Thanks Kieth.<div><br></div><div>This makes sense. Based on air speed and air pressure, you would expect to see an adjusted air infiltration. </div><div><br></div><div>However, does eQuest take into account the location of the facade in the context of the building. For example, if you had a U-shaped building, the faces on the interior of the "U" would not see as much direct wind exposure as the faces on the exterior of the "U." Does eQuest take into account the effects the building geometry will have? </div>
<div><br><br><div class="gmail_quote">On Wed, Nov 28, 2012 at 4:46 PM, Keith Swartz <span dir="ltr"><<a href="mailto:kswartz@ecw.org" target="_blank">kswartz@ecw.org</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div lang="EN-US" link="blue" vlink="purple"><div><p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif"">Patrick,<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif"">eQUEST accounts for wind with most of the infiltration methodologies. From the Help screen…<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><u></u> <u></u></span></p><p class="MsoNormal"><img width="846" height="551" src="cid:image001.jpg@01CDCD7F.94D32A60"><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif"">…and…<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><u></u> <u></u></span></p><p class="MsoNormal"><img width="685" height="682" src="cid:image002.jpg@01CDCD7F.94D32A60"><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif"">Keith Swartz, PE, LEED AP<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif"">Senior Energy Engineer | <b>Energy Center of Wisconsin</b></span><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:gray"> | <b>Madison.Chicago.Minneapolis<u></u><u></u></b></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><a href="tel:608.210.7123" value="+16082107123" target="_blank">608.210.7123</a> | <a href="http://www.ecw.org/" title="Energy Center Home Page" target="_blank"><span style="text-decoration:none">www.ecw.org</span></a><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><u></u> <u></u></span></p><p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> Patrick Keeney [mailto:<a href="mailto:38keeney@cardinalmail.cua.edu" target="_blank">38keeney@cardinalmail.cua.edu</a>] <br>
<b>Sent:</b> Wednesday, November 28, 2012 12:21 PM<br><b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] Taking into account wind on building surface<u></u><u></u></span></p>
<div><div class="h5"><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">Hey All,<u></u><u></u></p><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">I was hoping someone could clarify whether or not eQuest takes into account the wind load placed on the exterior surface of the building. I know that the direction, speed, and temperature of the prevailing breezes are included in the weather file, but am unsure as to whether or not this data is included on heat transfer through the building envelope.<u></u><u></u></p>
</div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">The case in point is a large facade directly aligned with the winter prevailing breezes of our site and whether or not this heat transfer is being accounted for on the surface.<u></u><u></u></p>
</div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">Any and all help is much appreciated.<u></u><u></u></p></div><div><p class="MsoNormal">Thanks.<br clear="all"><u></u><u></u></p><div><p class="MsoNormal">
<u></u> <u></u></p></div><p class="MsoNormal">-- <br>Patrick J Keeney<br>MArch-MSSD Candidate<br><a href="tel:410-299-5627" value="+14102995627" target="_blank">410-299-5627</a><u></u><u></u></p></div></div></div></div></div>
</blockquote></div><br><br clear="all"><div><br></div>-- <br>Patrick J Keeney<br>MArch-MSSD Candidate<br>410-299-5627<br>