<font size="+1">You need to exhaust the 1500 CFM. If you exhaust
1200 eQuest will assume there is 300 CFM of return air. Your
model is a box<font size="+1">. <u> Everything</u> going in or ou<font
size="+1">t must balance. If you don't do it eQuest will.<br>
<font size="+1">Bruce Easterbrook P.Eng.<br>
<font size="+1">Abode Engineering</font><br>
</font></font></font></font>
<div class="moz-cite-prefix">On 29/10/2012 12:36 PM, Ömer Moltay
wrote:<br>
</div>
<blockquote cite="mid:508EB09F.5080806@mimtarch.com" type="cite">Dear
All,
<br>
<br>
I am trying to model a system with 1500 CFM system supply but no
return, all of the flow will be exhausted from the zones. Looking
at hourly reports, I can never get the return flow to be zero,
eQuest will always add exhaust and return and make my system
supply 3000 CFM. How does one zero the return flow?
<br>
<br>
Thanks,
<br>
<br>
Omer Moltay
<br>