i have followed the 62-1999 rates for the baseline. as the epact
requirements state the 90.1-2004 app g method has been modified to
meet the requirements of epact. this is one the differences. it is
my understanding that where there is a difference between epact
requirements and 90.1-2004 modeling requirements the epact
requirement takes precedence. <br>
<br>
On 10/22/12 10:35 AM, Steve Jacobs wrote:
<blockquote
cite="mid:CAKV7dFfo=33jWn9YpAUYTM20Zip_siP8048vFssxA4wdyxU2Zg@mail.gmail.com"
type="cite">
<div>Hi everyone,</div>
<div>I have a question about the ventilation requirements for 179d
modeling. The NREL guidelines state to use 62-1999 for the
baseline and the actual rates for the proposed building. I'm so
use to modeling ventilating rates the same in both models I
wanted to make sure I'm interpreting this correctly. I've been
doing separate 62 calculations per ASHRAE 62-1999 for the
baseline. This can make a significant difference in the OA rates
between the baseline and proposed. The 1999 rates are higher
than the 2004/2007 rates for some building area types. Also, if
the baseline model is a VAV system with a critical zone driving
the OA rate, the difference can be even greater. </div>
<div> </div>
<div>
<div>How have you guys handled this situation?</div>
</div>
<div> </div>
<div>On a separate note, has anyone done epact for building on a
central plant. Obviously it is not covered by the NREL
guidelines, so it seems like it is on the engineer to come up
with a reasonable interpretation.</div>
<div> </div>
<div> </div>
<div>- Steve</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
</body>
</html>