    Peter,<br>
    <br>
    I think this is a very unwise way to model complex fenestration,
    because you'll be using the Simple Window Model in DOE-2, which
    assumes that the angular<br>
    variation of SHGC and temperature variation of U-factor are the same
    as for single-pane clear glass.  I haven't followed the development
    of LBNL's Window (not Windows :-)) program for the past five years,
    but the program used to produce a text "WINDOW 4" file that can be
    read into DOE-2 or eQUEST.    If this is still possible, I would
    recommend using that method.  There are still the questions of
    venetian blind shading that is not dependent only on the angle of
    incidence, but also the azimuth relative to the blinds (there must
    be a technical term for this, but I don't know that off the cuff),
    and if you want to change the angle of the venetian blinds depending
    on season.  I can think of ways of dealing with these issues, but it
    would require writing a USER FUNCTION, which I don't think has been
    implemented in DOE-2.2.<br>
    <br>
    Joe <br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <br>
    On 12/22/2012 5:51 PM, Peter Baumstark wrote:
    <blockquote
      cite="mid:1356227493.86472.YahooMailRC@web181505.mail.ne1.yahoo.com"
      type="cite">
      <meta http-equiv="Context-Type" content="text/html;
        charset=us-ascii">
      <div>
        <div>Ok. . .  I have a situation where I'm modeling a facility
          relative to ASHRAE 90.1 baseline.  The customer is using dual
          pane, low-e windows, with integrated venetian blinds between
          the two panes of glass.  One pane is low-e and the other is
          clear.  Air gap between the two (not Argon or anything like
          that).<br>
          <br>
          I use the LBNL Windows tool, with blinds set at 45 deg, and
          the blinds increase the window assembly U value and SHGC
          significantly.<br>
          <br>
          So for performance relative to 90.1, would it be acceptable to
          simply utilize the U & SHGC from with Windows tool?  Are
          there any restrictions on the angle of the blinds, or whether
          the angle should be different for winter vs summer?<br>
          <br>
          I'd appreciate any guidance on how to best model this
          scenario.<br>
          <br>
          Thank you,<br>
          Pete Baumstark<br>
          San Jose, CA<br>
        </div>
      </div>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>