div lang="EN-US" link="blue" vlink="purple"><div><p class="MsoNormal">Hi there:<u></u><u></u></p><p class="MsoNormal">
<u></u> <u></u></p><p class="MsoNormal">I meet a strange simulation result. The project is is 6000 SQM warehouse plus a 1000 SQM office. The result shows a surprising natural gas usage 84581 MBTU or 89237 GJ. 96% belongs to space heating. <u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p><p><span style="font-size:11.0pt;font-family:"Calibri","sans-serif"">REPORT- LS-C BuiLding Peak Load Components shows heating load 32.5 W/m2 (excluding outside ventilation air loads). This is normal. <u></u><u></u></span></p>
<p><span style="font-size:11.0pt;font-family:"Calibri","sans-serif""><u></u> <u></u></span></p><p class="MsoNormal">REPORT- SS-D Building HVAC Load Summary shows annual heating energy 1460 MBTU or 1540 GJ.<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">Is there anywhere else to check the source of the extra abnormal space heating load?<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">
THX!<u></u><u></u></p><p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#545861">ZHENG LING, </span></b><b><span style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#545861">P.Eng.</span></b><span style="font-size:10.0pt;font-family:"Century Gothic","sans-serif""><u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#545861">Mechanical<u></u><u></u></span></b></p><p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Century Gothic","sans-serif""> <u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#d52b1e">Williams Engineering Canada Inc.<u></u><u></u></span></b></p><p class="MsoNormal"><span style="font-size:8.0pt;font-family:"Arial","sans-serif"">10010-100 Street, Edmonton, AB, T5J 0N3<u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#545861">T: </span></b><span style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#545861">780.409.3185 </span><b><span style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#545861"> F: </span></b><span style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#545861">780.425.1520 </span><b><span style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#545861">W: </span></b><span lang="EN-CA" style="font-size:12.0pt;font-family:"Times New Roman","serif""><a href="http://www.williamsengineering.com/" target="_blank"><span lang="EN-US" style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#545861;text-decoration:none">williamsengineering.com</span></a></span><span style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#545861"> <u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4c3327"><br></span><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4c3327">Engage. Innovate. Inspire.</span></b><span style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#4c3327"><br>
</span><span style="font-size:7.5pt;font-family:"Arial","sans-serif";color:gray"><br></span><b><span style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#7ab800">Please consider the environment before printing this email.</span></b><b><span style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#545861"><br>
</span></b><span lang="EN-CA" style="font-size:12.0pt;font-family:"Times New Roman","serif""><a href="http://www.williamsengineering.com/legal" target="_blank"><b><span lang="EN-US" style="font-size:7.5pt;font-family:"Arial","sans-serif";color:#545861;text-decoration:none">Email Transmission Policy</span></b></a></span><span style="font-size:10.0pt;font-family:"Century Gothic","sans-serif""><u></u><u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p></div></div><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>