Good afternoon,<br><div class="gmail_quote">

<p class="MsoNormal"> </p>

<p class="MsoNormal">Im
trying to find out the following maybe you guys can help me out here. I’m
currently modeling a facility of a total of 47,600 SF including a 28,000 SF
Warehouse. The facility includes 2 levels of offices, breakrooms, etc and a
double height warehouse adjacent to them. The proposed design is composed
of   2 AHUs, one for the first floor, one for the second and an only
heating and ventilation system based on 2 boilers for the warehouse. According
to this, the baseline should be a System 5 Packaged VAV with Reheat, Packaged
rooftop VAV with reheat, Direct expansion cooling type and  Hot-water
fossil fuel boiler for heating. One system per floor. FYI, we tried the whole
addenda “dn” thing but it did not work because the allowance of fan power for
the warehouse area was extremely low, so we kept the normal compliance path.
However, when this is the case, we would have to model the baseline and
proposed warehouse with both heating and cooling. (specified on Table G3.1) same
system 5; but my question would be in terms of envelope. Would they have to be classified
as regular non-residential R values for the proposed? Shouldn’t both baseline
and proposed warehouse have the same u- values as well? Should they be
classified as semiheated envelope values, since in reality this is a warehouse
and the owner/architect are not really counting on putting insulation in this
area?</p>

<p class="MsoNormal">I
would appreciate your suggestions and interpretation.</p>

<p class="MsoNormal"> </p>

<p class="MsoNormal"><br></p>

<p class="MsoNormal"><img src="cid:ii_13a99ec8581eb2a5" alt="Inline image 1"><br></p>
<br>_______________________________________________<br>
Trace-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:TRACE-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">TRACE-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></div><br>